DCE device hostname resolution

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCE device hostname resolution
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:39 PM . Last Modified: ‎2024-04-08 12:29 AM

0 Likes
8
1200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:39 PM . Last Modified: ‎2024-04-08 12:29 AM

DCE device hostname resolution

Hi,

My End User is having issues with resolving a monitored device IP to the given hostname in DCE monitoring. This seems to be happening for a specific UPS unit which has like the rest of the monitored devices been registered on the DNS server. The UPS is running NMC firmware version 6.4.6 and the End User is able to get the name resolved on the network. 

It is only on the DCE desktop client that the IP is not resolving to the hostname as we have tested using the network troubleshooting tools on the DCE web interface and we are able to resolve the IP to Hostname.

The UPS was discovered and left for 2 days with the hostname still showing the IP address instead. Is there something we are perhaps overlooking? Is this an isolated issue?

DCE is currently running v7.4.0. 

Any suggestions on how we can troubleshoot and resolve this issue?

 

Kevin

(CID:120129751)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:39 PM . Last Modified: ‎2024-04-08 12:29 AM

0 Likes
6
1199
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:39 PM . Last Modified: ‎2024-04-08 12:29 AM

Hi Kevin,

 

Any testing I've done in the lab here was pretty quick to update the IP to hostname on the DCE server. It's been that easy here for quite some time. You mention is it only one UPS doing this. I'm assuming the customer have other devices that are working OK,

How are these different (working vs not working)?

Are they on different network segments?

Are hey all in the same DNS server? 

Do both working and not working have both forward and reverse lookup?

Have you rebooted the DCE server?

Does a local laptop use the same DNS server? Can it ping or do a lookup on the UPS by hostname? Other devices?

It should just work but have you tried removing and re-adding the device?

 

Steve

 

(CID:120129787)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:39 PM . Last Modified: ‎2024-04-08 12:29 AM

In response to DCIM_Support
0 Likes
0
1199
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:39 PM . Last Modified: ‎2024-04-08 12:29 AM

Hi Steve

Thanks to Kevin for assisting here, I am the end user.

Answers to your questions:

How are these different (working vs not working)? - No, we have not had any of the UPS's or PDU's on the DNS, and hence they've all shown just the IP address in the hostname field, this is causing a problem on the reports, as we have almost 1500 devices, and a list of IP's does not help. We are now trying to add them to DNS in order to resolve a sensible name on the application and report. We have added a few devices to the DNS in order to get it working, once we have the process sorted, we will add the remainder. None of the units added to our DNS are resolving.

Are they on different network segments? Yes, they all on different segments / subnets, but all routed appropriately, so pingable and accessible from the main DCE subnet. Using the resolve tools on the UPS, it can resolve the name and IP from the DNS.

Are hey all in the same DNS server? Yes, all on one DNS server, and also the same DNS server for the DCE.

Do both working and not working have both forward and reverse lookup? None working, and forward and reverse look up confirmed working. Checked with a seperate machine in the same subnet as DCE, another machine in the same subnet as the one main test UPS in my lab, using DCE web to verify the reverse and forward lookup, as well as the onboard DNS check tools on the UPS web interface, all resolve the name from IP, and IP from name.

 Have you rebooted the DCE server? Yes,  numerous times, just tried another reboot 10 minutes ago.

Does a local laptop use the same DNS server? Can it ping or do a lookup on the UPS by hostname? Other devices? Yes, it uses the same DNS, and can ping and do lookup on UPS by Hostname. DCE and the test UPS's

It should just work but have you tried removing and re-adding the device? Yes, also removed it from the "saved discoveries" rebooted the server, and tried a new discovery....numerous times....

 

I really hope you can assist with any other tests to resolve this.

 

Please let me know if any further info is required.

 

Regards

Steven

 

 

 

(CID:120129941)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:39 PM . Last Modified: ‎2024-04-08 12:29 AM

In response to DCIM_Support
0 Likes
0
1199
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:39 PM . Last Modified: ‎2024-04-08 12:29 AM

Hi Steven,

 

Sorry I didn't get back to you sooner.

IN my experience, if DCE has the correct DNS entries and DNS has forward and reverse lookups, it should just work.

Is this a hardware server? 

If hardware or VM with public and private networks, are the public and private IP schemes different? (something like 10.10.x.x on one side and 192.168.x.x on the other)

If you go here:

http:///nbc/status/Troubleshoot

Can you ping and resolve by hostname / fqdn?

 

Steve

(CID:120130296)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:39 PM . Last Modified: ‎2024-04-08 12:29 AM

In response to DCIM_Support
0 Likes
0
1201
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:39 PM . Last Modified: ‎2024-04-08 12:29 AM

Hi Steve

I logged onto the server late yesterday....and the devices I added to DNS on friday, that did not resolve on Friday were resolved yesterday in DCE, so it is working.

 

The additional question now, is what is a reasonable wait time before resolving, is there a way to speed it up?  A few minutes would be OK, but 24 or 48 hours seems too long, any settings I can look at to improve this?

 

Thanks

Steven

 

(CID:120130656)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:39 PM . Last Modified: ‎2024-04-08 12:29 AM

In response to DCIM_Support
0 Likes
0
1201
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:39 PM . Last Modified: ‎2024-04-08 12:29 AM

Hi Steven,

 

There are no settings that you can change specific to this functionality. From what I have experienced in my lab with 50-80 devices, it usually takes less than an hour to resolve. I have seen some quicker.

If your system i staking 24-48 hours, maybe you should check resources. Either increase RAM / disk space (if it's a VM, be sure to add a new disk and not increase the default 18g drive) or slow polling down to see if you can speed other actions up. If you've also got NetBotz and use surveillance, changing frame rate and resolution to lower settings will allow the system to perform other actions that it may be unable to perform otherwise. 

 

Maybe even test with a trial VM. Add a single device that has a hostname. If it's taking forever in that configuration, perhaps there are VM host or network related issues.

 

Thanks,

Steve.

(CID:120130725)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:39 PM . Last Modified: ‎2024-04-08 12:29 AM

In response to DCIM_Support
0 Likes
0
1201
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:39 PM . Last Modified: ‎2024-04-08 12:29 AM

Thanks Steve

I will add a few more devices to DNS and check how long it takes to resolve. Do I need to remove and re-add them, or will hostname automatically resolve if it finds it in DNS?

 

To answer the above questions:

The server is VM based, we have allocated additional storage of which we are using 24%. (Separate 100G drive). We also only have a private IP scheme, one internal IP.

Maybe it is RAM limited, I dont know. How do I find the quantity of RAM installed / used? is there, this may assist.

 

We have one x Netbotz installed as test only.

 

Thanks

Steven

(CID:120130742)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:39 PM . Last Modified: ‎2024-04-08 12:29 AM

In response to DCIM_Support
0 Likes
0
1201
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:39 PM . Last Modified: ‎2024-04-08 12:29 AM

Hi Steven,

 

I would be guessing if I said it will work more quickly one way or the other but in both cases, device already added or device added after DNS entries (forward and reverse) configured, the hostname will eventually get associated with the device in DCE.


Steve

(CID:120130748)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:40 PM . Last Modified: ‎2023-10-22 01:24 AM

0 Likes
0
1201
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:40 PM . Last Modified: ‎2023-10-22 01:24 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore