How to add the "Spacelogic AS-P" device to "Data Center Expert"? AS-P has connected modules DI-16, DO-FA-12, UI-8.DO-FC-4.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-02-16 07:27 AM
I think the Spacelogic device is a Modbus device. The incorrect file type error occurs when you try to add a Modbus DDF as an SNMP DDF and vice versa.
In DCE, go to Device > Modbus Device Communication Settings > Device Definition Files > Add/Update Definitions.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-02-10 09:01 AM
Hi @PFMEP ,
Please check this page to see whether the connected devices are currently supported:
https://ddf.ecostruxureit.com
If not, please submit an Asset Definition Request here:
https://app.ecostruxureit.com/request/
You might want to contact support for help with the requirements for the asset definition request.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-02-16 06:31 AM
I found on https://ddf.ecostruxureit.com DDF for SpaceLogic AS-P, but my DCE can't import xml files.
I got error "Incorrect file type"
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-02-16 07:27 AM
I think the Spacelogic device is a Modbus device. The incorrect file type error occurs when you try to add a Modbus DDF as an SNMP DDF and vice versa.
In DCE, go to Device > Modbus Device Communication Settings > Device Definition Files > Add/Update Definitions.