Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Issues monitoring Vertiv fleet in DCE 7.8

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Re: Issues monitoring Vertiv fleet in DCE 7.8
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
4jp
4jp
Explorer

Posted: ‎2023-05-24 02:00 PM . Last Modified: ‎2023-05-24 02:02 PM

0 Likes
4
3593
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-24 02:00 PM . Last Modified: ‎2023-05-24 02:02 PM

Issues monitoring Vertiv fleet in DCE 7.8

We have a fleet of 60-70 Vertiv UPS's of varying models, mostly GXT4's but also some GXT6's with IS-UNITY-DP cards in them that we use over SNMPv3. Most of the Unity cards are on FW 8.0.3.0

 

Basically, some of our UPS's are showing up fine in DCE and all sensors are live, while other seemingly identical ones show up as having a communications lost error and all of the sensors show as disconnected.

 

For example in one comm room we have 2 identical GXT4s with the same line card, on the same firmware level, connected to the same edge router, and as far as I can tell have identical configurations but one of them has been in a "communications failure" since last month. 

 

We have:

  • Tested upgrading firmware to 8.2.3 on a known working one. This caused the UPS to go into a "communications failure" state and sit there since then
  • Compared port / VLAN configurations between known working / not working ones, and they are often identical
  • Tried the usual troubleshooting through DCE itself like entering / exiting maintenance mode, and requesting device scans
  • Loaded an up to date Liebert DDF provided from the Ecostruxure folks with no change
  • Downloaded and manually compared the config files on select few machines and they are identical (disregarding IP/MAC)
  • Rebooted / reseated the line cards. The webGUI always works on these devices

 

I was also able to complete SNMPv3 walks from both the DCE server itself and from my PC offsite. Pings / tracerts complete fine. SNMP packets are not being blackholed I'm told

 

Any advice on what to do here? Are there any more logs I can look at that might be helpful? I am pretty much at a loss now. APC support was of no help because "these are not APC devices".....

 

 
Labels
  • Labels:
  • Data Center Expert
  • Tags:
  • dce
  • english
  • vertiv
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
brucep26b
brucep26b
Contributor

Posted: ‎2023-05-24 02:53 PM

0 Likes
1
3583
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-24 02:53 PM

I know you shouldn't have to do these things however. What happens when you

Delete device from DCE and add it again?

Factory reset the Webcard and configure?

Swap Webcard for one UPS to another(if possible) does problem follow the card?

Reply

Link copied. Please paste this link to share this article on your social media post.

Shaun
Shaun Leader
Leader

Posted: ‎2023-05-24 07:40 PM

0 Likes
1
3568
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-24 07:40 PM

Hi @4jp,

 

This should be supported as long as the DCE is under a support agreement.  Multi-vendor support is right there in the brochure, so we'll live up to that where we can (eg if the root cause is ours).  If you want to DM me a ticket number, or try again with your local support and point to this if needed, we should be able to help further.

 

Usually my go-to for issues like this is packet captures, which really needs to go through support rather than posting them on a public forum.  But a few easy things we can test, which can help nail down some v3-specific issues:

 

  • Does rebooting the DCE restore communication with affected devices?
  • Does rebooting/restarting an 8.0.3.0 device cause it to go lost-comm?
  • Does rebooting/restarting an 8.2.3 device cause it to go lost-comm? (assuming the reboot restored comm in the first place)
  • Have device credentials changed during this upgrade process?
  • Is it possible to test whether SNMPv1 works when v3 doesn't

Thanks,

  Shaun

Reply

Link copied. Please paste this link to share this article on your social media post.

4jp
4jp
Explorer

Posted: ‎2023-05-25 06:56 AM

In response to brucep26b
0 Likes
0
3552
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-25 06:56 AM

I have not tried to delete / re-add the devices yet but that would be a next step. I can get one of our techs to swap the line cards around (and pray it doesn't bork them both). 

Reply

Link copied. Please paste this link to share this article on your social media post.

4jp
4jp
Explorer

Posted: ‎2023-05-25 07:33 AM

In response to Shaun
0 Likes
0
3550
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-25 07:33 AM

Would there be a more appropriate support route I could try then? The ticket I had with EcoStruxure support, they recommended I call the APC support number and that's the route I tried. 

 

I can reboot devices but there is typically no change. The 8.2.3 devices we have tried upgrading seem to stay in the lost communications state no matter if I reboot them or manually try to scan them

 

If I reboot / maintenance mode a 8.0.3 device, it usually will show comms lost, then when it reboots, it comes back online as expected

 

However, I just tried that again on a machine I haven't previously touched and I never could get DCE to communicate with it again. I am now trying to remove it / re-add it and I'll see what happens. I can get a tech to swap / reseat the linecards failing that

 

SNMPv1 isn't really an option long term because our security folks frown upon it i'm told... I'd have to investigate that further, though, it might be an option for testing

 

No, device credentials should not have changed. Unfortunately I am also pretty new to struxureware, and I did not engineer our environment.. I just administer it for now

 

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore