Posted: 2020-06-21 05:03 AM
Hi Team,
Kindly I keep getting this alarm after adding the ups communication card to DCE, I have tried to reinstall DDF for the specific UPS but still not sorted.
Please assist.
Thank you.
Regards,
Felix
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-06-21 05:19 AM
Dear @Angwenyi ,
This is not a DDF-file or device problem. There is a standard solution for this error, which is described in detail in Data Center Expert | Alarm "Device status may be inaccurate due to attempt to transfer DDF failed".
I hope this will help you.
With respect.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-06-21 05:19 AM
Dear @Angwenyi ,
This is not a DDF-file or device problem. There is a standard solution for this error, which is described in detail in Data Center Expert | Alarm "Device status may be inaccurate due to attempt to transfer DDF failed".
I hope this will help you.
With respect.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.