Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ITA failed restore

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Re: ITA failed restore
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:33 AM . Last Modified: ‎2024-04-02 11:31 PM

0 Likes
5
1546
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:33 AM . Last Modified: ‎2024-04-02 11:31 PM

ITA failed restore

I was trying to restore my ITA system from my DCO backup, it failed, it worked for me before though. Blow is a snippet of error messages from platform log. I confirm the backup image is good. 

 

03/01/20 11:25:51 ERROR Operations::OperationsLib::warnHandler Use of uninitialized value $host in concatenation (.) or string at /usr/sha
re/perl5/vendor_perl/Operations/ClusterManager.pm line 680.
at /usr/share/perl5/vendor_perl/Operations/ClusterManager.pm line 680.
Operations::ClusterManager::waitForOperationShutdown('Operations::ClusterManager') called at /usr/share/perl5/vendor_perl/Operatio
ns/BackupManager.pm line 589
Operations::BackupManager::stopOperation('Operations::BackupManager') called at /usr/share/perl5/vendor_perl/Operations/BackupMana
ger.pm line 395
Operations::BackupManager::doRestore('Operations::BackupManager', '/tmp/Final_EMEA_2019_7_10_Room_Power_2019-07-10_16.58.tar.gz')
called at /sbin/Platform.pm line 283

03/01/20 11:25:51 INFO Operations::ClusterManager::waitForOperationShutdown Waiting for Operation to shut down on host: for 300 s
03/01/20 11:25:52 INFO Operations::ClusterManager::waitForOperationShutdown .
03/01/20 11:25:52 ERROR Operations::OperationsLib::dieHandler Expected 'PeerHost' at /usr/share/perl5/vendor_perl/Operations/OperationsLib
.pm line 2318.
at /usr/share/perl5/vendor_perl/IO/Socket/IP.pm line 454.
IO::Socket::IP::_configure('IO::Socket::SSL=GLOB(0x41a04c8)', 'HASH(0x2512c30)') called at /usr/share/perl5/vendor_perl/IO/Socket/
IP.pm line 370
IO::Socket::IP::configure('IO::Socket::SSL=GLOB(0x41a04c8)', 'HASH(0x2512c30)') called at /usr/share/perl5/vendor_perl/IO/Socket/S
SL.pm line 279
IO::Socket::SSL::configure('IO::Socket::SSL=GLOB(0x41a04c8)', 'HASH(0x2512c30)') called at /usr/lib64/perl5/IO/Socket.pm line 49
IO::Socket::new('IO::Socket::SSL', 'Proto', 'tcp', 'SSL_cert_file', '/etc/isx-operations/ssl/certificate.crt', 'SSL_key_file', '/e
tc/isx-operations/ssl/certificate.key', 'PeerPort', 'https', ...) called at /usr/share/perl5/vendor_perl/IO/Socket/IP.pm line 337
IO::Socket::IP::new('IO::Socket::SSL', 'PeerAddr', undef, 'PeerPort', 'https', 'Proto', 'tcp', 'Timeout', 1, ...) called at /usr/s
hare/perl5/vendor_perl/Operations/OperationsLib.pm line 2318
Operations::OperationsLib::getHttpsContent('Operations::OperationsLib=HASH(0x2529d78)', undef, '/clients/alive', 1, undef) called
at /usr/share/perl5/vendor_perl/Operations/ClusterManager.pm line 492
Operations::ClusterManager::isWebsiteRunning('Operations::ClusterManager', undef, '/clients/alive') called at /usr/share/perl5/ven
dor_perl/Operations/ClusterManager.pm line 576
Operations::ClusterManager::jbossCli('Operations::ClusterManager', undef, '?operation=attribute&name=server-state') called at /usr
/share/perl5/vendor_perl/Operations/ClusterManager.pm line 557
Operations::ClusterManager::isOperationRunning('Operations::ClusterManager', undef) called at /usr/share/perl5/vendor_perl/Operati
ons/ClusterManager.pm line 688
Operations::ClusterManager::waitForOperationShutdown('Operations::ClusterManager') called at /usr/share/perl5/vendor_perl/Operatio
ns/BackupManager.pm line 589
Operations::BackupManager::stopOperation('Operations::BackupManager') called at /usr/share/perl5/vendor_perl/Operations/BackupMana
ger.pm line 395
Operations::BackupManager::doRestore('Operations::BackupManager', '/tmp/Final_EMEA_2019_7_10_Room_Power_2019-07-10_16.58.tar.gz')
called at /sbin/Platform.pm line 283

(CID:153551022)

Labels
  • Labels:
  • IT Advisor
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:33 AM . Last Modified: ‎2024-04-02 11:31 PM

0 Likes
0
1546
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:33 AM . Last Modified: ‎2024-04-02 11:31 PM

Hi Yilai,

Apparently timeout expired waiting for operation to shut down (300 s). Can I ask for the complete server logs + the used backup file (via your shared site), so I can take a look.

I was wondering if rebooting the server and then restoring the backup file could have helped?

Kind regards

(CID:153551150)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:33 AM . Last Modified: ‎2024-04-02 11:31 PM

0 Likes
0
1546
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:33 AM . Last Modified: ‎2024-04-02 11:31 PM

Hi Jef, 

I tried your suggestion to reboot the system, but I forgot to change the parameter of our auto config system - the ITA packages got downgraded back to DCO. However, the log remains, and shouldn't affect our troubleshooting. I collected the platform and server log from OS, and zipped with the backup that was used, named as "ITA_restore_issue.zip". 

Thanks

(CID:153551329)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:33 AM . Last Modified: ‎2024-04-02 11:31 PM

0 Likes
0
1546
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:33 AM . Last Modified: ‎2024-04-02 11:31 PM

Thank Yilai,

I will get back to you asap,

Kind regards

(CID:153551606)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:33 AM . Last Modified: ‎2024-04-02 11:31 PM

0 Likes
0
1546
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:33 AM . Last Modified: ‎2024-04-02 11:31 PM

Hi Yilai,

Thanks again for providing the data.

I have tested restoring the provided backup file on my ITA 9.0.4 without any problem.

However, according to the provided log files, it seems the "Operations" is unable to shutdown, and therefore the restore job could not be continued (and fails). This might be code related issue, that may need to be investigated. I have therefore created a backlog for code investigations (based on your log entries).

Kind regards

(CID:153551732)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:33 AM . Last Modified: ‎2023-10-22 02:41 AM

0 Likes
0
1546
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:33 AM . Last Modified: ‎2023-10-22 02:41 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.