Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

NetBotz 750 dropping sensor pod connections.

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • NetBotz 750 dropping sensor pod connections.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
G-Pop
G-Pop
Explorer

Posted: ‎2024-04-25 08:23 AM

0 Likes
3
1710
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-25 08:23 AM

NetBotz 750 dropping sensor pod connections.

Our NetBotz 750 does this intermittently: 

Alert Description:

Disconnected 2893991570125504295: 28298600004E3F27 is not responding.

Alert Type:

Sensor pod unplugged

Alert Description:

Communication with the 2893991570125504295: 28298600004E3F27 has been restored.

Alert Type:

Sensor pod replugged

Disconnection and reconnection happens within a couple of minutes.

All sensor pods, cables, etc. are new, but issue remains.  Any thoughts?

Thanks ... Jake.

Labels
  • Labels:
  • Datacenter Netbotz & Monitoring
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Teken
Teken
Champion

Posted: ‎2024-04-26 08:39 AM . Last Modified: ‎2024-04-26 08:40 AM

0 Likes
2
1693
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-26 08:39 AM . Last Modified: ‎2024-04-26 08:40 AM

To be clear is this one of the universal sensors declaring this fault like a AP9335 temp, AP9335TH temp / humidity, AP9520 TH display, other? 

Or is this one of those extended sensor pods that offer more ports? If the latter than I would ask is the (Terminator) plug inserted as required in the A-Link port?

 

If everything is new (sensors) and hardware swap the ports to see if the problem follows the sensor.


If it does that points to the sensor, cable, both. It should be called out trying different cables from shielded vs none shielded would be a good test.

 

If you have extended the cable run insure the cable is at least 23 AWG and not 24-28 AWG as the resistance can drop the voltage and the returned (resistance) expected can result in the problem you see. 

CAT5e is called out by APC and CAT7 / CAT8 which is shielded isn’t for some reason.

Reply

Link copied. Please paste this link to share this article on your social media post.

G-Pop
G-Pop
Explorer

Posted: ‎2024-05-16 02:00 AM

In response to Teken
0 Likes
1
1618
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-16 02:00 AM

Thanks for responding!  We have six Sensor Pod 150's daisy chained with CAT6, unshielded.  Terminator plug in the last A-Link port.  "Unplugging" is random (times & sensors).  Tried switching ports.  No effect.  This is our second "750" appliance.  Better than the first but still flaky.  Below is an incident example.  Thanks for your help.

G-Pop.

Alert Description:

Disconnected TEMPERATURE: Rack B1 - FWD is not responding.

Alert Type:

Temperature sensor unplugged

Pod:

NetBotz Sensor Pod 150 3 - B1 TH Probe 1

Time Detected:

2024/03/08 02:56:12-0500 EST PM

Notification Time:

2024/03/08 02:56:18-0500 EST PM

Version:

5.3.5.434

Hostname:

apc-6-datacenter

IP Address:

(omitted)

Notification:

Netbotz_Alerts

Alert Id:

2076

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2024-05-17 07:46 AM

In response to G-Pop
0 Likes
0
1616
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-17 07:46 AM

I would disconnect five pods and see if the problem goes away. If so add one more pod to see what happens.

 

My expectation is you’ll begin to see a drop out by the 4th - 6th pod. Report back what you see and observe. 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore