Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Energy Efficiency Configuration Issues

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Energy Efficiency Configuration Issues
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 08:29 PM . Last Modified: ‎2024-04-03 01:12 AM

0 Likes
4
1448
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 08:29 PM . Last Modified: ‎2024-04-03 01:12 AM

Energy Efficiency Configuration Issues

Hi,

 

I'm facing several issues with the Energy Efficiency configuration as follows:

  • After finalizing the system configuration, scripts, ... etc. I'm getting a very high negative value in the power system percentage, and a very large cooling system percentage (more than 200%), with the PUE being very low (way lower than the predicted value).

  • In the redundancy field under the Energy Efficiency property, does it have to be N for all equipments?  Does this impact the PUE or the subsystem consumption?

  • In the subsystem cost section in EE dashboard, Whenever I change the graph settings (price, currency, & CO2 emission), they always turn back to the default values after sometime.

  • I'm aware that switch-gears must only connect to either PDUs or UPSs, but what about in-between (input/output) panels or DBs.  Does it matter if they are PDUs or generic power panels?  Also, can they have identical scripts to the load (i.e. UPS)?

 

Thank you for the support.

 

Regards,

Mohamed

(CID:146670771)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 08:29 PM . Last Modified: ‎2024-04-03 01:12 AM

0 Likes
2
1448
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 08:29 PM . Last Modified: ‎2024-04-03 01:12 AM

Hi Mohamed,

Sorry for the very late response. 

I guess (only guessing) you might have minus/negative sign somewhere in the configuration/scripts leading to a negative PUE. PUE values are positive and basically depends on the configuration itself.

The N redundancy and other settings also depends on the setup, some of the settings may not have a clear/visible impact in the final displayed PUE.

And the "Subsystem Cost", this may require detail investigation of the setup and details/info on what is expected to be seen.

I think the power path in EE is from Swichgear -> UPS -> PDU
PDU -> UPS is not supported.
I would suggest using PDU and not generic power panels, since they may have different behavior in the setup.
I think usually up to user to define his/her configuration & scripts and there is no restriction not having the same/similar scripts on different devices.

Kind regards

(CID:149784403)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 08:29 PM . Last Modified: ‎2024-04-03 01:12 AM

In response to DCIM_Support
0 Likes
0
1448
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 08:29 PM . Last Modified: ‎2024-04-03 01:12 AM

Hello Mohamed, Adding to Jef's response. You will need to start the power path with a switchgear device which is configured to feed the UPS's or start of your power path. 

Based on your posting, I assume you have already defined an energy system in the EE view in the desktop client. I also assume you have assigned scripts to the items in the energy system? So your energy system view may look something like this simple example below?

Jef mentioned its possible one of the scripts you're using is returning a negative value. You should be able to double click each of the scripts in the lower left side pane and click the "evaluate" button (highlighted in yellow below) to force the script to execute immediately so you can see the result in the evaluated pane.

The values should be positive. If you see a negative value then you'd need to investigate why the sensor or items queried in the script are returning negative numbers.

Regards

Greg Sterling

(CID:149784456)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 08:29 PM . Last Modified: ‎2024-04-03 01:12 AM

In response to DCIM_Support
0 Likes
0
1448
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 08:29 PM . Last Modified: ‎2024-04-03 01:12 AM

Hi Jef & Greg, Thank you both for your replies.

Yes, I've already defined an energy system and assigned a script to each item.

I've gone through all the scripts and didn't find any negative value returned.

The only thing I'm suspecting is that I have a mixture of PDUs and power panels, can this be the reason ? and should it have a significant impact on the result ?

However, I've already submitted a ticket to further investigate those issues.

Regards,

Mohamed

(CID:149784542)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 08:30 PM . Last Modified: ‎2023-10-22 02:01 AM

0 Likes
0
1448
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 08:30 PM . Last Modified: ‎2023-10-22 02:01 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore