DCO Import from DCE RPDU measured load issue

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCO Import from DCE RPDU measured load issue
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
127
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:16 PM . Last Modified: ‎2024-04-07 11:56 PM

0 Likes
19
1899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:16 PM . Last Modified: ‎2024-04-07 11:56 PM

DCO Import from DCE RPDU measured load issue

Hi Team,

I have a project with DCE and DCO integration. I have rack PDUs from different providers, APC, Eaton and Dell.

In DCE I can see the power load of all PDUs, but in DCO when I associate the external devices to each rack PDU, I can only see the measured load of APC PDUs.

Is not possible to see in DCO the measured load of rack PDUs that are not from APC? I have the Capacity module installed.

Thanks in advance

(CID:122692923)

Labels
  • Labels:
  • Data Center Expert
  • Data Center Operation
  • DDF
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 19
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:16 PM . Last Modified: ‎2024-04-07 11:56 PM

0 Likes
17
1899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:16 PM . Last Modified: ‎2024-04-07 11:56 PM

Hi Javier

this is a DCE DDF issue. There are several posts about this (1 from me I think) and doco describing exactly what's needed.  Have a search on EcoStruxure IT Help Center.  If u still can't find repost and I'll try to dig it out

cheers

(CID:122692960)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:16 PM . Last Modified: ‎2024-04-07 11:55 PM

In response to DCIM_Support
0 Likes
0
1899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:16 PM . Last Modified: ‎2024-04-07 11:55 PM

Thank You Ed,

I think I found It:

http://sxwhelpcenter.ecostruxureit.com/display/public/DCIMDEVELOPER/DCE+Sensor+Mapping+to+DCO

I requested the DDF files for these PDUs last week , could they be wrong? I checked the XML DDF files and seems they are ok, at least the OUTPUT_POWER_TOTAL OID exists.

Regards

 

(CID:123342925)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:16 PM . Last Modified: ‎2024-04-07 11:55 PM

In response to DCIM_Support
0 Likes
0
1899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:16 PM . Last Modified: ‎2024-04-07 11:55 PM

Hi Javier

Perhaps older DDFs may need an update or two?  I recommend going back to SE and specifying you need the rPDU DDFs to work with DCO:Capacity.

If you feel adventurous / want to confirm exactly where the problem lies, you can check exactly what DCE is presenting by using www.SoapUI.org and accessing the DCE device and sensor API for the devices in question.

Cheers

(CID:123342927)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:16 PM . Last Modified: ‎2024-04-07 11:55 PM

In response to DCIM_Support
0 Likes
0
1899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:16 PM . Last Modified: ‎2024-04-07 11:55 PM

Hi Javier Zurera

This is embarrassing - I'd like to assist you - could you list the rack PDU's that you are having issues with? Or perhaps point me to the requests you have made for the DDF's.?

Best regards

     Anders

 

(CID:123342929)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:16 PM . Last Modified: ‎2024-04-07 11:55 PM

In response to DCIM_Support
0 Likes
0
1899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:16 PM . Last Modified: ‎2024-04-07 11:55 PM

Hi Anders,

 

now DCO import the power load from Eaton rPDUs in DCE but the values are not correct. I think DCO does not know with values has to import. 

 

I think it should be the addition of Input1 Real Power1 and Input1 Real Power 2. I have attached pictures of both sytems. 

 

With Dell rPDUs DCO does not import any data

 

 

Thanks in advance.

(CID:123342879)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:16 PM . Last Modified: ‎2024-04-07 11:55 PM

In response to DCIM_Support
0 Likes
0
1899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:16 PM . Last Modified: ‎2024-04-07 11:55 PM

Hi,

these are the rPDU models:

 

Dell 6608 --> does not import load from DCE

Eaton eMAA13 --> import incorrect values from DCE

Eaton EMAB05 --> import incorrect values from DCE

APC AP8953 --> works fine

 

Regards

 

(CID:123342931)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:16 PM . Last Modified: ‎2024-04-07 11:55 PM

In response to DCIM_Support
0 Likes
0
1899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:16 PM . Last Modified: ‎2024-04-07 11:55 PM

Excellent Javier Zurera

I'll investigate and get back to you.

Best Regards

    Anders

(CID:123342912)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:16 PM . Last Modified: ‎2024-04-07 11:55 PM

In response to DCIM_Support
0 Likes
0
1899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:16 PM . Last Modified: ‎2024-04-07 11:55 PM

Hi team,

we have also another issue. With Eaton rPDUs we can see only humidity sensor in DCO, it does not import temperature values from DCE. With Dell and APC rPDUs both sensors work fine.

Regards

(CID:123342916)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:17 PM . Last Modified: ‎2024-04-07 11:55 PM

In response to DCIM_Support
0 Likes
0
1899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:17 PM . Last Modified: ‎2024-04-07 11:55 PM

Hi Javier Zurera

we will investigate the Eaton rPDU temperature problem as well.

/Anders

(CID:123342914)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:17 PM . Last Modified: ‎2024-04-07 11:55 PM

In response to DCIM_Support
0 Likes
0
1899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:17 PM . Last Modified: ‎2024-04-07 11:55 PM

Thank you team,

these rPDUs are part of a pilot test that we are doing with Repsol in Spain. The scope of the final project is very big, including DCO and DCE deployment in all the data centers that Repsol have over the world.

For us is very important that these kind of rPDUs can be measured with DCO because they have the same rPDUs in all the data centers. For Repsol is a critical point to finally decide which DCIM provider they will contract.

So please, make your best effort to solve this problem.

Best regards.

(CID:123342891)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:17 PM . Last Modified: ‎2024-04-07 11:55 PM

In response to DCIM_Support
0 Likes
0
1899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:17 PM . Last Modified: ‎2024-04-07 11:55 PM

Javier Zurera we are working on it - you will get contacted by Amaresh in the near future.

Best regards

   Anders

(CID:123342900)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:17 PM . Last Modified: ‎2024-04-07 11:55 PM

In response to DCIM_Support
0 Likes
0
1899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:17 PM . Last Modified: ‎2024-04-07 11:55 PM

Thank you Anders Thorbjørn Jensen and Amaresh.

We have realiazed thate there is also an error displaying the name of the Eaton rPDUs on DCO.The customer have a lot of Eaton rPDUs and is very difficult to iddentify which one belongs to each rack without the name, we have to check the IP address in both systems.

Maybe you can also fix this. These are the details:

In DCO in the field Label we see the model name of the rPDU:

You can see this information in the top right side of Eaton rPDU config page in the  model field:

 

The correct name should be got from the field Hostname that is established in the Network settings page configuration:

 

Best regards

 

(CID:123342870)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:17 PM . Last Modified: ‎2024-04-07 11:55 PM

In response to DCIM_Support
0 Likes
0
1899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:17 PM . Last Modified: ‎2024-04-07 11:55 PM

Hi Javier Zurera,

I made the necessary changes and a new version of DDF is submitted in the corresponding Device Support ticket you have created. Kindly test it and let me know the results.

Regards,

Ragupathy Kandasamy.

(CID:123342904)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:17 PM . Last Modified: ‎2024-04-07 11:55 PM

In response to DCIM_Support
0 Likes
0
1899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:17 PM . Last Modified: ‎2024-04-07 11:55 PM

Hi Javier Zurera,

With reference to the changes required for Dell 6608 rPDU, we are awaiting information requested by us on the corresponding Device Support ticket created by you. Once we receive them, we will proceed with the changes.

Regards,

Divya Shankar

(CID:123342902)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:17 PM . Last Modified: ‎2024-04-07 11:55 PM

In response to DCIM_Support
0 Likes
0
1899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:17 PM . Last Modified: ‎2024-04-07 11:55 PM

Hi Divya,

tomorrow I will check the new DDFs for Eaton rPDUs in customer site. I will also take the captures for Dell equipment and attach them to the related Device Support ticket.

Regards

 

 

(CID:123342893)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:17 PM . Last Modified: ‎2024-04-07 11:55 PM

In response to DCIM_Support
0 Likes
0
1899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:17 PM . Last Modified: ‎2024-04-07 11:55 PM

Hello Javier Zurera,

We recently learnt that there currently does not exist a valid DCO mapping for any of the listed items (Input Power, Peak Power, Average Power, Peak Current). This information has been navigated to the DCE team to obtain further clarity on the possibility of providing DCO support and we are awaiting reply from the concerned team. Please do not test the DDF (Version 10) which was recently provided. We apologies for the inconvenience caused.

I will keep you posted regarding any updates from DCE team.

Regards, 
Ragupathy Kandasamy.

(CID:123342863)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:17 PM . Last Modified: ‎2024-04-07 11:55 PM

In response to DCIM_Support
0 Likes
0
1899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:17 PM . Last Modified: ‎2024-04-07 11:55 PM

Hi Javier

Good to hear your prof of concept went well and that we were able to help you solve some of it.

We will work with the remaining outstanding issues regarding your devices that need support in DCO.

kind regards

Jesper Thomsen

(CID:123343803)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:18 PM . Last Modified: ‎2024-04-07 11:55 PM

In response to DCIM_Support
0 Likes
0
1899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:18 PM . Last Modified: ‎2024-04-07 11:55 PM

Hi Javier Zurera,

I have made the required changes and submitted the updated DDF on the corresponding Device Support ticket created by you. With these changes, DCO can import load from DCE. Please test and confirm the results.

Regards,

Divya Shankar

(CID:123343900)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:18 PM . Last Modified: ‎2023-10-22 01:38 AM

0 Likes
0
1899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:18 PM . Last Modified: ‎2023-10-22 01:38 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore