Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

How to read temperature from AP8881 (APC PDU) in DCE?

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • How to read temperature from AP8881 (APC PDU) in DCE?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 11:05 PM . Last Modified: ‎2024-04-03 12:15 AM

0 Likes
8
2636
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 11:05 PM . Last Modified: ‎2024-04-03 12:15 AM

How to read temperature from AP8881 (APC PDU) in DCE?

I use a DCE 7.2 version, and last time we bought new APC PDU AP8881 with temperature sensors (AP9335T). I can read a temperature when I connect by a WEB browser, but when I add this PDU to the DCE server I can't read a temperature.

What I must to do to read a temperature in DCE?

(CID:150733096)

Labels
  • Labels:
  • Data Center Expert
  • DDF
  • NetBotz
  • Tags:
  • bug
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 11:05 PM . Last Modified: ‎2024-04-03 12:15 AM

0 Likes
0
2634
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 11:05 PM . Last Modified: ‎2024-04-03 12:15 AM

Dear Zenon Ruta,

This is very strange, since everything should work by default, i.e. as soon as you make a discovering above the indicated =SE= rPDU with the climate sensor in DCE software, you should see its readings (temperature (and humidity, for AP9335TH). This should work even if you have a very outdated version of DCE-7.2 (the latest is DCE-7.7.1).

Can we know the firmware versions on your rPDU, as well as see screenshots from the rPDU web-GUI and from the DCE-client?

With respect.

(CID:150733112)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 11:05 PM . Last Modified: ‎2024-04-03 12:15 AM

0 Likes
3
2634
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 11:05 PM . Last Modified: ‎2024-04-03 12:15 AM

Hi Zenon,

it’s likely just due to 7.2 and it’s older DDF files. The first thing I’d suggest is backing up the server and contacting support to get upgrades.  If you don’t want to upgrade just now, you can go to DCEs SNMP device menu and on the DDF tab, there is an option to have DCE connect to the web and download the latest DDF files. 

thanks,

Steve.  

(CID:150733120)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 11:05 PM . Last Modified: ‎2024-04-03 12:15 AM

In response to DCIM_Support
0 Likes
0
2634
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 11:05 PM . Last Modified: ‎2024-04-03 12:15 AM

Thanks, but unfortunately, our DCE system can not establish connection outside the internal network (network security).

How can I download a DDF file for new PDU AP8881?

 

Best Regards

(CID:150733219)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 11:05 PM . Last Modified: ‎2024-04-03 12:15 AM

In response to DCIM_Support
0 Likes
0
2634
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 11:05 PM . Last Modified: ‎2024-04-03 12:15 AM

Hi,

At the top of this page, you should see a "DDF" link. You can probably find the APC PDU DDF there but others may be required. You can usually get the file here too but something seems broken at the moment:

https://sxwhelpcenter.ecostruxureit.com/display/download/DCE+device+firmware+catalog

 

Again, I suggest getting up to date with the version of DCE to avoid other issues.


Steve

(CID:151060568)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 11:05 PM . Last Modified: ‎2024-04-03 12:15 AM

In response to DCIM_Support
0 Likes
0
2634
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 11:05 PM . Last Modified: ‎2024-04-03 12:15 AM

Thank 😀

I will be trying.

 

Zenon

(CID:151060577)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 11:05 PM . Last Modified: ‎2024-04-03 12:14 AM

0 Likes
0
2634
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 11:05 PM . Last Modified: ‎2024-04-03 12:14 AM

DCE Ve 7.2 was released bak in August 2012 (note that when temperature probe connected rPDUs' did not exist).  As such, my first thing to check would be the Device Definition File (DDF), as per Steve's note below.   Here is also a link to the release notes, of which alot of them are around cybersecurity updates that are included in subsequent DCE release updates.

https://sxwhelpcenter.ecostruxureit.com/display/public/UADCE725/StruxureWare+Data+Center+Expert+Rele...

(CID:150733128)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 11:06 PM . Last Modified: ‎2024-04-03 12:14 AM

0 Likes
0
2634
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 11:06 PM . Last Modified: ‎2024-04-03 12:14 AM

Dear Warren Robb,

From your comments:

DCE Ve 7.2 was released bak in August 2012 (note that when temperature probe connected rPDUs' did not exist)...

I must refute, as this is incorrect information. Back in 2011, our data center was equipped with a large number of rPDU2G AP8881 with the firmware v.5.x.x and sensors AP9335T(H). Even then, we used the DCE software solution in which the temperature and humidity of the sensors, that were connected to the above rPDUs, were successfully displayed.

Therefore, I can say for sure, that Zenon Ruta problem is that he uses an outdated version of DCE software along with rPDU 2G AP8881 with the latest firmware v.6.x.x. Thus, the normal solution to this problem is to use the latest version of DCE software, which I wrote about in my answer.

With respect.

(CID:151062270)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 11:06 PM . Last Modified: ‎2023-10-22 02:33 AM

0 Likes
0
2634
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 11:06 PM . Last Modified: ‎2023-10-22 02:33 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore