Easy UPS 3S RS-485 port issues

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Re: Easy UPS 3S RS-485 port issues
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
127
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
jaimegut
Crewman jaimegut Crewman
Crewman

Posted: ‎2022-07-31 07:40 PM . Last Modified: ‎2022-10-19 12:44 AM

0 Likes
19
7568
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-31 07:40 PM . Last Modified: ‎2022-10-19 12:44 AM

Easy UPS 3S RS-485 port issues

Hello community !

 

Need some support in getting an Easy UPS 3S talking via the Modbus RS-485 port.  Here is the FW version

 

Rectifier: V55.008.002

Inverter: V55.008.002

 

I've tried both with a Panel Server PAS600 and PAS800 with similar results when trying to use ModScan to read register values.

 

ModBus Set values:
Address: 001
Com Mode: ASCII (have tried RTU as well with exact same results)

Baud Rate: 9600

 

Com set: Normal

 

There's a tutorial video on YouTube that shows exactly how some colleagues in Schneider Electric Spain did this and I've replicated the steps with no luck.

 

https://www.youtube.com/watch?v=XdSHnuA9-i0

 

In the video, the narrator even shows the exact function code they are reading and the registers, no success when I try the same.

 

At some point I even tried flipping the + and - wires on the back of the UPS to try and rule out that as a possible issue.

 

Looking for some additional ideas, maybe a FW issue or something else.

 

Any ideas are welcome.

 

I've read similar previous posts below:

 

https://community.se.com/t5/EcoStruxure-Building-Operation/Modbus-integration-of-a-3S-UPS-on-EBO/m-p...

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 19
jaimegut
Crewman jaimegut Crewman
Crewman

Posted: ‎2022-08-01 03:33 AM

In response to Smith904
0 Likes
0
7533
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-01 03:33 AM

I should have mentioned that I already had the ModBus register map and tried different register reads. 

Any other suggestions?

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

tjlaw
Lt. Commander tjlaw Lt. Commander
Lt. Commander

Posted: ‎2022-08-10 10:06 PM

0 Likes
16
7406
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-10 10:06 PM

HI, 

 

Just wondering if you tried connect directly via USB to RS485 to the UPS and scanned using ModScan? Or maybe you can share the error you have while using ModScan through Panel Server? 

 

BR, 

 

TJ

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

jaimegut
Crewman jaimegut Crewman
Crewman

Posted: ‎2022-08-30 12:50 PM

In response to tjlaw
0 Likes
15
7249
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-30 12:50 PM

I completely missed that there was activity on this thread, my bad.

 

Actually I have tried USB directly to the RS-485 port as well and scanned using ModScan, nothing seems to be talking out of the RS-485 terminals.

 

Using the PanelServer is the same (either via the embedded webpage of the panel server or using ModScan going through the panel server), there's nothing but "no comms" status being returned.

 

I've been careful to follow all the settings listed in the ModBus manual (stop bits, parity, default baud rate, etc.).  I even went as far as flipping the + / -  on the back of the Easy UPS to try and see if that would present any different results (both when using the panel server or communicating directly).  Nothing shows any signs of that port actually doing anything unfortunately.

 

The registers that I'm trying to read from are a few easy points to verify that communication is even possible.

 

For example,

Input Voltage on each phase, address 10012, 10013, 10014 using read function 0x03

Input Frequency on each phase, address 10018, 10019, 10020 using read function 0x03

 

I'm pretty sure that the unit I have is not communicating via the RS-485 port.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Dominique38
Ensign Dominique38 Ensign
Ensign

Posted: ‎2022-09-08 05:57 AM . Last Modified: ‎2022-09-08 05:58 AM

In response to jaimegut
0 Likes
14
7144
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-08 05:57 AM . Last Modified: ‎2022-09-08 05:58 AM

Hi,

Be sure that menu "Communication Set " is set to Normal.

Take care about modbus address sent to the UPS, depends of tool used

With Modscan, you must add one to register address

Exemple, for address 2710 hexa format requested, you have to set either 10001 decimal format or 2711 haxa format

 
 

After that, Easy 3S is working fine with modbus requests

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

jaimegut
Crewman jaimegut Crewman
Crewman

Posted: ‎2022-09-08 06:06 AM

In response to Dominique38
0 Likes
13
7138
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-08 06:06 AM

Thank you for the response @Dominique38 ,,, I did verify this already see attached document.

 

And yes, I have considered the offset based on the Modbus protocol to make sure that I wasn't polling an incorrect register.

 

 

 

 

Attachments
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Dominique38
Ensign Dominique38 Ensign
Ensign

Posted: ‎2022-09-08 06:14 AM

In response to jaimegut
0 Likes
12
7134
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-08 06:14 AM

 

See my Modscan request:

Easy.png


is there an answer form the Easy ??

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

jaimegut
Crewman jaimegut Crewman
Crewman

Posted: ‎2022-09-08 06:53 AM

In response to Dominique38
0 Likes
2
7131
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-08 06:53 AM

@Dominique38 

 

Let me ask something, so I can replicate exactly what you are doing.  

 

1. Are you using panel server in between the Easy UPS and Modscan ?  ( That's the setup I have and have also tried going direct via a USB to RS-485 converter)   I am asking so I can replicate the method you are doing.

 

2. In the Easy UPS, under "ModBus Set", what setting are you using (RTU / ASCII) ?  

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Dominique38
Ensign Dominique38 Ensign
Ensign

Posted: ‎2022-09-08 07:24 AM

In response to jaimegut
0 Likes
1
7124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-08 07:24 AM

I use a small USB/RS485 converter 2 wires form Aliexpress, like this one:

https://fr.aliexpress.com/item/1005003032516569.html

 

Then i use RTU mode and 9600bd (works bettter than 19200), 8 bits/no parity/no flow control/one stop

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Shaun
Commander Shaun Commander
Commander

Posted: ‎2022-09-08 07:26 AM

In response to Dominique38
0 Likes
8
7123
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-08 07:26 AM

Hi @Dominique38 

 

That looks reasonable to me -the next bytes look like a modbus exception so it looks like communication is good (eg, both ends are speaking to each other, they just don't like the answer)

 

Could you try requesting less than 125 registers?  The modbus map is non-contiguous (there's "reserved blocks" eg at 10056-70).  How that's handled varies between devices - some only complain if you start the request in empty space, some won't allow you to address empty space at all.

 

I haven't been able to test this myself yet, but this is the only difference I can see between your examples and the spanish video, so it may be worth trying.

 

Regards,

  Shaun

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Dominique38
Ensign Dominique38 Ensign
Ensign

Posted: ‎2022-09-08 07:33 AM

In response to Shaun
0 Likes
7
7120
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-08 07:33 AM

Hi Shaun,

 

i did not see the video

Here is the answer of the 125 register: the Easy is able to reply the 125 registers contiguous even if some of them are reserved

Easy2.png.jpg

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

tjlaw
Lt. Commander tjlaw Lt. Commander
Lt. Commander

Posted: ‎2022-09-08 07:49 AM

In response to Dominique38
0 Likes
0
7109
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-08 07:49 AM

Hi, 

 

Do you mind sharing the UPS firmware version you communicating with? Compared with the firmware version encountered by @jaimegut 

 

 

BR, 

 

TJ

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

jaimegut
Crewman jaimegut Crewman
Crewman

Posted: ‎2022-09-08 07:59 AM

In response to Dominique38
0 Likes
0
7106
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-08 07:59 AM

Just replicated everything you've suggested,

 

3S_ModScan_101.jpg

 

3S_ModScan_102.jpg

 

MODBUS Message TIME-OUT is the response being sent back to ModScan (Pictures shows both 125 registers and 10 registers attempted to be read)

 

I'm striking out with this particular unit left and right

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Shaun
Commander Shaun Commander
Commander

Posted: ‎2022-09-08 08:09 AM . Last Modified: ‎2022-09-08 08:09 AM

In response to Dominique38
0 Likes
5
7103
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-08 08:09 AM . Last Modified: ‎2022-09-08 08:09 AM

@Dominique38 , sorry, I got you and the customer confused.

 

That does seem to rule out that idea though, thanks for that.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Dominique38
Ensign Dominique38 Ensign
Ensign

Posted: ‎2022-09-08 08:43 AM

In response to Shaun
0 Likes
4
7094
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-08 08:43 AM

I can not check UPS firmware now, i'll do it next Monday.

Check your USB/RS485 converter...??

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

jaimegut
Crewman jaimegut Crewman
Crewman

Posted: ‎2022-09-08 09:02 AM

In response to Dominique38
0 Likes
2
7091
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-08 09:02 AM

I'm using:

 

https://www.gearmo.com/shop/usb-to-rs485-rs422-converter-with-ftdi-chip/

 

Hasn't been a problem on other devices 😀

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Dominique38
Ensign Dominique38 Ensign
Ensign

Posted: ‎2022-09-11 11:54 PM

In response to jaimegut
0 Likes
1
7030
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-11 11:54 PM

Hi,

Here is UPS firmware version:

easy3.JPG

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

jaimegut
Crewman jaimegut Crewman
Crewman

Posted: ‎2022-09-12 06:11 AM

In response to Dominique38
0 Likes
0
7015
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-12 06:11 AM

I'm sourcing another USB to RS485 converter, will have it in a day or two. 

 

I'll provide an update to see if that changes anything, however I doubt this is the problem since the results have been the same using an EcoStruxure Panel (PAS600) server to try reach its registers through TCP-IP and the panel server as well was not able to establish communications with the UPS unit.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

jaimegut
Crewman jaimegut Crewman
Crewman

Posted: ‎2022-09-20 06:17 AM

In response to Dominique38
0 Likes
0
6892
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-20 06:17 AM

@Dominique38 

Sorry, it took me a week to source the component to be similar to the one you are using.

 

Just tried it out, no difference in the results.  

 

Changed Baud Rate, flipped the +/- wires, changed from RTU to ASCII (both on the UPS and on ModScan), did several things to make sure it wasn't a bad item on the physical wiring or a setting oversight.

 

I'm back to thinking that this particular unit I have is not able to communicate over the RS-485 port in the back.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

afecomt
Crewman afecomt
Crewman

Posted: ‎2024-09-27 03:04 AM

0 Likes
0
4249
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-27 03:04 AM

updating firmware sometimes solve the problem

tenemos muchos problemas con este ups. 

schenider support requested us logs with Tuner software. lets see

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore