Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Device Alarm Configurations

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Device Alarm Configurations
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 05:34 PM . Last Modified: ‎2024-04-03 03:19 AM

0 Likes
4
1588
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 05:34 PM . Last Modified: ‎2024-04-03 03:19 AM

Device Alarm Configurations

We are running DCE 7.2.7.25. I am in the process up upgrade over 100 store level APC Smart 1500, 2200 and 3000 UPSs. I am using the user config file to set all the global configurations on the NMC. I am also using DCE to set the device alarms, so we are not overwhelmed with faulty alerts. This seems to be a time-consuming task even when I’m able to set up groups of devices at a time. Is there a function in DCE to allow you to create a device alarm template and then set all new UPS to this same standard?  

 

(CID:140709545)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 05:34 PM . Last Modified: ‎2024-04-03 03:19 AM

0 Likes
2
1588
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 05:34 PM . Last Modified: ‎2024-04-03 03:19 AM

Hi Chuck,

If you're looking to add a device and have it automatically obtain a configuration such as temperature threshold, load alarm etc then no, there is no automated way to do this.

You mentioned using user config file though. Are you setting everything up by sending a config.ini using the configuration utility? If so, DCE has an easier way than that. You have the option to use the Device-->APC SNMP DeviceConfiguration option. If you have NMCs with 6.x and higher firmware, you can't set any user info on the device. That changed a while back and I don't believe the old version of DCE you mentioned has that option:

 

 

For most other settings however, you can use the standard device configuration and can push certain configuration options to devices.You can also save that configuration as a template and the next time you add a device, you can push that template...just not automatically.

You may want to consider asking for a feature request for this which can be done here:

https://sxwhelpcenter.ecostruxureit.com/display/public/Feature+requests?queryString=feature%20reques...

 

Thanks,

Steve.

 

 

(CID:140709862)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 05:34 PM . Last Modified: ‎2024-04-03 03:19 AM

0 Likes
2
1589
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 05:34 PM . Last Modified: ‎2024-04-03 03:19 AM

Hi Chuck,

If you're looking to add a device and have it automatically obtain a configuration such as temperature threshold, load alarm etc then no, there is no automated way to do this.

You mentioned using user config file though. Are you setting everything up by sending a config.ini using the configuration utility? If so, DCE has an easier way than that. You have the option to use the Device-->APC SNMP DeviceConfiguration option. If you have NMCs with 6.x and higher firmware, you can't set any user info on the device. That changed a while back and I don't believe the old version of DCE you mentioned has that option:

 

 

For most other settings however, you can use the standard device configuration and can push certain configuration options to devices.You can also save that configuration as a template and the next time you add a device, you can push that template...just not automatically.

You may want to consider asking for a feature request for this which can be done here:

https://sxwhelpcenter.ecostruxureit.com/display/public/Feature+requests?queryString=feature%20reques...

 

Thanks,

Steve.

 

 

(CID:140709862)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 05:35 PM . Last Modified: ‎2024-04-03 03:18 AM

In response to DCIM_Support
0 Likes
0
1588
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 05:35 PM . Last Modified: ‎2024-04-03 03:18 AM

P.S.

This option I mentioned is only for configuring the device and nothing specific to the device alarms as listed/configured in DCE.

(CID:140709870)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 05:35 PM . Last Modified: ‎2024-04-03 03:18 AM

In response to DCIM_Support
0 Likes
0
1588
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 05:35 PM . Last Modified: ‎2024-04-03 03:18 AM

I was afraid the alarm configuration template I was looking for was not yet an option in DCE. The alternative for configuring the devices will save me a lot of time. 

 

Thank you

Chuck

(CID:140709984)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 05:35 PM . Last Modified: ‎2023-10-22 01:53 AM

0 Likes
0
1588
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 05:35 PM . Last Modified: ‎2023-10-22 01:53 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore