Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Manual Power measurements visualization

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Manual Power measurements visualization
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:34 PM . Last Modified: ‎2024-04-03 02:36 AM

0 Likes
4
1113
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:34 PM . Last Modified: ‎2024-04-03 02:36 AM

Manual Power measurements visualization

Hi Team!

I'm testing Manual Power measurements import feature now.

I have several power panels feeded by main power panel with power measuring devices in my setup.

I want to use manual power measurements feature for panel load visualization.

I've create excel spreadsheet and upload it to DCO.

Now I have measured load on Main panels, but it not reflects on connected power consumers.

Main panel:

 

Connected "child":

 

In the same time, if I connect rPDU to Main panel, imported measured load will be transfered to rPDu level and displayed on the tooltip:

 

I assume it happens because of different consumer types, so the question:

How can I display measured power on "child" power panels if I have measures from Main panel breakers?

Do we have any options to "link" measured values to input breaker of power panel for example?

(CID:143760788)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:34 PM . Last Modified: ‎2024-04-03 02:36 AM

0 Likes
0
1113
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:34 PM . Last Modified: ‎2024-04-03 02:36 AM

Hello Valentin. I assume the measurements you have displayed above represent the totals for the pdu but you also have breaker level power values?

If yes, then you have to look at sensor mapping the breaker sensors to the breaker poles in the panels inside the pdu's. Once the breaker sensors are mapped to the breaker poles, you should see power data downstream on your rack pdu's and so on.

https://sxwhelpcenter.ecostruxureit.com/display/UADCO8x/Configuring+branch+circuit+monitoring

Keep in mind the power overlay on racks and rack pdu's displays power data in watts/Kw not amps so you will want to map your watts/Kw power data if you have that.

Regards

Greg Sterling

(CID:143760914)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:34 PM . Last Modified: ‎2024-04-03 02:36 AM

0 Likes
0
1113
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:34 PM . Last Modified: ‎2024-04-03 02:36 AM

Hi Greg!

I use buit-in transformation according to this article: https://sxwhelpcenter.ecostruxureit.com/display/public/UADCO8x/Importing+manual+power+measurements

So, I fill excel template with values and import it to DCO. It was automatically associated with objects in model and I have measures on breaker level:

In this example I connect power panel (which represent busbar section in my model) to breaker in positions 1-2-3 and rPDU to breaker in positions 4-5-6/

The problem is that measures are not displayed downstream on connected power panel. It's displays fine on rPDU and rack, but not on power panel.

Am I miss something?

(CID:144311016)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:34 PM . Last Modified: ‎2024-04-03 02:36 AM

0 Likes
0
1113
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:34 PM . Last Modified: ‎2024-04-03 02:36 AM

No, I think you are correct in that case. The downstream power should be visible on rack pdu's but I do not think it will display on downstream power devices.

Regards

Greg Sterling

(CID:144867763)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:35 PM . Last Modified: ‎2023-10-22 03:00 AM

0 Likes
0
1113
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:35 PM . Last Modified: ‎2023-10-22 03:00 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore