Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ITE Event Notifications

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • ITE Event Notifications
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ IT Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
00071491
00071491
Explorer

Posted: ‎2026-04-14 07:27 AM

0 Likes
4
630
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-04-14 07:27 AM

ITE Event Notifications

Hello,

 

We've just onboarded to IT Expert and have added 30 UPS devices.  Previously, we were configuring each devices individually and setting event action notifications through the web GUI via Configuration > Notification > Event Actions > By Group (Screenshots).

00071491_0-1776176278182.png

00071491_1-1776176641494.png

 

We'd like to disable all e-mail notifications from the local device and rely solely on ITE to send out Warning and Critical e-mail notices.  At this time, we no longer wish to receive Informational events.  How can we accomplish this in ITE without having to manually log into each UPS device to disable it?  Are there any other recommendations you think we'd benefit from?

 

 

Labels
  • Labels:
  • IT Expert
  • Tags:
  • english
  • events
  • notifications
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
G_Kemp
G_Kemp
Contributor

Posted: ‎2026-04-16 06:13 AM

1 Like
0
593
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-04-16 06:13 AM

You can either use a config.ini file with only the changes you want to make (ex: email=disabled) along with the iniutil.exe with the list of devices and push.  Or in ITE go to Device Configuration, 1. select a device to use as template, 2. make the change(s) you want (search for email), 3. select target devices, 4. review and apply,

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
G_Kemp
G_Kemp
Contributor

Posted: ‎2026-04-16 06:13 AM

1 Like
0
594
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-04-16 06:13 AM

You can either use a config.ini file with only the changes you want to make (ex: email=disabled) along with the iniutil.exe with the list of devices and push.  Or in ITE go to Device Configuration, 1. select a device to use as template, 2. make the change(s) you want (search for email), 3. select target devices, 4. review and apply,

Reply

Link copied. Please paste this link to share this article on your social media post.

VSales
VSales Contributor
Contributor

Posted: ‎2026-04-16 01:01 PM

0 Likes
0
599
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-04-16 01:01 PM

 

Hello 00071491,

Yes, you can leverage IT Expert to perform a mass configuration push across your devices to disable all device-level notifications. We have both a step-by-step article and a video tutorial that walk through this process in detail. You can access them using the link below:

https://community.se.com/t5/Device-configuration/Video-Device-configuration/ta-p/446970

As an added benefit, using IT Expert as your primary notification engine gives you greater control over alerting. You can define what is considered critical versus warning based on your business priorities and operational requirements. This is achieved through severity policies, which allow you to tailor notifications to what matters most to your organization. The following article will help you get started with configuring these policies:

https://community.se.com/t5/ITE-Configuration/Create-an-alarm-severity-policy-in-IT-Expert/ta-p/4502...

As always, our Customer Success Managers and Support teams are available to assist you throughout this process.

Thank you,
Victor

Reply

Link copied. Please paste this link to share this article on your social media post.

00071491
00071491
Explorer

Posted: ‎2026-04-17 06:19 AM

0 Likes
1
545
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-04-17 06:19 AM

Thank you, both for the replies.  I'm not yet familiar with the config.ini process but I did end up changing the SMTP server to a fake address for the time being.  All devices showed successful, but we still had a handful that were still e-mailing.  Manually logging into those devices show the fake server address, but somehow e-mails were still being sent.  We removed the recipient on those few and now appear to be fine.  I'll take a look at the links as well.

Reply

Link copied. Please paste this link to share this article on your social media post.

G_Kemp
G_Kemp
Contributor

Posted: ‎2026-04-20 12:27 PM

In response to 00071491
0 Likes
0
530
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-04-20 12:27 PM

Great information here for using the iniutil and how to configure.  While the GUI is great, there are certain things that are easier to adjust or modify with a config.ini file, especially if you have dozens or hundreds to do. 

How can I mass configure a Network Management Card (NMC) or NMC embedded product?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore