Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Is there a way to update excell cell on a regular basis according to a particular data in DCE?

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Is there a way to update excell cell on a regular basis according to a particular data in DCE?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
160
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 03:51 PM . Last Modified: ‎2024-04-05 12:26 AM

0 Likes
4
1743
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:51 PM . Last Modified: ‎2024-04-05 12:26 AM

Is there a way to update excell cell on a regular basis according to a particular data in DCE?

I want DCE to update total power in an excel cell in my excel table? Is it possible?

(CID:129412706)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 03:51 PM . Last Modified: ‎2024-04-05 12:26 AM

0 Likes
2
1743
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:51 PM . Last Modified: ‎2024-04-05 12:26 AM

Hi Ibrahim.

 

DCE can post reports to a windows server or to an FTP server. It does not post .xls or any other Excel specific formatted files, it can post delimited text files which can be opened in Excel.

 

If you want to update an existing file on your computer, you'll need to poll the device directly using SNMP and edit the Excel file yourself. You can also poll the DCE server using the web API and again update your file using your code. The third option is to use the report export feature and again create your own code to pull data from that file and update your Excel file.

 

Thanks,

Steve.

(CID:129412879)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 03:51 PM . Last Modified: ‎2024-04-05 12:26 AM

0 Likes
2
1744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:51 PM . Last Modified: ‎2024-04-05 12:26 AM

Hi Ibrahim.

 

DCE can post reports to a windows server or to an FTP server. It does not post .xls or any other Excel specific formatted files, it can post delimited text files which can be opened in Excel.

 

If you want to update an existing file on your computer, you'll need to poll the device directly using SNMP and edit the Excel file yourself. You can also poll the DCE server using the web API and again update your file using your code. The third option is to use the report export feature and again create your own code to pull data from that file and update your Excel file.

 

Thanks,

Steve.

(CID:129412879)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 03:51 PM . Last Modified: ‎2024-04-05 12:26 AM

In response to DCIM_Support
0 Likes
0
1743
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:51 PM . Last Modified: ‎2024-04-05 12:26 AM

Thanks for your help.Can DCE automatically export reports in somewhere my computer.For example,I want DCE to export zone 1 temperatures everyday in excel format.Is it possible?

(CID:130096552)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 03:52 PM . Last Modified: ‎2024-04-05 12:26 AM

In response to DCIM_Support
0 Likes
0
1743
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:52 PM . Last Modified: ‎2024-04-05 12:26 AM

Hi Ibrahim,

 

Not exactly. First you have to create a report. Choose the reports perspective, temperature, and generate report:

 

Choose a relative range such as the last 24 hours and a summary or table format depending on what exactly you're looking for. Choose the device group(s) and the specific sensors you're looking for:

If you're looking for one day's data, always use relative range as if you choose a specific date, that date's data will always be reported. Run the report and once you've verified it's what you want to see, save that report:

 

If you now go to reports–>manage export scheduling:

 

you can see the report you just made:

Choose export action configuration.

Here you can add an export such as a windows export.

Once finished creating the export type, select the report and edit the criteria:

Enable the export. Choose the export you created in the previous step, (no Excel option) choose the appropriate delimiter choose a locale, and schedule it for a specific day or all days.

 

K-base FA301697 can be helpful here as well as the system's on-line help files.

 

Thanks,

Steve

 

 

(CID:130096787)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 03:52 PM . Last Modified: ‎2023-10-22 02:50 AM

0 Likes
0
1743
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:52 PM . Last Modified: ‎2023-10-22 02:50 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore