New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
NBRK0250 out of Band
EcoStruxure IT Forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-08-1106:53 AM
NBRK0250 out of Band
Hello! Can i conect any Netbotz with a out of band 4G/5G solution for backup comunication?
For example, If i want to have a primary way to comunicate (ethernet), and if its fail the sistemas automaticly change to 4G/5G comunicaction throught a modem.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-08-1206:22 AM
Hi @Anonymous user ,
No, there is no modem connection option on the NBRK0250. The only thing I can suggest is a 3rd party gateway that can take an e-mail and transmit it as text. We don't have any that we specifically suggest but there are a few products or services out there if you do a google search. Here are a few:
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-08-1206:22 AM
Hi @Anonymous user ,
No, there is no modem connection option on the NBRK0250. The only thing I can suggest is a 3rd party gateway that can take an e-mail and transmit it as text. We don't have any that we specifically suggest but there are a few products or services out there if you do a google search. Here are a few: