Posted: 2026-04-22 05:47 AM
We’ve received a POA&M related to a security vulnerability and wanted to reach out for your expertise. Our initial research suggests that the issue is linked to the DCE Proprietary Rocky-Linux OS, specifically concerning Python 3.6— has reached end-of-life.
Currently, we are running version 8.1.1 in production, and even the latest release (9.1.1) continues to rely on Proprietary Rocky-Linux 8.10, which includes the same Python 3.6 version. Since Python 3.6 is hard coded at the OS level, patching or updating it isn't possible through the usual channels.
Given these constraints, we’re reaching out to ask for your guidance and recommendations on how best to address this vulnerability moving forward. Any insights or suggestions you can share would be greatly appreciated.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-04-22 10:38 AM
did you have a specific CVE or ERRATA that your security team flagged? Red Hat and Rocky Linux backport security fixes so a package version by itself isn't enough to determine if it is vulnerable.
https://access.redhat.com/solutions/57665
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-04-23 08:33 AM
No specifc CVE associated here is the Plugin ID and the output
Plugin ID: 148367
Plugin Output:
The following Python installation is unsupported :
Path : /
Port : 443
Installed version : 2.7.18
Latest version : 3.10
Support dates : 2020-01-01 (end of life)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-04-25 07:21 AM
Dear @Irizarrym,
Yes, Rocky Linux 8 (8.10), which is used by the current DCE IT appliance, is far from new and has a significant list of outdated packages. However, since it is a direct clone of RHEL-8, according to the official explanation of https://access.redhat.com/support/policy/updates/errata#RHEL8_Planning_Guide, this OS can still be used until 2029 and will receive all the necessary critical security and functionality fixes. In addition, it should be noted that:
- Packages within RHEL 8, 9, and 10 Application Streams may have a shorter life cycle than a specific RHEL minor release.
- The inclusions list below is a minimum set of packages that apply to Urgent bug fixes.
- bind, bash, chrony, grub2, grubby, glibc, gnutls, httpd, kernel, libgcrypt, libvirt, nss, openssh, openssl, python 3.6 (RHEL 8), python 3.9 (RHEL 9), python 3.12 (RHEL 10), qemu-kvm, rpm, sudo, systemd, wget, yum / dnf
Link copied. Please paste this link to share this article on your social media post.