Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

DDF Stulz WIB 8000

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Re: DDF Stulz WIB 8000
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
160
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 06:29 PM . Last Modified: ‎2024-04-03 02:58 AM

0 Likes
6
2138
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:29 PM . Last Modified: ‎2024-04-03 02:58 AM

DDF Stulz WIB 8000

(CID:141268073)

Labels
  • Labels:
  • Data Center Expert
  • DDF
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 06:29 PM . Last Modified: ‎2024-04-03 02:58 AM

0 Likes
0
2137
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:29 PM . Last Modified: ‎2024-04-03 02:58 AM

Dear Andrew Stoakes,

From your question:

Does anyone out there have a working SNMP DDF for the Stulz "WIB 8000"?

For example, from topic Can anybody give me the Modbus ddf files for Stulz C7000 & for WIB 8000, working SNMP DDF-file can be downloaded from the DDF resource:

When discovering this device in DCE it "initialising" for about 15 minutes and then errors. The only sensor is the "Link" and the value is "Off Line"

Please specify which DDF-file for Stulz WIB8000 you are using (name and version)?

I think it would be useful for you to read several similar topics:

  •  
  • Can anybody give me the Modbus ddf files for Stulz C7000 & for WIB 8000
  •  

If you have more questions, please ask.

With respect.

(CID:141268153)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 06:29 PM . Last Modified: ‎2024-04-03 02:58 AM

0 Likes
1
2137
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:29 PM . Last Modified: ‎2024-04-03 02:58 AM

Thanks

I have version 23 of the "Stulz WIB" SNMP DDF which appears to be the latest version available. I have also looked at all the forums that I could find but there are no real answers, some people appear to have this working but with modified DDFs, others don't.

Really at a loss as to what's going on. I have confirmed that we are able to read SNMP data from the WIB from the DCE server so the WIB is configured correctly. 

When I first add the WIB to DCE it takes 15-30min to initialise but the only sensor is the link sensor which then goes offline. I have left this overnight as sugested in some of the comments but still no result. 

(CID:141268588)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 06:29 PM . Last Modified: ‎2024-04-03 02:58 AM

In response to DCIM_Support
0 Likes
0
2137
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:29 PM . Last Modified: ‎2024-04-03 02:58 AM

Dear Andrew Stoakes,

From your comments:

I have version 23 of the "Stulz WIB" SNMP DDF which appears to be the latest version available. I have also looked at all the forums that I could find but there are no real answers, some people appear to have this working but with modified DDFs, others don't.

The cause of your problems is definitely not in the specified SNMP DDF-file stulz_wib.xml.

When I first add the WIB to DCE it takes 15-30min to initialise but the only sensor is the link sensor which then goes offline. I have left this overnight as sugested in some of the comments but still no result.

Carefully check the SNMP settings on the WIB8000 device and on the DCE-server. See Andrew Stoakes helpful hint for setting up the WIB8000:

Be aware that by default the port on the WIB is set to 162 not 161. By default DCE will scan on port 161, the WIB will need to be changed.

To change the WIB setting

  1. disable SNMP
  2. Change the port to 161
  3. Restart the WIB
  4. Enable SNMP
  5. Use a snmp browser to confirm that you can read the values from the WIB on 161

Hope this helps you.

With respect.

(CID:141268642)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 06:29 PM . Last Modified: ‎2024-04-03 02:58 AM

0 Likes
1
2137
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:29 PM . Last Modified: ‎2024-04-03 02:58 AM

Think i have found the issue. The WIB is located on a section of the network that is remote and a via a slow link that has high latency. I have increased the timeout setting to 45 seconds and the retries to 5. I now have information from eh WIB and its online. 

I have noticed that even though the scheduled scan is set to every minute that the last scan time was 05:52am this morning, the current time is 07:28am indicating that we have communication issues with the device. all other equipment on that network segment is reporting as requested.   

(CID:141269000)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 06:29 PM . Last Modified: ‎2024-04-03 02:58 AM

In response to DCIM_Support
0 Likes
0
2137
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:29 PM . Last Modified: ‎2024-04-03 02:58 AM

Dear Andrew Stoakes,

From your comments:

I have noticed that even though the scheduled scan is set to every minute that the last scan time was 05:52am this morning, the current time is 07:28am indicating that we have communication issues with the device. all other equipment on that network segment is reporting as requested.

I'm glad you found the true problem in your WIB8000 solution. I hope, that you solve this problem and get the desired result.

If you have more questions, please ask.

With respect.

(CID:141269119)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 06:30 PM . Last Modified: ‎2023-10-22 01:47 AM

0 Likes
0
2136
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:30 PM . Last Modified: ‎2023-10-22 01:47 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore