Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

DCO 8.2.12 snmp monitoring issue

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Re: DCO 8.2.12 snmp monitoring issue
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
160
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 02:12 PM . Last Modified: ‎2024-04-04 12:15 AM

0 Likes
6
1831
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:12 PM . Last Modified: ‎2024-04-04 12:15 AM

DCO 8.2.12 snmp monitoring issue

Hello,

When we upgraded DCO to version 8.2.12, we noticed that DCE->DCO monitoring didn't work anymore. DCE, which was upgraded at same time with DCO to version 7.6.0 gives an error message 'Unknown status code for essential services' for DCO. 

We have imported 'schneiderops.xml' file to DCE, data content seems equal with previous version. Should we get a new file for DCO 8.2.12 or what can be wrong in our setup.

Regards,

 Michael

 

 

(CID:136153038)

Labels
  • Labels:
  • Data Center Expert
  • Data Center Operation
  • Tags:
  • bug
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 02:12 PM . Last Modified: ‎2024-04-04 12:15 AM

0 Likes
4
1831
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:12 PM . Last Modified: ‎2024-04-04 12:15 AM

Hi Micheal,

I could reproduce the similar alarm notification in my setup as well. I have registered a bug report for this.

Thanks,

Kind regards 

 

---

update:

Fixed/resolved in DCO 8.3

(CID:136153093)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 02:12 PM . Last Modified: ‎2024-04-04 12:15 AM

0 Likes
4
1832
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:12 PM . Last Modified: ‎2024-04-04 12:15 AM

Hi Micheal,

I could reproduce the similar alarm notification in my setup as well. I have registered a bug report for this.

Thanks,

Kind regards 

 

---

update:

Fixed/resolved in DCO 8.3

(CID:136153093)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 02:12 PM . Last Modified: ‎2024-04-04 12:15 AM

In response to DCIM_Support
0 Likes
0
1831
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:12 PM . Last Modified: ‎2024-04-04 12:15 AM

Hi

I have updated DCO to version 8.2.12 and in DCE, I get the same error code of unknown status for essential services, please I need your help.

(CID:140216823)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 02:13 PM . Last Modified: ‎2024-04-04 12:14 AM

In response to DCIM_Support
0 Likes
0
1831
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:13 PM . Last Modified: ‎2024-04-04 12:14 AM

Hi Caroll,

It is included in our bug reports and not resolved yet - I think it is expected to be fixed in a near future release version. 

Kind regards

(CID:140216826)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 02:13 PM . Last Modified: ‎2024-04-04 12:14 AM

In response to DCIM_Support
0 Likes
0
1831
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:13 PM . Last Modified: ‎2024-04-04 12:14 AM

it's okay. query, this error does not affect any function, right?

 

regards

(CID:140218156)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 02:13 PM . Last Modified: ‎2024-04-04 12:14 AM

In response to DCIM_Support
0 Likes
0
1831
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:13 PM . Last Modified: ‎2024-04-04 12:14 AM

Hi Caroll,

No, it dose not affect any function.

Kind regards

(CID:140218441)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 02:13 PM . Last Modified: ‎2023-10-22 01:32 AM

0 Likes
0
1831
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:13 PM . Last Modified: ‎2023-10-22 01:32 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore