Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Measurement trending

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Measurement trending
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
160
Jef
Jef Leader
114
gsterling
gsterling Mentor
79
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
jzurera
jzurera
Troubleshooter

Posted: ‎2026-10-30 06:27 AM

0 Likes
1
127
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-10-30 06:27 AM

Measurement trending

Hi team,

 

We have a facility with ITA 10, where we monitor rack power consumption through sensor mapping. The racks are still empty in terms of equipment, but we can see real-time power consumption through the electrical panel.

 

The capacity pop-up shows a power value higher than what we’re currently measuring. We’ve noticed that this is related to the Measurement Trending configuration window, but we don’t understand how it works. We’d like the capacity to show the peak value from the last 30 days rather than an estimate—is that possible?

jzurera_0-1793366848507.png

 

jzurera_1-1793366857928.png

 

Labels
  • Labels:
  • IT Advisor
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
gsterling
gsterling Mentor
Mentor

Posted: ‎2026-11-02 04:29 AM

0 Likes
0
97
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-11-02 04:29 AM

Hello jzurera

 

The measurement trending view allows the customer to customize how measurements are treated in ITA. These settings apply customer who have set their Power Capacity setting in the tools -> preferences pane to "Predictive Power".

 

I'll summarize whats briefly stated on community page: https://community.se.com/t5/ITA-Capacity/About-predicted-power/ta-p/447181

 

The measurement trending view allows the customer to customize how much power history ITA considers when predictive power capacity is calculated as well as how capacity is calculated based on the measurement data and whether the content of a rack has changed.

 

In the measurement trending pane, here are the most important settings:

* Look back is the number of days of power history ITA looks back in the power history for the device. This is data stored on ITA. When set to 90 days, this means ITA is looking back at 90 days of peak power history. The look back period should be set to the number of days the customer feels represents is a reasonable peak power period.. for example if peak power usage is consistent except for one weekend a month, then I'd recommend at least a 30 day look back.

* Min factor and Max factor may be the key to your question. These two values add a multiplier to the measurements used to compute the capacity calculation. Their purpose is to account for fluctations in IT equipment as rack and room content changes. The above community URL tries to explain the scenario in more detail. 

  Min factor is the minimum multiplier applied to the peak power value

  Max factor is the maximum multiplier which can be added to the peak power value.

 

If you want your rack capacity to be solely based on peak power measurements, then you should change both min and max factor to be set to 1.00. This means no min or max factor will be added to the peak measurement when capacity is calculated.

 

I think this may answer your question?

 

There are drawbacks to having a long look-back time. If a power device failure to a rack pdu, pdu, rpp, or UPS were to occur and cause a failover to the alternate side of the power path, then all of the peaks on the alternate side would jump higher. These peaks would remain in the capacity calculations until the look-back period passes.

 

There are also drawbacks to having a look-back which is too short. If the customer sets their look-back to a week, and one weeked per month the customer sees extra high peaks, then for the other three weeks per month the racks may appear to have more free capacity than they should.

 

Regards

 

Greg Sterling

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
gsterling
gsterling Mentor
Mentor

Posted: ‎2026-11-02 04:29 AM

0 Likes
0
97
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-11-02 04:29 AM

Hello jzurera

 

The measurement trending view allows the customer to customize how measurements are treated in ITA. These settings apply customer who have set their Power Capacity setting in the tools -> preferences pane to "Predictive Power".

 

I'll summarize whats briefly stated on community page: https://community.se.com/t5/ITA-Capacity/About-predicted-power/ta-p/447181

 

The measurement trending view allows the customer to customize how much power history ITA considers when predictive power capacity is calculated as well as how capacity is calculated based on the measurement data and whether the content of a rack has changed.

 

In the measurement trending pane, here are the most important settings:

* Look back is the number of days of power history ITA looks back in the power history for the device. This is data stored on ITA. When set to 90 days, this means ITA is looking back at 90 days of peak power history. The look back period should be set to the number of days the customer feels represents is a reasonable peak power period.. for example if peak power usage is consistent except for one weekend a month, then I'd recommend at least a 30 day look back.

* Min factor and Max factor may be the key to your question. These two values add a multiplier to the measurements used to compute the capacity calculation. Their purpose is to account for fluctations in IT equipment as rack and room content changes. The above community URL tries to explain the scenario in more detail. 

  Min factor is the minimum multiplier applied to the peak power value

  Max factor is the maximum multiplier which can be added to the peak power value.

 

If you want your rack capacity to be solely based on peak power measurements, then you should change both min and max factor to be set to 1.00. This means no min or max factor will be added to the peak measurement when capacity is calculated.

 

I think this may answer your question?

 

There are drawbacks to having a long look-back time. If a power device failure to a rack pdu, pdu, rpp, or UPS were to occur and cause a failover to the alternate side of the power path, then all of the peaks on the alternate side would jump higher. These peaks would remain in the capacity calculations until the look-back period passes.

 

There are also drawbacks to having a look-back which is too short. If the customer sets their look-back to a week, and one weeked per month the customer sees extra high peaks, then for the other three weeks per month the racks may appear to have more free capacity than they should.

 

Regards

 

Greg Sterling

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore