Hi team,
We have a facility with ITA 10, where we monitor rack power consumption through sensor mapping. The racks are still empty in terms of equipment, but we can see real-time power consumption through the electrical panel.
The capacity pop-up shows a power value higher than what we’re currently measuring. We’ve noticed that this is related to the Measurement Trending configuration window, but we don’t understand how it works. We’d like the capacity to show the peak value from the last 30 days rather than an estimate—is that possible?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-11-02 04:29 AM
Hello jzurera
The measurement trending view allows the customer to customize how measurements are treated in ITA. These settings apply customer who have set their Power Capacity setting in the tools -> preferences pane to "Predictive Power".
I'll summarize whats briefly stated on community page: https://community.se.com/t5/ITA-Capacity/About-predicted-power/ta-p/447181
The measurement trending view allows the customer to customize how much power history ITA considers when predictive power capacity is calculated as well as how capacity is calculated based on the measurement data and whether the content of a rack has changed.
In the measurement trending pane, here are the most important settings:
* Look back is the number of days of power history ITA looks back in the power history for the device. This is data stored on ITA. When set to 90 days, this means ITA is looking back at 90 days of peak power history. The look back period should be set to the number of days the customer feels represents is a reasonable peak power period.. for example if peak power usage is consistent except for one weekend a month, then I'd recommend at least a 30 day look back.
* Min factor and Max factor may be the key to your question. These two values add a multiplier to the measurements used to compute the capacity calculation. Their purpose is to account for fluctations in IT equipment as rack and room content changes. The above community URL tries to explain the scenario in more detail.
Min factor is the minimum multiplier applied to the peak power value
Max factor is the maximum multiplier which can be added to the peak power value.
If you want your rack capacity to be solely based on peak power measurements, then you should change both min and max factor to be set to 1.00. This means no min or max factor will be added to the peak measurement when capacity is calculated.
I think this may answer your question?
There are drawbacks to having a long look-back time. If a power device failure to a rack pdu, pdu, rpp, or UPS were to occur and cause a failover to the alternate side of the power path, then all of the peaks on the alternate side would jump higher. These peaks would remain in the capacity calculations until the look-back period passes.
There are also drawbacks to having a look-back which is too short. If the customer sets their look-back to a week, and one weeked per month the customer sees extra high peaks, then for the other three weeks per month the racks may appear to have more free capacity than they should.
Regards
Greg Sterling
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-11-02 04:29 AM
Hello jzurera
The measurement trending view allows the customer to customize how measurements are treated in ITA. These settings apply customer who have set their Power Capacity setting in the tools -> preferences pane to "Predictive Power".
I'll summarize whats briefly stated on community page: https://community.se.com/t5/ITA-Capacity/About-predicted-power/ta-p/447181
The measurement trending view allows the customer to customize how much power history ITA considers when predictive power capacity is calculated as well as how capacity is calculated based on the measurement data and whether the content of a rack has changed.
In the measurement trending pane, here are the most important settings:
* Look back is the number of days of power history ITA looks back in the power history for the device. This is data stored on ITA. When set to 90 days, this means ITA is looking back at 90 days of peak power history. The look back period should be set to the number of days the customer feels represents is a reasonable peak power period.. for example if peak power usage is consistent except for one weekend a month, then I'd recommend at least a 30 day look back.
* Min factor and Max factor may be the key to your question. These two values add a multiplier to the measurements used to compute the capacity calculation. Their purpose is to account for fluctations in IT equipment as rack and room content changes. The above community URL tries to explain the scenario in more detail.
Min factor is the minimum multiplier applied to the peak power value
Max factor is the maximum multiplier which can be added to the peak power value.
If you want your rack capacity to be solely based on peak power measurements, then you should change both min and max factor to be set to 1.00. This means no min or max factor will be added to the peak measurement when capacity is calculated.
I think this may answer your question?
There are drawbacks to having a long look-back time. If a power device failure to a rack pdu, pdu, rpp, or UPS were to occur and cause a failover to the alternate side of the power path, then all of the peaks on the alternate side would jump higher. These peaks would remain in the capacity calculations until the look-back period passes.
There are also drawbacks to having a look-back which is too short. If the customer sets their look-back to a week, and one weeked per month the customer sees extra high peaks, then for the other three weeks per month the racks may appear to have more free capacity than they should.
Regards
Greg Sterling