Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

How to connect the inputs of a rack ATS to a breaker panel?

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Re: How to connect the inputs of a rack ATS to a breaker panel?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 10:00 PM . Last Modified: ‎2024-04-04 03:29 AM

0 Likes
6
1629
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:00 PM . Last Modified: ‎2024-04-04 03:29 AM

How to connect the inputs of a rack ATS to a breaker panel?

Hello,

A can't connect the inputs (power dependency) of a rack ATS to a breaker in a breaker panel. I can only connect to a rack PDU in the same rack.

This customer installed all ATS's in 2 extra racks.

The power supplies come from 2 breaker panels.

The outputs go to an extra rack PDU in each rack.

Workaround?

Regards

(CID:133373841)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 10:00 PM . Last Modified: ‎2024-04-04 03:29 AM

0 Likes
0
1629
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:00 PM . Last Modified: ‎2024-04-04 03:29 AM

Hi Eduard,

By design rack ATS can only be connected to the possible two rack pdu's in the same rack, eg 1 pair of rack pdu's can connect only one downstream rack ATS.

Unfortunately no reasonable workaround to offer, I guess any workarounds may result additional "problem" (such as adding new device and/or incorrect power capacity calculations ...), sorry.

Kind regards

(CID:133373867)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 10:00 PM . Last Modified: ‎2024-04-04 03:28 AM

0 Likes
2
1629
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:00 PM . Last Modified: ‎2024-04-04 03:28 AM

I had the same problem. I got round it by creating a receptacle in the server rack (e.g. a 16A IEC60309 socket, connected to the correct breaker on the panel) and then connecting the ATS to that receptacle. That way, you can have an ATS go straight back to the breaker panel without going through a PDU. You can do that in the rack's power properties page.

(CID:133373934)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 10:00 PM . Last Modified: ‎2024-04-04 03:28 AM

In response to DCIM_Support
0 Likes
0
1629
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:00 PM . Last Modified: ‎2024-04-04 03:28 AM

I tried your workaround but can't add a receptacle. I used following procedure: 

Is this the procedure you used?

I get an error:

 

 

 

The following url seems not to excist

http://www.schneider-electric.com/ws/ReceptacleTypes

(CID:134023040)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 10:00 PM . Last Modified: ‎2024-04-04 03:28 AM

In response to DCIM_Support
0 Likes
0
1629
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:00 PM . Last Modified: ‎2024-04-04 03:28 AM

Hello. To be clear, you do not need to add a receptacle type to DCO, you should add a receptacle to the rack which contains the rack based ATS.

From the rack properties view click the power pane and the new button to create a rack based receptacle.

From the popup window you can define the rack based receptacle. The receptacle type is selected from the pull down list in this view. If proper receptacle type is missing then you'd need to use SOAP or curl to add the proper receptacle type to the below list per the procedure which had been pasted above.

Once created you'll see the rack based receptacles in the power dependency properties for the rack based ATS in the same rack.

Regards

GregS

(CID:134023584)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 10:00 PM . Last Modified: ‎2024-04-04 03:28 AM

0 Likes
0
1629
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:00 PM . Last Modified: ‎2024-04-04 03:28 AM

I have many AP7732 and similar 2U rack mount ATS in my environments.  My work around has been as follows.  I have created a 1U 30A  PDU calling it a "Modified ATS"  I then stack two of them in a 2U space connecting one to a "A" feed PDU and the other to a "B" feed PDU in the rack that they exist.  This allows me to easily dedicate the power path.

(CID:133374217)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 10:01 PM . Last Modified: ‎2023-10-22 02:28 AM

0 Likes
0
1629
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:01 PM . Last Modified: ‎2023-10-22 02:28 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore