Nagios with powernet410.mib send a strange message

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • 🔒 Closed
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:18 AM . Last Modified: ‎2024-04-05 03:52 AM

0 Likes
4
931
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:18 AM . Last Modified: ‎2024-04-05 03:52 AM

Nagios with powernet410.mib send a strange message

Dear team,

I've a customer who is monitoing traps from DCE with Nagios XI using the powernet410.mib and has received this message from Nagios:

APC ISXC: An ISXC Failure Alarm exists.: An ISXC Failure Alarm exists. / enterprises.318.2.3.10.0 ():B010203_nbErrorCond_E7B6A6A1 enterprises.318.2.3.23.0 ():53 65 20 70 65 72 64 69 C3 B3 20 6C 61 20 63 6F 6D 75 6E 69 63 61 63 69 C3 B3 6E enterprises.318.2.3.1.0 ():2 enterprises.318.2.3.11.0 ():B010203_nbSNMPEncDA85077F enterprises.318.2.3.24.0 ():SF03R05 (172.26.230.13) enterprises.318.2.3.16.0 (): enterprises.318.2.3.25.0 ():PDU enterprises.318.2.3.17.0 ():QD1626311534 enterprises.318.2.3.20.0 ():Modular PDU enterprises.318.2.3.21.0 ():172.26.230.13 enterprises.318.2.3.26.0 ():SF03R05 enterprises.318.2.3.27.0 (): enterprises.318.2.3.22.0 ():B010203_nbSNMPEncDA85077F_STATUS enterprises.318.2.3.28.0 ():45 73 74 61 64 6F 20 64 65 6C 20 76 C3 AD 6E 63 75 6C 6F enterprises.318.2.3.29.0 ():0 enterprises.318.2.3.6.0 ():1511462664 enterprises.318.2.3.7.0 ():0 enterprises.318.2.3.30.0 ():53 65 20 68 61 20 70 65 72 64 69 64 6F 20 6C 61 20 63 6F 6D 75 6E 69 63 61 63 69 C3 B3 6E 20 63 6F 6E 20 27 53 46 30 33 52 30 35 20 28 31 37 32 2E 32 36 2E 32 33 30 2E 31 33 29 27 2E
Date/Time: 2017-11-23 19:48:02

What that means? Need we any additional OID?

Best regards,

 

Enric Climent

 

(CID:126180295)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:18 AM . Last Modified: ‎2024-04-05 03:52 AM

0 Likes
2
931
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:18 AM . Last Modified: ‎2024-04-05 03:52 AM

Hi Enric,

you don't need another OID or MIB. The information contained in a trap from DCE is outlined in the following base:

http://www.apc.com/us/en/faqs/index?page=content&id=FA231439&actp=search&viewlocale=en_US&searchid=1...

Some of the data appears to be in code instead of text so it may be something to do with how the trap receiver is formatting the data. I'd suggest either checking what your getting with another trap receiver or maybe even just a packet capture. You can try updating the MIB but I do not believe that is the reason for what appears to be a formatting issue. 

Thanks,

Steve

(CID:126180317)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:18 AM . Last Modified: ‎2024-04-05 03:52 AM

0 Likes
2
932
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:18 AM . Last Modified: ‎2024-04-05 03:52 AM

Hi Enric,

you don't need another OID or MIB. The information contained in a trap from DCE is outlined in the following base:

http://www.apc.com/us/en/faqs/index?page=content&id=FA231439&actp=search&viewlocale=en_US&searchid=1...

Some of the data appears to be in code instead of text so it may be something to do with how the trap receiver is formatting the data. I'd suggest either checking what your getting with another trap receiver or maybe even just a packet capture. You can try updating the MIB but I do not believe that is the reason for what appears to be a formatting issue. 

Thanks,

Steve

(CID:126180317)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:19 AM . Last Modified: ‎2024-04-05 03:52 AM

In response to DCIM_Support
0 Likes
0
931
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:19 AM . Last Modified: ‎2024-04-05 03:52 AM

Hi Steve,

The customer isn't be able to format well the data in Nagios. Could you help us and tell us what have to do into Nagios?

Best regards,

 

Enric

 

(CID:126184567)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:19 AM . Last Modified: ‎2024-04-05 03:52 AM

In response to DCIM_Support
0 Likes
0
933
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:19 AM . Last Modified: ‎2024-04-05 03:52 AM

Hi Eric,

 

Sorry but I can not help with Nagios. I am not familiar with that product and if they do need Nagios specific help, they may want to contact the vendor. 

To make sure it is an issue with the system and how it is formatting the data, I suggest causing another (different type) trap from DCE and seeing if Nagios has issues with that one too. Potentially doing a packet capture during the traps that do not appear to be formatted properly would be helpful as well.

 

Steve

(CID:126184893)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:19 AM . Last Modified: ‎2023-10-22 03:09 AM

0 Likes
0
932
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:19 AM . Last Modified: ‎2023-10-22 03:09 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore