Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

How to model the iBathway in DCO

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • How to model the iBathway in DCO
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 05:21 PM . Last Modified: ‎2024-04-03 03:23 AM

0 Likes
3
1392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 05:21 PM . Last Modified: ‎2024-04-03 03:23 AM

How to model the iBathway in DCO

Hi,

 

I have multiple iBathway canalis lines (from Schneider Electric), each line/iBathway is installed above each row inside the data center, and each line/iBathway consists of the below:

1- PowerLogic PM 5310 >> inside the feeding box at beginning of the each line (feeding each line/iBathway).

2- Energy meters iEM3155 >> inside the feeding boxes along the line/iBathway and above each APC rack (feeding APC racks).

 

Now, i need to ask how to model and associate them in DCO, i mean how to draw the line/iBathway and how to create the power path.

Note: there is no genomes for the above two models.

 

Thanks for advance for quick response.

 

 

(CID:140219332)

Labels
  • Labels:
  • Data Center Operation
  • Genome
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 05:21 PM . Last Modified: ‎2024-04-03 03:23 AM

0 Likes
1
1392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 05:21 PM . Last Modified: ‎2024-04-03 03:23 AM

Hello Momen.

Currently busbars or overhead busways are not supported in DCO as a device modeled above the racks. I have seen customers take a floor pdu and make it thin, and stretch it out the length of a row (for example) and then use a panel inside to model the rack connections.

It may then be possible to model the measured data ... but that part I'd have to test as I know multiple BCM devices can be associated to a PDU device but I'm not 100% certain whether multiple power meters can be.

The ability to model busbar like devices is on the feature roadmap so you can expect to see feature improvements in this area in a future release.

Regards

Greg Sterling

(CID:140710941)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 05:21 PM . Last Modified: ‎2024-04-03 03:23 AM

In response to DCIM_Support
0 Likes
0
1392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 05:21 PM . Last Modified: ‎2024-04-03 03:23 AM

Hi Greg,

Following your reply and your suggestion above:

Kindly i need to ask how to model the power meter 5310 and the Energy meter iEM3155 in the DCO.

As the PM5310 and iEM3155 don't have genomes in DCO, and when i associate them to generic panel breakers i don't get the readings.

 

So please i need to know how to get data from the PM5310 and iEM3155 into DCO.

(CID:140710943)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 05:21 PM . Last Modified: ‎2023-10-22 02:32 AM

0 Likes
0
1392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 05:21 PM . Last Modified: ‎2023-10-22 02:32 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore