Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Is it possible to manage alarm configurations for Netbotz 450s in DCE?

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Is it possible to manage alarm configurations for Netbotz 450s in DCE?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 06:31 PM . Last Modified: ‎2024-04-04 11:30 PM

0 Likes
2
1494
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 06:31 PM . Last Modified: ‎2024-04-04 11:30 PM

Is it possible to manage alarm configurations for Netbotz 450s in DCE?

I notice they do not show up in the "Alarm configuration" tab of DCE, but a NB 200 does. Not a big deal , just wondered why they don't show up there.

(CID:132647794)

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 06:31 PM . Last Modified: ‎2024-04-04 11:30 PM

0 Likes
0
1494
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 06:31 PM . Last Modified: ‎2024-04-04 11:30 PM

Hi Justin,

 

The short answer is no. You can't configure NetBotz 3xx, 4xx, and 5xx through the alarm configuration tab.

 

Now the long answer. The NetBotz 200 and 250s are based on the same platform as the APC network management cards. They can only speak to DCE using SNMP. They can also be configured as the NMC is by using it's config.ini or configuration file. Data is passed between the systems using SNMP. Alerting through DCE is also done based on SNMP

 

The NetBotz 3xx, 4xx, and 5xx use HTTP post or HTTP get for all communications with DCE. DCE configures the NetBotz appliance and communicates data using this method. This communications method was created way back when it was NetBotz central. At that time, the intelligence at the "edge" was felt to be more important. This way if DCE went down, the NetBotz would still do all their own alerting. That NetBotz Central functionality, although updated quite a bit, is still the basis for the communications and alerting between DCE and NetBotz.

 

DCE won't alert for the NetBotz like it does for the SNMP devices. You can either go directly to the NetBotz appliance to configure it's alert functionality or you can use the menues shown here:

You can create thresholds, Alert actions, and alert profiles through this option.

 

Thanks,

Steve

 

(CID:132647801)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 06:31 PM . Last Modified: ‎2024-04-04 11:30 PM

0 Likes
0
1495
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 06:31 PM . Last Modified: ‎2024-04-04 11:30 PM

Hi Justin,

 

The short answer is no. You can't configure NetBotz 3xx, 4xx, and 5xx through the alarm configuration tab.

 

Now the long answer. The NetBotz 200 and 250s are based on the same platform as the APC network management cards. They can only speak to DCE using SNMP. They can also be configured as the NMC is by using it's config.ini or configuration file. Data is passed between the systems using SNMP. Alerting through DCE is also done based on SNMP

 

The NetBotz 3xx, 4xx, and 5xx use HTTP post or HTTP get for all communications with DCE. DCE configures the NetBotz appliance and communicates data using this method. This communications method was created way back when it was NetBotz central. At that time, the intelligence at the "edge" was felt to be more important. This way if DCE went down, the NetBotz would still do all their own alerting. That NetBotz Central functionality, although updated quite a bit, is still the basis for the communications and alerting between DCE and NetBotz.

 

DCE won't alert for the NetBotz like it does for the SNMP devices. You can either go directly to the NetBotz appliance to configure it's alert functionality or you can use the menues shown here:

You can create thresholds, Alert actions, and alert profiles through this option.

 

Thanks,

Steve

 

(CID:132647801)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 06:32 PM . Last Modified: ‎2023-10-22 02:49 AM

0 Likes
0
1494
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 06:32 PM . Last Modified: ‎2023-10-22 02:49 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore