Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

How can I get sensor value for snmp device ?

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase โ†’ Use quotes " " (e.g., "error 404")
  • Wildcard โ†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR โ†’ Combine keywords (e.g., login AND error, login OR signโ€‘in)
  • Keep it short โ†’ Use 2โ€“3 relevant words , not full sentences
  • Filters โ†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • How can I get sensor value for snmp device ?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-04 06:40 PM . Last Modified: โ€Ž2024-04-04 11:28 PM

0 Likes
6
1562
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 06:40 PM . Last Modified: โ€Ž2024-04-04 11:28 PM

How can I get sensor value for snmp device ?

Hello,

I have an issue with the detection of my device sensor, I can't get temperature value, power consumption of my snmp device . Even if I put the oid in the setting of snmp, struxuware don't give me more informations on my sensor

How can I resolve this problem ?

(CID:132650310)

Labels
  • Labels:
  • Data Center Expert
  • Tags:
  • bug
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-04 06:40 PM . Last Modified: โ€Ž2024-04-04 11:28 PM

0 Likes
1
1562
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 06:40 PM . Last Modified: โ€Ž2024-04-04 11:28 PM

Hi Kemal,

 

Your first choice should always be to put in a DDF request. This is for new DDFs or for update to current DDFs and they should be able to assist in getting any of the values available through SNMP on your device.

 

If using supplemental OIDs, please make sure you try with a leading period. For instance, instead of:

1.3.6.1.4.1.318

use

.1.3.6.1.4.1.318

Notice the leading period.

Secondly, make sure you use the correct instance(s). As an example, the following OID is for an APC UPS and it's battery capacity:

.iso.org.dod.internet.private.enterprises.apc.products.hardware.ups.upsBattery.upsAdvBattery.upsAdvBatteryCapacity

.1.3.6.1.4.1.318.1.1.1.2.2.1

This will not return a value in DCE. You should do an SNMP get of the OID to see the proper and available instances and in this case, the device will respond with an instance of 0...you'll need to use the following OID to get this value:

.1.3.6.1.4.1.318.1.1.1.2.2.1.0

 

Another thing to consider is that there is no multiplier. If you pull an OID similar to the one I just mentioned, it may return the value in tenths. At 100% capacity, it may return 1000 to indicate 100.0%

Finally, a supplemental OID in DCE will only work with numeric values. Text will not work and if you were to even poll a value such as time (hh:mm:ss), you will not receive any values after the colon. you may simply see "hh" and nothing else. This is a limitation of supplemental OIDs.

Much of this should also be noted in k-base FA158341 


If you're not getting any values at all, it could be that you need to troubleshoot SNMP as a whole. K-base FA226273 should help with that.

 

Thanks,

Steve.

 

(CID:132650325)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-04 06:40 PM . Last Modified: โ€Ž2024-04-04 11:28 PM

0 Likes
1
1563
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 06:40 PM . Last Modified: โ€Ž2024-04-04 11:28 PM

Hi Kemal,

 

Your first choice should always be to put in a DDF request. This is for new DDFs or for update to current DDFs and they should be able to assist in getting any of the values available through SNMP on your device.

 

If using supplemental OIDs, please make sure you try with a leading period. For instance, instead of:

1.3.6.1.4.1.318

use

.1.3.6.1.4.1.318

Notice the leading period.

Secondly, make sure you use the correct instance(s). As an example, the following OID is for an APC UPS and it's battery capacity:

.iso.org.dod.internet.private.enterprises.apc.products.hardware.ups.upsBattery.upsAdvBattery.upsAdvBatteryCapacity

.1.3.6.1.4.1.318.1.1.1.2.2.1

This will not return a value in DCE. You should do an SNMP get of the OID to see the proper and available instances and in this case, the device will respond with an instance of 0...you'll need to use the following OID to get this value:

.1.3.6.1.4.1.318.1.1.1.2.2.1.0

 

Another thing to consider is that there is no multiplier. If you pull an OID similar to the one I just mentioned, it may return the value in tenths. At 100% capacity, it may return 1000 to indicate 100.0%

Finally, a supplemental OID in DCE will only work with numeric values. Text will not work and if you were to even poll a value such as time (hh:mm:ss), you will not receive any values after the colon. you may simply see "hh" and nothing else. This is a limitation of supplemental OIDs.

Much of this should also be noted in k-base FA158341 


If you're not getting any values at all, it could be that you need to troubleshoot SNMP as a whole. K-base FA226273 should help with that.

 

Thanks,

Steve.

 

(CID:132650325)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-04 06:40 PM . Last Modified: โ€Ž2024-04-04 11:28 PM

In response to DCIM_Support
0 Likes
0
1562
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 06:40 PM . Last Modified: โ€Ž2024-04-04 11:28 PM

Hello Steve,

 

Thank you very much , I can clearly understand now.

(CID:132659396)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-04 06:40 PM . Last Modified: โ€Ž2024-04-04 11:27 PM

0 Likes
0
1562
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 06:40 PM . Last Modified: โ€Ž2024-04-04 11:27 PM

Dear kemal,

Tell us please, did you solve your problem or not?

With respect.

(CID:132653782)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-04 06:40 PM . Last Modified: โ€Ž2024-04-04 11:27 PM

0 Likes
0
1562
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 06:40 PM . Last Modified: โ€Ž2024-04-04 11:27 PM

yes the problem is solved

(CID:132653922)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-04 06:40 PM . Last Modified: โ€Ž2024-04-04 11:27 PM

0 Likes
0
1562
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 06:40 PM . Last Modified: โ€Ž2024-04-04 11:27 PM

Ok, thanks for the good feedback ๐Ÿ˜€.

(CID:132653938)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-04 06:41 PM . Last Modified: โ€Ž2023-10-22 02:18 AM

0 Likes
0
1562
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 06:41 PM . Last Modified: โ€Ž2023-10-22 02:18 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

Youโ€™ve reached the end of your document

WHATโ€™S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore