Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Missing Temperature History reports on DCE Web Interface

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Re: Missing Temperature History reports on DCE Web Interface
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
markus.albisser
markus.albisser
Contributor

Posted: ‎2025-08-27 09:38 PM

0 Likes
3
1751
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-27 09:38 PM

Missing Temperature History reports on DCE Web Interface

Dear all

 

Since some time, I miss the history reports when accessing the EcoStuxure DCE (Version 8.3.0.91). The history is available when I am using the client installation, therefore it is not a storage problem. Strange is that the history for the humidity I can see and access, but not for temperature, fan speed or valve position. I tried with a different browser, same result. Within the client, I am logged in with the same user as via web browser. I also reloaded the DCE server.

 

Any idea why this happen? The history was available in the past, but I cannot tell since when it is no longer there (as I said, it is missing via web interface, but is available on the client).

 

Many thanks

Markus

Labels
  • Labels:
  • Data Center Expert
  • Tags:
  • EcoStruxure DCE web history
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
markus.albisser
markus.albisser
Contributor

Posted: ‎2025-09-26 07:48 AM

1 Like
0
1624
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-26 07:48 AM

Hi all, just to give you an update here. I got the solution from support, to get the charts within the DCE web client restored: In the DCE client, go to System -> Server Administration Settings -> Time Settings. Under Regional Settings, chose "English" as the server Locale.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
APC_Steve
APC_Steve Leader
Leader

Posted: ‎2025-08-28 04:42 AM . Last Modified: ‎2025-08-28 05:00 AM

0 Likes
0
1738
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-28 04:42 AM . Last Modified: ‎2025-08-28 05:00 AM

Hi @markus.albisser ,  I've not see the specific behavior you're describing but I am curious as to the user that you're logging in as. Is this an LDAP user? I ask because there are some inconsistencies with the web when logging in as an LDAP/AD user. If so, I suggest you log in or have someone log in as a local user and verify they see the same thing you're seeing.

 

Other than that, you may want to contact tech support directly as this may take a bit more discovery work and back and forth before we may be able to isolate the issue.


Thanks,

Steve

 

P.S.
The LDAP issue I mentioned above is noted as resolved in DCE 9.0.

Reply

Link copied. Please paste this link to share this article on your social media post.

markus.albisser
markus.albisser
Contributor

Posted: ‎2025-08-28 05:04 AM

0 Likes
0
1735
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-28 05:04 AM

Hi @APC_Steve , many thanks for your feedback. Yes, we have an AD integration, but the issue I see with a local created user. To be sure the issue is still there, I created a new user and assigned the groups "Server Administrators" and "Device Administrators". The result is the same.

 

The weird thing is that, when I open such a page where the history is empty and I click on "Export to CSV", the exported CSV contains all the historical data! Therefore, the data is there, but it somehow cannot be displayed.

 

But I will follow your recommendation and contact the tech support.

 

Thank you

Markus

Reply

Link copied. Please paste this link to share this article on your social media post.

markus.albisser
markus.albisser
Contributor

Posted: ‎2025-09-26 07:48 AM

1 Like
0
1625
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-26 07:48 AM

Hi all, just to give you an update here. I got the solution from support, to get the charts within the DCE web client restored: In the DCE client, go to System -> Server Administration Settings -> Time Settings. Under Regional Settings, chose "English" as the server Locale.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore