Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

How to disable support for 3DES suite through dev Firewall?

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • How to disable support for 3DES suite through dev Firewall?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 03:55 PM . Last Modified: ‎2024-04-05 12:25 AM

0 Likes
6
2873
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:55 PM . Last Modified: ‎2024-04-05 12:25 AM

How to disable support for 3DES suite through dev Firewall?

Hello,
Our security scan has found the following vulnerability with our all APC AP8888 devices
***TLS/SSL Birthday attacks on 64-bit block ciphers (SWEET32)***
Is there any firewall rule that I can create in the device through the GUI under security >>firewall options to disable 3DES cipher suite? So that we can provide mitigation to this vulnerability?
Thanks in advance for any information you may provide.

(CID:129413129)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 03:55 PM . Last Modified: ‎2024-04-05 12:25 AM

0 Likes
0
2873
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:55 PM . Last Modified: ‎2024-04-05 12:25 AM

Dear Cristian Arias Lopez,

Please clarify:

  • What version of firmware on your AP8888 is used?
  • On your AP8888 devices the HTTP protocol (80 port) is disabled and only the HTTPS protocol (443 port) is enabled (or not)?
  • What is the minimum supported encryption method used on your AP8888 devices (SSLv3, TLSv1, TLSv1.1 or TLSv1.2)?

The more information you provide, the sooner we solve your problem.

With respect.

(CID:129413313)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 03:55 PM . Last Modified: ‎2024-04-05 12:25 AM

0 Likes
0
2873
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:55 PM . Last Modified: ‎2024-04-05 12:25 AM

 

Hello, 

Thank you for the prompt reply. All our PDU devices have the same configuration, however, we have different FW versions since there are various models.

These are for the settings for the models

AP8888

Firmware 6.4.4

HTTP: Disable

HTTPS: Enable/port443/ minimum protocol TLS 1.2

FTP: Disable

Telnet: Disable

SSH: Enable/port22

SNMPv1: Disable

SNMPv3: Enable/SHA/AES

Firewall: Disable

Thank you for all your assistance.

 ******Vulnerability Title******

TLS/SSL Birthday attacks on 64-bit block ciphers (SWEET32)

*******Vulnerability Description******

Legacy block ciphers having a block size of 64 bits are vulnerable to a practical collision attack when used in CBC mode. All versions of the SSL/TLS protocols that support cipher suites which use 3DES as the symmetric encryption cipher are affected. The security of a block cipher is often reduced to the key size k: the best attack should be the exhaustive search of the key, with complexity 2 to the power of k. However, the block size n is also an important security parameter, defining the amount of data that can be encrypted under the same key. This is particularly important when using common modes of operation: we require block ciphers to be secure with up to 2 to the power of n queries, but most modes of operation (e.g. CBC, CTR, GCM, OCB, etc.) are unsafe with more than 2 to the power of half n blocks of message (the birthday bound). With a modern block cipher with 128-bit blocks such as AES, the birthday bound corresponds to 256 exabytes. However, for a block cipher with 64-bit blocks, the birthday bound corresponds to only 32 GB, which is easily reached in practice. Once a collision between two cipher blocks occurs it is possible to use the collision to extract the plain text data.

******Proof****

* Negotiated with the following insecure cipher suites: * TLS 1.0 ciphers: * TLS_DHE_RSA_WITH_3DES_EDE_CBC_SHA * TLS_PSK_WITH_3DES_EDE_CBC_SHA * TLS_RSA_WITH_3DES_EDE_CBC_SHA * TLS 1.1 ciphers: * TLS_DHE_RSA_WITH_3DES_EDE_CBC_SHA * TLS_PSK_WITH_3DES_EDE_CBC_SHA * TLS_RSA_WITH_3DES_EDE_CBC_SHA * TLS 1.2 ciphers: * TLS_DHE_RSA_WITH_3DES_EDE_CBC_SHA * TLS_PSK_WITH_3DES_EDE_CBC_SHA * TLS_RSA_WITH_3DES_EDE_CBC_SHA

(CID:129413634)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 03:55 PM . Last Modified: ‎2024-04-05 12:25 AM

0 Likes
0
2873
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:55 PM . Last Modified: ‎2024-04-05 12:25 AM

Dear Cristian Arias Lopez,

I believe, that at the moment, even if you have the latest firmware v.6.5.2 on your devices (I highly recommend upgrading since you use SNMPv3), you can not get rid of the above mentioned vulnerability.

I.e., the enable and subsequent configuration of the firewall in this case are useless. This vulnerability can be closed only by making the necessary changes in the firmware of the devices, i.e. refusing to use 3DES cipher suite altogether. More information about this can be found at link Impact and Mitigation on site https://sweet32.info/.

