Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Cooling optimization (Calculated plane)

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Cooling optimization (Calculated plane)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 02:13 PM . Last Modified: ‎2024-04-04 12:14 AM

0 Likes
5
2091
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:13 PM . Last Modified: ‎2024-04-04 12:14 AM

Cooling optimization (Calculated plane)

Jef Faridi Hi jef

Its been a long time hope you're doing good

I'm preparing a cfd for our new project its for 156 racks in which we are using 6 crah units in-row cooling the details are below

2 ups: each 1200 KW- Total 2400 KW redundant

2 PDU- Power panels which are then connected to rack pdu

we are using 2 rpdu's  in each cabinet (Redundant Environment) each rpdu is connected with 63amp single phase breaker of PDU

and the load inside each cabinet is 7700 watts (7.7KW)

(i have used a generic server and kept 7700 watt in each cabinet)

 My question is when i calculate the cooling the ( calculated plane ) the average cooling seems not perfect attached are the screenshots you can check the cabinets

the right hand side cabinets are showing more temperature than the left side even though i have kept the same load in each cabinet with same size of breaker and also if the cooling unit is closed to the cabinets why the temperature is still high for those cabinets. it seems there is something wrong

On the end row the right hand side displays the normal temp while the left side here shows abnormal values and those cabinets are also close to the cooling units

 

Pls suggest and support- if anything else is required to identify the issue kindly ask

 

Regards

 

 

 

(CID:136153147)

Labels
  • Labels:
  • Data Center Operation
  • Tags:
  • bug
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 02:14 PM . Last Modified: ‎2024-04-04 12:14 AM

0 Likes
0
2091
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:14 PM . Last Modified: ‎2024-04-04 12:14 AM

Hi Waseem,

Many thanks for providing the access to your setup, which I've studied locally.

It appears basically a configuration related, there is no bug here 😀

In this setup:

you have 156 racks containing 1 server each (7.7 kW), that may give us 1201 kW power consumption in total 

you have also 6 cooling units (with 24 kW power consumption each, 144 kW in total)

heat in total: 1345 kW 

Those 6 cooling units have 138 kW cooling capacity each, so

cooling capacity in total would be: 828 kW

So it appears there is not enough cooling capacity here.

There are also some other configuration settings could be looked into:

You have perforated floor tiles, so you might want to enable the Raised floor settings and enter your floor height (right click on floor > Properties > Floor):

Cooling units contain manually defined values, such as:

Some of those numbers seem to be randomly chosen and if the calculations (behind the scene) don't add up, then we may see unexpected simulation.

Location and orientation of the floor equipment would definitely also play an import role when simulating the temperature map. 

Kind regards

(CID:136644952)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 02:13 PM . Last Modified: ‎2024-04-04 12:14 AM

0 Likes
0
2091
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:13 PM . Last Modified: ‎2024-04-04 12:14 AM

Hi Waseem, you mention in row cooling units but the images show perimeter units.  Proximity of the cabinet to the cooling unit is no guarantee of better cooling.  You can see all through the room, it's cooler in each aisle further away from CRAH. 

Also check the underfloor pressure.

You may also like to use the DCO Lab client to move the CRAHs around the room to see how each config affects cooling performance. 

Lets see what Jef Faridi says.

Cheers

Ed

 

(CID:136153410)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 02:14 PM . Last Modified: ‎2024-04-04 12:14 AM

0 Likes
0
2091
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:14 PM . Last Modified: ‎2024-04-04 12:14 AM

Hi Waseem,

Many thanks I'm fine, hope you are well too.

I've sent you an invite to my =S= box, can you please share a copy of your backup file with me, then I will take a look, thanks.

Kind regards

(CID:136153551)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 02:14 PM . Last Modified: ‎2024-04-04 12:14 AM

0 Likes
0
2091
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:14 PM . Last Modified: ‎2024-04-04 12:14 AM

Jef Faridi Hi jef

Actually it is a demo server created by Schneider for us to present the demo for our new project

I will share the details via email

Regards

(CID:136153716)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 02:14 PM . Last Modified: ‎2024-04-04 12:14 AM

0 Likes
0
2092
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:14 PM . Last Modified: ‎2024-04-04 12:14 AM

Hi Waseem,

Many thanks for providing the access to your setup, which I've studied locally.

It appears basically a configuration related, there is no bug here 😀

In this setup:

you have 156 racks containing 1 server each (7.7 kW), that may give us 1201 kW power consumption in total 

you have also 6 cooling units (with 24 kW power consumption each, 144 kW in total)

heat in total: 1345 kW 

Those 6 cooling units have 138 kW cooling capacity each, so

cooling capacity in total would be: 828 kW

So it appears there is not enough cooling capacity here.

There are also some other configuration settings could be looked into:

You have perforated floor tiles, so you might want to enable the Raised floor settings and enter your floor height (right click on floor > Properties > Floor):

Cooling units contain manually defined values, such as:

Some of those numbers seem to be randomly chosen and if the calculations (behind the scene) don't add up, then we may see unexpected simulation.

Location and orientation of the floor equipment would definitely also play an import role when simulating the temperature map. 

Kind regards

(CID:136644952)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 02:14 PM . Last Modified: ‎2023-10-22 01:07 AM

0 Likes
0
2091
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:14 PM . Last Modified: ‎2023-10-22 01:07 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore