Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

NetBotz external port configuration

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • NetBotz external port configuration
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 01:05 AM . Last Modified: ‎2024-04-02 11:20 PM

0 Likes
11
2448
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 01:05 AM . Last Modified: ‎2024-04-02 11:20 PM

NetBotz external port configuration

I would like to configure NetBotz570 external sensor ports. The sensors are temperature and humidity sensors.

What is the correct sensor name when I add custom analog sensor to the system?

I would like to add this temperature and humidity data to the DCE virtual sensor option. Where I can get the average of this sensors. There is a predefined sensor, Temperature Detector TS-100 where the sensor is identified like a temperature sensor via the NetBotz systems.

 

How to configure the system to show a temperature sensor is connected to the 0-5V external port?

 

(CID:153945165)

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 01:06 AM . Last Modified: ‎2024-04-02 11:20 PM

0 Likes
5
2448
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 01:06 AM . Last Modified: ‎2024-04-02 11:20 PM

Hi,

 

The proper values for the 0-5v device should show properly in both NetBotz and DCE regardless of what icon is displayed in the UI. There is no way to force the icon to show up as the temperature icon. Yes, they will always show up as the generic blue sensor icon.

 

As for reports in DCE, I added a 0-5v cable on an appliance:

 

DCE can see it as the "Temperature (temperature_forum)" sensor:

As with your report, I do not see it available under the temperature report:

 

The only thing I can suggest is to create a "custom" report in DCE instead of a temperature report to see these values. As you can see here, I am able to filter by the partial word "temp" and I see not only my temperature (temperature_forum) sensor but the other temperature sensors in that group as well:

 

I can add this as an enhancement request but I can not promise it will make it into the system.

 

Steve

(CID:154403447)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 11
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 01:05 AM . Last Modified: ‎2024-04-02 11:20 PM

0 Likes
0
2448
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 01:05 AM . Last Modified: ‎2024-04-02 11:20 PM

If I choose the predefined sensor Temperature Detector TS-100 the NetBotz recognize that is a temperature sensor. You can see the icon before the label text.

When I create a new custom sensor. I set the sensor type to temp or temperature, there is no change. The icon is set to default sensor. (blue icon)  

I don’t know what is the proper name for the sensor type to be recognized it as a temperature or humidity sensor. 

 

 

(CID:153945471)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 01:06 AM . Last Modified: ‎2024-04-02 11:20 PM

0 Likes
0
2448
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 01:06 AM . Last Modified: ‎2024-04-02 11:20 PM

Dear Gabor Novak,

Thank you very much for the explanatory screenshots to your main question:

What is the correct sensor name when I add custom analog sensor to the system?

This is an interesting question and I would also like to hear the =SE= staff answer.

I suspect that's how NetBotz software works with custom analog (0-5V) and custom current (4-20mA) ports. This means, that they will always appear as a blue circle no matter what name you give them.

By the way, what is your version of NetBotz software?

With respect.

(CID:153945540)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 01:06 AM . Last Modified: ‎2024-04-02 11:20 PM

0 Likes
0
2448
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 01:06 AM . Last Modified: ‎2024-04-02 11:20 PM

Dear @spezialist, system and radio engineer

 

I suspect that's how NetBotz software works with custom analog (0-5V) and custom current (4-20mA) ports. This means, that they will always appear as a blue circle no matter what name you give them.

I don’t think so, because there is the predefined sensor which is called Temperature Detector TS-100 is 0-5V sensor. The screenshot above was made, when I changed the 0-5V sensor form the list.

 

When we look the DCE system, you can view this kind of “blue icon” as other numeric sensor. You can’t create report for temperature and humidity. Because the systems doesn’t recognize it as temperature and humidity sensor. You can’t create virtual sensor from this “blue icon”, the temperature and humidity doesn’t appears in the DCE system.

For example when I look into the DDF file, there is the same sections. 

(num=numeric) for the temperature temp etc. 

The type of the sensor is telling the systems, which kind of sensor is that.

	       num
			MANUFACTURER_CODE
			
				MANUFACTURER_CODE
			
			1
			
			Status Information
		

 

When we add a new custom sensor, if I’m correct we tell the same information to the netbotz system. The type of the sensor (temp, hum, etc.). The label and the working parameters.  (scaling, units)

 

By the way, what is your version of NetBotz software?

 

It is the newest, 4.6.4. 

 

Gabor

(CID:154402992)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 01:06 AM . Last Modified: ‎2024-04-02 11:20 PM

0 Likes
0
2448
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 01:06 AM . Last Modified: ‎2024-04-02 11:20 PM

Dear Gabor Novak,

You correctly noticed everything, but DDF-files of the DCE software have nothing to do with this, since you have a NetBotz appliance, and not a NetBotz device - this is an important difference.

Nevertheless, when you select a predefined by developers sensor model from the NetBotz appliance menu, I suspect that the appropriate template for it is selected inside (i.e. hardcoded). When you choose just add custom sensor 0-5V, then an appropriate template is created for it, as for a numerical sensor and no more.

Maybe Steven Marchetti can help us understand this important issue?

With respect.

(CID:154403293)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 01:06 AM . Last Modified: ‎2024-04-02 11:20 PM

0 Likes
5
2449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 01:06 AM . Last Modified: ‎2024-04-02 11:20 PM

Hi,

 

The proper values for the 0-5v device should show properly in both NetBotz and DCE regardless of what icon is displayed in the UI. There is no way to force the icon to show up as the temperature icon. Yes, they will always show up as the generic blue sensor icon.

 

As for reports in DCE, I added a 0-5v cable on an appliance:

 

DCE can see it as the "Temperature (temperature_forum)" sensor:

As with your report, I do not see it available under the temperature report:

 

The only thing I can suggest is to create a "custom" report in DCE instead of a temperature report to see these values. As you can see here, I am able to filter by the partial word "temp" and I see not only my temperature (temperature_forum) sensor but the other temperature sensors in that group as well:

 

I can add this as an enhancement request but I can not promise it will make it into the system.

 

Steve

(CID:154403447)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 01:06 AM . Last Modified: ‎2024-04-02 11:20 PM

In response to DCIM_Support
0 Likes
0
2448
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 01:06 AM . Last Modified: ‎2024-04-02 11:20 PM

Steven Marchetti, very thanks for the detailed explanation on this issue.

(CID:154403463)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 01:06 AM . Last Modified: ‎2024-04-02 11:20 PM

In response to DCIM_Support
0 Likes
0
2448
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 01:06 AM . Last Modified: ‎2024-04-02 11:20 PM

Welcome

 

(CID:154403488)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 01:06 AM . Last Modified: ‎2024-04-02 11:20 PM

In response to DCIM_Support
0 Likes
0
2447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 01:06 AM . Last Modified: ‎2024-04-02 11:20 PM

The proper values for the 0-5v device should show properly in both NetBotz and DCE regardless of what icon is displayed in the UI. There is no way to force the icon to show up as the temperature icon. Yes, they will always show up as the generic blue sensor icon.

 

The icon type is not so important for me, but the meaning is. When I setup a new custom 0-5V sensor, the first field is the type. My guess is that this field is not working properly, it doesn’t recognize the specified sensor.

I mentioned it before the predefined 0-5V sensor (Temperature Detector TS-100) works fine, it’s shows as a temperature sensor.  If I use this kind of sensor definition for the 0-5V sensor. The DCE can see the value as a temperature and I can create from this temperature value virtual sensor for the average temperature.  

My problem is just that I can’t create virtual sensor for average temperature and humidity.

(CID:154403860)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 01:06 AM . Last Modified: ‎2024-04-02 11:20 PM

In response to DCIM_Support
0 Likes
0
2447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 01:06 AM . Last Modified: ‎2024-04-02 11:20 PM

Sorry, I addressed the image and report mentioned (in reply to spezialist) but missed the virtual sensor aspect of your question. I've specifically noted this aspect of the issue to the enhancement request I created on the initial response. Again, as with the report, you can choose to create a different virtual sensor. In this case, you can add these as "Other Numeric" sensors.

Here, you can see I haven't yet deleted the "temperature_forum" 0-5 volt sensor I created for the initial response and it is available as  different type:

I know this is not exactly what you're looking for but if you have multiple sensors of this type, you can still get a virtual sensor for them. 


Steve

(CID:154404388)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 01:06 AM . Last Modified: ‎2024-04-02 11:20 PM

In response to DCIM_Support
0 Likes
0
2447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 01:06 AM . Last Modified: ‎2024-04-02 11:20 PM

Dear Steven Marchetti

 

Sorry, I addressed the image and report mentioned in reply to spezialist) but missed the virtual sensor aspect of your question. I've specifically noted this aspect of the issue to the enhancement request I created on the initial response. Again, as with the report, you can choose to create a different virtual sensor. In this case, you can add these as "Other Numeric" sensors.


 

Thanks, I have missed that option.

Tomorrow I will check it.


(CID:154404396)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 01:06 AM . Last Modified: ‎2023-10-22 03:15 AM

0 Likes
0
2447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 01:06 AM . Last Modified: ‎2023-10-22 03:15 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore