Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

DCO Upgrade issue

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCO Upgrade issue
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
160
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 04:13 AM . Last Modified: ‎2024-04-05 03:04 AM

0 Likes
13
1971
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:13 AM . Last Modified: ‎2024-04-05 03:04 AM

DCO Upgrade issue

Hi Team,

I have tried to upgrade from DCO 8.2 to 8.2.2 directly from the server and it failed. I have uploaded the ISO package from version 8.2.2 to the server and then upgraded  from it, but then in the logs, I read that it tries to connect to Centos repository looking for updates.

This installation does not have connection to the Internet, but even selecting the option "Do not download packages from the Internet" it also reports the same error: failing to connect to  http://mirrorlist.centos.org

Is there anyway to update the server without having connection to the Internet and without deploying a new virtual machine?

I have attached a file with the update log.update_logs.txt

Regards

(CID:128067748)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 13
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 04:13 AM . Last Modified: ‎2024-04-05 03:03 AM

0 Likes
0
1971
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:13 AM . Last Modified: ‎2024-04-05 03:03 AM

Hi Javier, I am in the same boat... Our update fails and within the resulting log files I see terms like "build doesn't match" something or other. I'm trying again now, but as suggested... with the "do not download..." part checked.

(CID:128067804)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 04:13 AM . Last Modified: ‎2024-04-05 03:03 AM

0 Likes
2
1971
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:13 AM . Last Modified: ‎2024-04-05 03:03 AM

Javier

A mi me ha pasado lo mismo en otras actualizaciones, al final se soluciono haciendo una copia, reinstalando manualmente y restaurando la copia,

Si dan otra solucion y funciona, genial para otras ocasiones.

saludos

(CID:128067824)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 04:13 AM . Last Modified: ‎2024-04-05 03:03 AM

In response to DCIM_Support
0 Likes
0
1971
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:13 AM . Last Modified: ‎2024-04-05 03:03 AM

Gracias Miguel Angel,

es lo que quería evitar, porque en clientes es un engorro tener que montar máquinas nuevas para hacer un restore.

Con conexión a Internet he probado hacerlo directamente desde ahí y ha funcionado. A ver si nos dan una solución.

Saludos!

(CID:128067830)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 04:14 AM . Last Modified: ‎2024-04-05 03:03 AM

In response to DCIM_Support
0 Likes
0
1971
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:14 AM . Last Modified: ‎2024-04-05 03:03 AM

Perfecto, si hay internet siempre va, pero no siempre tenemos en los clientes.

un saludo

(CID:128067833)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 04:14 AM . Last Modified: ‎2024-04-05 03:03 AM

0 Likes
0
1971
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:14 AM . Last Modified: ‎2024-04-05 03:03 AM

Hi Team,

Is there anyway to upgrade DCO without being connected to the Internet?

Regards

(CID:128747778)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 04:14 AM . Last Modified: ‎2024-04-05 03:03 AM

0 Likes
0
1971
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:14 AM . Last Modified: ‎2024-04-05 03:03 AM

Hi Jef Faridi,

Can you confirm that it is impossible to upgrade DCO without connection to the Internet?

We have an upgrade to 8.2.2 waiting for this issue, and we would not want to ask for a new VM to deploy the new version to our customer.

Regards

(CID:128749509)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 04:14 AM . Last Modified: ‎2024-04-05 03:03 AM

0 Likes
0
1971
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:14 AM . Last Modified: ‎2024-04-05 03:03 AM

Hi Javier,

It would be great if we could check your updated log files, so could you please:

a) retry the upgrade by selecting the option "Do not download packages from the Internet"

b) and then after a short while (5-10 min.), download the server logs and share with me (I will send you an invite to my box folder).

Thanks,

Kind regards

(CID:128749512)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 04:14 AM . Last Modified: ‎2024-04-05 03:03 AM

0 Likes
0
1971
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:14 AM . Last Modified: ‎2024-04-05 03:03 AM

HI Jef,

what logs do you need? Can you indicate me the proccess to download the logs that you need?

There are some logs in the screen during the upgrade process, but I think that are not the ones you need.

Regards

(CID:128750291)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 04:14 AM . Last Modified: ‎2024-04-05 03:03 AM

0 Likes
0
1971
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:14 AM . Last Modified: ‎2024-04-05 03:03 AM

Hi Javier,

Many thanks for checking, server log (full set) can be collected from webmin interface: StuxureWare DC Operation > Download Log Files > "Download log files"
(the log collection may take several minutes and the collected file format would be: logs-xxx.tar.gz)

Kind regards

(CID:128750311)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 04:14 AM . Last Modified: ‎2024-04-05 03:03 AM

0 Likes
0
1971
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:14 AM . Last Modified: ‎2024-04-05 03:03 AM

Hi Jef,

I have tried once again the upgrade and I got the same failure. I have shared in  your box the server's logs as you requested.

Here I also attach some screenshots of the upgrade:

(CID:128750992)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 04:14 AM . Last Modified: ‎2024-04-05 03:03 AM

0 Likes
0
1971
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:14 AM . Last Modified: ‎2024-04-05 03:03 AM

Hi Javier,

Many thanks - will look into the logs and get back to you as soon as possible,

Kind regards

(CID:128751028)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 04:14 AM . Last Modified: ‎2024-04-05 03:03 AM

0 Likes
0
1971
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:14 AM . Last Modified: ‎2024-04-05 03:03 AM

Hi Javier,

I will contact you directly (by email) soon, thanks.

Kind regards

(CID:128751352)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 04:15 AM . Last Modified: ‎2023-10-22 01:41 AM

0 Likes
0
1971
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:15 AM . Last Modified: ‎2023-10-22 01:41 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore