Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

DCE API

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Re: DCE API
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
TS1
TS1
Explorer

Posted: ‎2024-12-01 11:31 PM . Last Modified: ‎2024-12-01 11:37 PM

0 Likes
4
1523
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-01 11:31 PM . Last Modified: ‎2024-12-01 11:37 PM

DCE API

Hi, 

 

Exploring the option of using the SOAP Api calls associated with DCE to get the below details for the UPS or any power devices:
  1. Input Voltage
  2. UPS on Battery
  3. Battery Faults

DCE Dashboard version: 7.5

Please let me know if there are any options to get the above details.

 

 

Labels
  • Labels:
  • Data Center Expert
  • Tags:
  • DCE API
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
Cory_McDonald
Cory_McDonald Champion
Champion

Posted: ‎2024-12-04 04:34 AM

1 Like
2
1497
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-04 04:34 AM

Hello @TS1,

 

I would recommend doing any integrations with Rest API for DCE, which is available starting in DCE version 8.1.0: https://community.se.com/t5/DCE-FAQ/Data-Center-Expert-REST-API/ta-p/463059

 

To do the level of filtering that you are looking for you will have to parse data within your application or polling utility.

1. For input voltage, you will need to poll the /v1/sensors/type/{type} for type of NUMBER and then filter the data further within your tool to look for specific kind of "voltage" and label of "Input Voltage".  This will give you all input voltages for all devices in DCE. 

 

Cory_McDonald_0-1733315467876.png

 

 

If you are only looking for a specific devices input voltage, you can instead use the /v1/devices/{guid}/sensors call and use the GUID of the device in question to poll all of its sensors and then do the filtering.

 

It is recommended that if you are building polls that will reoccur that you store the GUID's of the devices and sensors that you need and you can then do very specific calls for the data in question instead of polling all data each time, which may cause you to reach the rate limit of the API.

 

2. Similar to #1 you can instead use the /v1/alarms to poll all alarms and then parse for the specific text string you desire in the "description" field.

 

You can also poll alarms for specific devices using the /v1/devices/{guid}/alarms call.

 

3. Same process as #2.

 

Kind Regards,
Cory

Reply

Link copied. Please paste this link to share this article on your social media post.

TS1
TS1
Explorer

Posted: ‎2024-12-04 08:39 PM

In response to Cory_McDonald
0 Likes
1
1465
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-04 08:39 PM

 

Thanks Cory for the response. But currently DCE dashboard version is 7.5. Is it possible to get the details such as input voltage, battery faults , ups on battery  using the SOAP API calls. 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Shaun
Shaun Leader
Leader

Posted: ‎2024-12-05 04:06 AM

0 Likes
0
1452
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-05 04:06 AM

Hi @TS1,

 

There's really no shortcut to this in the SOAP API.  You need to use getSensorsForDevice() from the SensorService endpoint to list out the sensors available, record the IDs for the ones you're interested in, and then getSensorData() (from the same endpoint) to retrieve the values.

 

It's difficult to provide shortcuts to get to specific data, because .. for example, batteries - does the device have a battery, two batteries, battery modules, battery strings, battery frames, a BMS, etc. The sensors available for a device will vary wildly depending on the device itself.

 

(Aside: For new integrations, I really would recommend upgrading to a current version to get access to the REST API.  I've been using the SOAP API for years and I will not miss it. A small time investment now will have ongoing payoff.)

Reply

Link copied. Please paste this link to share this article on your social media post.

Cory_McDonald
Cory_McDonald Champion
Champion

Posted: ‎2024-12-05 06:11 AM

In response to TS1
0 Likes
0
1431
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-05 06:11 AM

Hello @TS1,

 

I highly recommend upgrading DCE as you are currently on an unsupported version.  You can check out our End of Life policy here so you know which versions of DCE are currently supported: https://community.se.com/t5/EcoStruxure-IT-Policies/End-of-Life-Policy/ta-p/446509

 

As an FYI, DCE 7.5 has been end-of-life about 5 years ago in December 2019.

 

Kind Regards,

Cory

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore