Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

DCE - 3rd party device communication lost after reboot using SNMPv3

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCE - 3rd party device communication lost after reboot using SNMPv3
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
160
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 03:20 PM . Last Modified: ‎2024-04-03 11:28 PM

0 Likes
1
845
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 03:20 PM . Last Modified: ‎2024-04-03 11:28 PM

DCE - 3rd party device communication lost after reboot using SNMPv3

Hi,

In DCE I am using SNMPv3 for monitoring wherever device is capable for that. I noticed that after device reboot I get communication lost and it will not resolve anymore in DCE.

I got internal Schneider support and did packet capture on DCE server filter to a ServerTech PDU communicate with DCE and here is the outcome from Schneider:

"This is a fault in the ServerTech PDUs; the DCE is treating this fault exactly as the SNMPv3 standard says it should.
Unfortunately this “feature” is part of the security model in SNMPv3, so it would be improper for us to alter this behaviour, as it’d then cause the DCE to weaken security and violate the standards.

Possible solutions:
- Run SNMPv3 without authorization (security) on these PDUs, as it’s a misbehaviour in this security that’s causing problems.
- Pursue this with ServerTech and see if they have a newer firmware, or any roadmap to a newer firmware that would behave correctly in this case."

Obviously first solution is not an option because I kill the essence of using SNMPv3.

The technical explanation is that vendor (ServerTech) did not implement correctly RFC3414 standard related to the following two values:

snmpEngineBoots “which is a count of the number of times the SNMP engine has re-booted/re-initialized since snmpEngineID was last configured”

snmpEngineTime “which is the number of seconds since the snmpEngineBoots counter was last incrememented”.

The strange thing is that I have the same issue with Cisco devices too. Of course everything is possible, maybe Cisco also wrongly implemented above mentioned RFC standard.

With the same internal support we did packet capture about the Cisco device but I am still waiting for feedback on that.

The reason is why opened this thread to highlight this interesting topic and encourage some other DCE users whose are using not Schneider/APC devices with SNMPv3 monitoring. Can someone test it? It is pretty simple because when you change for example the contact or location field that generate and snmpEngineBoot without any impact to the device.

A troubleshooting solution which solve the problem: restart DCE server.

I am pretty curious what is the experience with other 3rd party devices SNMPv3 monitoring.

By the way it is independent from DCE version because I experienced it with 7.5.0 as well as in the latest 7.6.0.

(CID:137111243)

Labels
  • Labels:
  • Data Center Expert
  • Tags:
  • bug
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 03:20 PM . Last Modified: ‎2023-10-22 01:09 AM

0 Likes
0
845
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 03:20 PM . Last Modified: ‎2023-10-22 01:09 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore