DCE 7.6 - incorrect reading with ACRD 301
EcoStruxure IT Forum
  • Re: DCE 7.6 - incorrect reading with ACRD 301
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
Back to EcoStruxure IT Forum
tjlaw
tjlaw Mentor
Mentor
Posted: ‎2021-01-06 04:32 AM
3987
Dear All,
We are getting incorrect readings from inRow ACRD301 (rd3xx -v6.6.4k, aos - 6.6.4). The temperature values in Celcuis are read in values of Fahrenheit (the voltage values are incorrect as well) as attached. We also found that the status of Inrows are all in Standby (but in fact 2 units are running).
We are using DDF - apc_acrd2g ver 14 but no luck.
Anyone encounter this before?
BR
TJ
  • Data Center Expert
tjlaw
tjlaw Mentor
Mentor
Posted: ‎2021-01-11 05:01 PM . Last Modified: ‎2021-01-11 05:02 PM
In response to Anonymous user
Dear All,
It seems that upgrading the InRow firmware to AOS 682 solved the issue.
Closing the case.
BR,
TJ
Replies 4
Anonymous user
Not applicable
Posted: ‎2021-01-07 12:43 AM
3968
Hi TJ,
Can you do an SNMP walk of the cooler?
It is possible that this is not a DCE issue but that the cooler is presenting the wrong information to the DCE.
-Gavan
tjlaw
tjlaw Mentor
Mentor
Posted: ‎2021-01-08 06:01 AM
Hi Gavan,
Thanks for the suggestion. I will upload the walk files once I gather them.
BR,
TJ
tjlaw
tjlaw Mentor
Mentor
Posted: ‎2021-01-10 11:53 PM
Hi Gavan,
Attached with the SNMP walk from DCE.
BR,
TJ
snmp_inrow_dcewalk.txt
tjlaw
tjlaw Mentor
Mentor
Dear All,
Closing the case.
BR,
TJ