For information, here is the result of scanning my rPDU with the latest firmware v.6.5.2 with the minimum supported protocol TLSv1.2:

bashnmap -p 443 --script ssl-enum-ciphers 192.168.0.76# nmap -p 443 --script ssl-enum-ciphers 192.168.0.76 Starting Nmap 6.40 ( http://nmap.org ) at 2018-03-30 11:42 EEST Nmap scan report for 192.168.0.76 Host is up (0.044s latency). PORT STATE SERVICE 443/tcp open https | ssl-enum-ciphers: | TLSv1.0: | ciphers: | TLS_DHE_RSA_WITH_3DES_EDE_CBC_SHA - strong | TLS_DHE_RSA_WITH_AES_128_CBC_SHA - strong | TLS_DHE_RSA_WITH_AES_256_CBC_SHA - strong | TLS_PSK_WITH_3DES_EDE_CBC_SHA - strong | TLS_PSK_WITH_AES_128_CBC_SHA - strong | TLS_PSK_WITH_AES_256_CBC_SHA - strong | TLS_RSA_WITH_3DES_EDE_CBC_SHA - strong | TLS_RSA_WITH_AES_128_CBC_SHA - strong | TLS_RSA_WITH_AES_256_CBC_SHA - strong | compressors: | NULL | TLSv1.1: | ciphers: | TLS_DHE_RSA_WITH_3DES_EDE_CBC_SHA - strong | TLS_DHE_RSA_WITH_AES_128_CBC_SHA - strong | TLS_DHE_RSA_WITH_AES_256_CBC_SHA - strong | TLS_PSK_WITH_3DES_EDE_CBC_SHA - strong | TLS_PSK_WITH_AES_128_CBC_SHA - strong | TLS_PSK_WITH_AES_256_CBC_SHA - strong | TLS_RSA_WITH_3DES_EDE_CBC_SHA - strong | TLS_RSA_WITH_AES_128_CBC_SHA - strong | TLS_RSA_WITH_AES_256_CBC_SHA - strong | compressors: | NULL | TLSv1.2: | ciphers: | TLS_DHE_RSA_WITH_3DES_EDE_CBC_SHA - strong | TLS_DHE_RSA_WITH_AES_128_CBC_SHA - strong | TLS_DHE_RSA_WITH_AES_128_CBC_SHA256 - strong | TLS_DHE_RSA_WITH_AES_256_CBC_SHA - strong | TLS_DHE_RSA_WITH_AES_256_CBC_SHA256 - strong | TLS_PSK_WITH_3DES_EDE_CBC_SHA - strong | TLS_PSK_WITH_AES_128_CBC_SHA - strong | TLS_PSK_WITH_AES_256_CBC_SHA - strong | TLS_RSA_WITH_3DES_EDE_CBC_SHA - strong | TLS_RSA_WITH_AES_128_CBC_SHA - strong | TLS_RSA_WITH_AES_128_CBC_SHA256 - strong | TLS_RSA_WITH_AES_256_CBC_SHA - strong | TLS_RSA_WITH_AES_256_CBC_SHA256 - strong | compressors: | NULL |_ least strength: strong MAC Address: 00:C0:B7:xx:xx:xx (American Power Conversion) Nmap done: 1 IP address (1 host up) scanned in 17.74 seconds

Therefore, at the moment, while this vulnerability is not completely closed, I highly recommend reconnecting all your rPDUs to an isolated private LAN, which only the DCE server has access to. It is this design, that initially assumes DCE software by default.

If this is not possible, and your rPDU should be on the public LAN, I recommend that you enable the firewall and restrict access by rules with the exact host(s) name from which access to port 443 is allowed. And of course, on the host(s) from which you will be accessing the web-GUI of your rPDU on port 443, you must work with a modern browser, as indicated on the resource https://sweet32.info/:

  • Web browsers should offer 3DES as a fallback-only cipher, to avoid using it with servers that support AES but prefer 3DES.

Only then this solution can very much minimize the risk from the above vulnerability and simply not use the vulnerable 3DES cipher suite for communicate.

I hope this helps you.

With respect.

(CID:129413740)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 03:56 PM . Last Modified: ‎2024-04-05 12:25 AM

0 Likes
0
2873
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:56 PM . Last Modified: ‎2024-04-05 12:25 AM

Hello, 

 

Thank you for the prompt reply I was really hoping that there was a simpler way to work around this vulnerability. I'll follow with the security team to discuss to discuss our options.

Thanks again for all your assistance.

(CID:130091598)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 03:56 PM . Last Modified: ‎2024-04-05 12:25 AM

0 Likes
0
2873
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:56 PM . Last Modified: ‎2024-04-05 12:25 AM

Dear Cristian Arias Lopez,

Ok, thanks for the feedback 😀.

I will also be interested in knowing your way of solving this problem.

(CID:130091596)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 03:56 PM . Last Modified: ‎2023-10-22 02:29 AM

0 Likes
0
2873
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:56 PM . Last Modified: ‎2023-10-22 02:29 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore