Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ISX Backup

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • ISX Backup
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 05:51 PM . Last Modified: ‎2024-04-04 11:46 PM

0 Likes
4
1534
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:51 PM . Last Modified: ‎2024-04-04 11:46 PM

ISX Backup

Dear Team,

I want to take backup of isx to my DR (Disaster Recovery) site. Please do let me know its requirement and procedure.

BR 

(CID:131962935)

Labels
  • Labels:
  • Data Center Expert
  • Data Center Operation
  • IT Advisor
  • Portal
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 05:51 PM . Last Modified: ‎2024-04-04 11:46 PM

0 Likes
1
1534
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:51 PM . Last Modified: ‎2024-04-04 11:46 PM

Hi Muhammad,

 

If your question is about how to do a backup, the documentation or spezialist 's answer should suffice. If you're looking for information about taking a backup from one server and putting it on another, there may be complications. If you're using a virtual version of DCE, you'll want to make sure that your disaster recovery version has the same resources as the main server. You'll want to make sure that this server has access to the same devices the primary server has for ports, SNMP access on the devices, etc. 

Please also note that the DCE license keys are tied to the mac address. If your disaster recovery system is another VM, you may want to create it with the same mac. If you can't or you're using 2 hardware servers, you'll need a second set of license keys. Your local tech support should be able to assist you with this as long as you have valid support contracts for both servers and keys for both systems.

 

Please note that according to another recent post from you, it appears that you're running version 7.0. That version is no longer officially supported and it is strongly recommended that you upgrade to the current 7.5.


Steve

(CID:131963146)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 05:51 PM . Last Modified: ‎2024-04-04 11:46 PM

0 Likes
0
1534
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:51 PM . Last Modified: ‎2024-04-04 11:46 PM

Dear Muhammad Shahzad,

I guess it's only about DCE software (early ISX Central)?

If so, then briefly, according to the web-page Server Backup/Restore, DCE software can perform three types of backup:

  • Full: all server data (configuration and repository) will be saved in every backup file.
  • Synchronized: only changes to server data (configuration and repository) will be saved after the initial backup file.
  • Configuration: only server configuration data will be saved in every backup file.

Backup can be performed on two types of repositories: Windows or NFS. In addition, the backup can be performed automatically in the scheduler or in the manual mode.

Additionally, a good video instruction can be found at link Configuring a Windows Share Backup of StruxureWare Data Center Expert.

I hope this is what you need.

If there are more questions, please ask.

With respect.

 

(CID:131963033)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 05:51 PM . Last Modified: ‎2024-04-04 11:46 PM

0 Likes
1
1535
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:51 PM . Last Modified: ‎2024-04-04 11:46 PM

Hi Muhammad,

 

If your question is about how to do a backup, the documentation or spezialist 's answer should suffice. If you're looking for information about taking a backup from one server and putting it on another, there may be complications. If you're using a virtual version of DCE, you'll want to make sure that your disaster recovery version has the same resources as the main server. You'll want to make sure that this server has access to the same devices the primary server has for ports, SNMP access on the devices, etc. 

Please also note that the DCE license keys are tied to the mac address. If your disaster recovery system is another VM, you may want to create it with the same mac. If you can't or you're using 2 hardware servers, you'll need a second set of license keys. Your local tech support should be able to assist you with this as long as you have valid support contracts for both servers and keys for both systems.

 

Please note that according to another recent post from you, it appears that you're running version 7.0. That version is no longer officially supported and it is strongly recommended that you upgrade to the current 7.5.


Steve

(CID:131963146)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 05:51 PM . Last Modified: ‎2024-04-04 11:46 PM

In response to DCIM_Support
0 Likes
0
1534
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:51 PM . Last Modified: ‎2024-04-04 11:46 PM

Thanks alot for your usual spport

(CID:131966110)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 05:52 PM . Last Modified: ‎2023-10-22 02:39 AM

0 Likes
0
1534
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:52 PM . Last Modified: ‎2023-10-22 02:39 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore