Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

How do I configure a link state alarm in DCE for a Netbotz device?

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Re: How do I configure a link state alarm in DCE for a Netbotz device?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 02:22 PM . Last Modified: ‎2024-04-03 11:56 PM

0 Likes
5
1402
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:22 PM . Last Modified: ‎2024-04-03 11:56 PM

How do I configure a link state alarm in DCE for a Netbotz device?

Hello,


I have a DCE 7.6 server monitoring a number of Netbotz 450 devices.

How do I configure a communication alarm / link state alarm in DCE so that it can notifiy me if it loses communication with the Netbotz 450 device ?

It looks like it is logging a critical alarm when I unplug the 450 from the network as a test but DCE is not sending me an e-mail alert indicating that the 450 is un-reachable.

I only get the link state alerts directly from the 450 itself once it is back on the network which is not overly useful.

Steve

(CID:136153938)

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 02:22 PM . Last Modified: ‎2024-04-03 11:56 PM

0 Likes
2
1402
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:22 PM . Last Modified: ‎2024-04-03 11:56 PM

Dear Steve McLaughlin,

In short, the current DCE-7.x software sends email notifications of loss of communication with NetBotz-4.x appliances only to DCE administrators (if the correct email addresses have been entered in System -> User and Device Group Access...).

This type of notification is not subject to any DCE notification policies. This, if you want, such a DCE-7.x and NetBotz-4.x appliances design 😀.

If you have more questions, please ask.

With respect.

(CID:136644407)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 02:22 PM . Last Modified: ‎2024-04-03 11:56 PM

0 Likes
0
1403
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:22 PM . Last Modified: ‎2024-04-03 11:56 PM

Dear Steve,

It is also possible to receive the Ethernet Link Status lost alarm from Netbotz if the following is configured on Netbotz Advance view. 

 

It is possible to create a threshold for the Ethernet Link Status and associate to your Profile-Alert Action(ie.,email) to receive the email alert when it occurs. 

 

 

Regards,

Bala

(CID:136644268)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 02:22 PM . Last Modified: ‎2024-04-03 11:56 PM

0 Likes
2
1403
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:22 PM . Last Modified: ‎2024-04-03 11:56 PM

Dear Steve McLaughlin,

In short, the current DCE-7.x software sends email notifications of loss of communication with NetBotz-4.x appliances only to DCE administrators (if the correct email addresses have been entered in System -> User and Device Group Access...).

This type of notification is not subject to any DCE notification policies. This, if you want, such a DCE-7.x and NetBotz-4.x appliances design 😀.

If you have more questions, please ask.

With respect.

(CID:136644407)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 02:22 PM . Last Modified: ‎2024-04-03 11:56 PM

In response to DCIM_Support
0 Likes
0
1403
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:22 PM . Last Modified: ‎2024-04-03 11:56 PM

Thanks!

Added an e-mail address to the DCE admin user and the communication alarms for Netbotz 450 devices work now.

(CID:136644699)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 02:23 PM . Last Modified: ‎2024-04-03 11:56 PM

In response to DCIM_Support
0 Likes
0
1403
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:23 PM . Last Modified: ‎2024-04-03 11:56 PM

Ok, thanks for the good feedback 😀.

(CID:136644702)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 02:23 PM . Last Modified: ‎2023-10-22 02:20 AM

0 Likes
0
1403
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:23 PM . Last Modified: ‎2023-10-22 02:20 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore