Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ITA Estimated Power summary

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Re: ITA Estimated Power summary
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
160
Jef
Jef Leader
114
gsterling
gsterling Mentor
79
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
NF-London
NF-London
Explorer

Posted: ‎2021-06-02 08:05 AM

0 Likes
4
2576
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-02 08:05 AM

ITA Estimated Power summary

Hi,

 

In the web client of ITA there is a power summary figure for each location of used/total power.  A user is asking me the source of these figures.  I cannot seem to reconcile these figures with my site figures though.  Sometimes it is almost exactly double the estimated load when totalled from each rack but in other cases it is not.

 

Mitigating factors:

 

  • These particular sites I am interested in did not have the rack equipment attached to the PDU's in the rack.
  • Most if not all the racked equipment is set to DN+1 for power redundancy, where kit has 2 PSU's connected to the 2 PDU's.
  • These locations contain racks monitored by intelligent PDU's via DCE (7.6).
  • The setting in ITA is set to "Predictive Power" - this has not changed.

 

  ITA Summary kWtotal of peak kW from DCE (30 day measured)estimated load in ITA web client (each rack EST LOAD totalled)
LOCATIONA2911.714.63
LOCATIONB157.57.72
LOCATIONC1810.314.46
LOCATIOND213418.62
LOCATIONE1910.714.87
LOCATIONF332730.45
LOCATIONG197-98.5

 

I need to help the user understand the basis of the summary figures and how they are calculated.

Labels
  • Labels:
  • IT Advisor
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Jef
Jef Leader
Leader

Posted: ‎2021-06-04 06:03 AM

In response to NF-London
0 Likes
1
2528
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-04 06:03 AM

Hi Nigel,

 

The utilized power is the sum of the equipment power consumption (equipment adjusted nameplate value). However, in the power calculations we need also include the equipment redundancy requirement/settings, for example for N+1 or 2N redundancy we need to multiply the power consumption by 2.

 

Kind regards,

Jef

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Jef
Jef Leader
Leader

Posted: ‎2021-06-03 12:25 AM

0 Likes
3
2564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-03 12:25 AM

Hi Nigel,

Power kpi’s displayed in the web client is basically the locations UPS power capacity and its utilized power.

In my example the utilized power is 68 kW and the total power is 800 kW:
Capture-jf.JPG

Kind regards,

Jef

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

NF-London
NF-London
Explorer

Posted: ‎2021-06-03 02:28 AM

In response to Jef
0 Likes
2
2550
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-03 02:28 AM

Yes it is these figures you have highlighted that I want to understand.  Where is the utilised power from?  How is it calculated?

 

In my table the first column has these summary figures from ITA web client but I cannot understand how they differ between the sites in relation to the 2nd and third columns of measured load and the totals of estimated loads from each rack in ITA.  Surely there must be some consistency?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Jef
Jef Leader
Leader

Posted: ‎2021-06-04 06:03 AM

In response to NF-London
0 Likes
1
2528
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-04 06:03 AM

Hi Nigel,

 

The utilized power is the sum of the equipment power consumption (equipment adjusted nameplate value). However, in the power calculations we need also include the equipment redundancy requirement/settings, for example for N+1 or 2N redundancy we need to multiply the power consumption by 2.

 

Kind regards,

Jef

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

NF-London
NF-London
Explorer

Posted: ‎2021-06-10 07:19 AM

In response to Jef
0 Likes
0
2505
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-10 07:19 AM

Thanks Jef.

 

I have been experimenting with changing the redundancy on devices installed.  Clearly it makes a difference to the ITA web client summary of utilized power.  I would prefer clearer notes on this as all the documentation I have read only refers to the upstream UPS supply and not the redundancy of the asset itself which is what is being chosen.

 

Nigel

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore