Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Connection Failure

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Connection Failure
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:07 PM . Last Modified: ‎2024-04-04 02:39 AM

0 Likes
35
6249
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:07 PM . Last Modified: ‎2024-04-04 02:39 AM

Connection Failure

Trying to discover an APC UPS (16kVA Symmetra LX) and keep getting Connection Failure.  I have already successfully discovered twenty-sixe (26) APC UPS's.  

Does IPv6 need to be Enabled or not?

(CID:134029354)

Labels
  • Labels:
  • IT Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 35
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:07 PM . Last Modified: ‎2024-04-04 02:39 AM

0 Likes
32
6248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:07 PM . Last Modified: ‎2024-04-04 02:39 AM

Dear John Beck,

IPv6 does not need to be enabled (unless it is a standard on your network).

Please, share a few screenshots where we will clearly see how you are discovering this type of equipment (16kVA Symmetra LX) in the EcoStruxure IT Gateway software.

With respect.

(CID:134029378)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:07 PM . Last Modified: ‎2024-04-04 02:39 AM

In response to DCIM_Support
0 Likes
0
6248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:07 PM . Last Modified: ‎2024-04-04 02:39 AM

Which screenshots do you need?

(CID:134029380)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:07 PM . Last Modified: ‎2024-04-04 02:39 AM

In response to DCIM_Support
0 Likes
0
6248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:07 PM . Last Modified: ‎2024-04-04 02:39 AM

I mean a screenshot of the Device Discovery web-page, as, for example, you can see it in instruction Installing and setting up EcoStruxure IT Gateway.

(CID:134029398)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:08 PM . Last Modified: ‎2024-04-04 02:39 AM

In response to DCIM_Support
0 Likes
0
6248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:08 PM . Last Modified: ‎2024-04-04 02:39 AM

You mean the following:

 

 

(CID:134029402)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:08 PM . Last Modified: ‎2024-04-04 02:39 AM

In response to DCIM_Support
0 Likes
0
6248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:08 PM . Last Modified: ‎2024-04-04 02:39 AM

Yes, I meant this, as well as the results screen of this discovering and the corresponding log file. What is written there?

With respect.

(CID:134029431)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:08 PM . Last Modified: ‎2024-04-04 02:39 AM

In response to DCIM_Support
0 Likes
0
6248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:08 PM . Last Modified: ‎2024-04-04 02:39 AM

Results screen:

 

(CID:134029446)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:08 PM . Last Modified: ‎2024-04-04 02:39 AM

In response to DCIM_Support
0 Likes
0
6248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:08 PM . Last Modified: ‎2024-04-04 02:39 AM

logs.zip

(CID:134029449)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:08 PM . Last Modified: ‎2024-04-04 02:39 AM

In response to DCIM_Support
0 Likes
0
6248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:08 PM . Last Modified: ‎2024-04-04 02:39 AM

I have also attached the Logs

(CID:134029451)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:08 PM . Last Modified: ‎2024-04-04 02:39 AM

In response to DCIM_Support
0 Likes
0
6248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:08 PM . Last Modified: ‎2024-04-04 02:39 AM

Dear John Beck,

Thanks for the detailed information.

First you need to go to the web-GUI of this problematic UPS and make sure that the SNMP v1 protocol in its network settings is enabled. In addition, there you also need to make sure the Read community and Write community strings are correct. This is also important.

With respect.

(CID:134029588)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:08 PM . Last Modified: ‎2024-04-04 02:39 AM

In response to DCIM_Support
0 Likes
0
6248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:08 PM . Last Modified: ‎2024-04-04 02:39 AM

(CID:134030353)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:08 PM . Last Modified: ‎2024-04-04 02:38 AM

In response to DCIM_Support
0 Likes
0
6248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:08 PM . Last Modified: ‎2024-04-04 02:38 AM

Yes it is - as follows:

 

 

(CID:134029679)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:08 PM . Last Modified: ‎2024-04-04 02:38 AM

In response to DCIM_Support
0 Likes
0
6248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:08 PM . Last Modified: ‎2024-04-04 02:38 AM

The READ and WRITE Community Strings are correct. There is a 16kVA Symmetra LX UPS in the rack next to this one. It is called VE012UP1 with an IP Address of 10.48.6.48 and it is working fine and it connected to EcoStruxure IT with no problems. I have been comparing settings on the Network Management Cards of both of these and I can't see any difference.

(CID:134029682)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:09 PM . Last Modified: ‎2024-04-04 02:38 AM

In response to DCIM_Support
0 Likes
0
6248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:09 PM . Last Modified: ‎2024-04-04 02:38 AM

Dear John Beck,

Ok, for comparison, please make use of the already known PortQuery command for the request of the two above mentioned UPSs (10.48.6.46 and 10.48.6.48) using the SNMP (UDP) protocol as in the screenshot:

If it's okay, you should see something like this UDP port 161 is LISTENING.

What will you receive in return? You will have only two options: either it is a network problem (firewall, for example) or it is the NMC problem of your UPS...

With respect.

(CID:134029746)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:09 PM . Last Modified: ‎2024-04-04 02:38 AM

In response to DCIM_Support
0 Likes
0
6248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:09 PM . Last Modified: ‎2024-04-04 02:38 AM

The following Port Query is for 10.48.6.46 for VE011UP1:

 

(CID:134029774)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:09 PM . Last Modified: ‎2024-04-04 02:38 AM

In response to DCIM_Support
0 Likes
0
6248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:09 PM . Last Modified: ‎2024-04-04 02:38 AM

The following Port Query is for 10.48.6.48 for VE012UP1 (the one that is connected):

 

(CID:134029777)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:09 PM . Last Modified: ‎2024-04-04 02:38 AM

In response to DCIM_Support
0 Likes
0
6248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:09 PM . Last Modified: ‎2024-04-04 02:38 AM

Why doe the one that has connected (VE012UP1 - 10.48.6.48) say "FILTERED"?   And the one that doesn't connect (VE011UP1 - 10.48.6.46) say "LISTENING"? 

(CID:134029790)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:09 PM . Last Modified: ‎2024-04-04 02:38 AM

In response to DCIM_Support
0 Likes
0
6248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:09 PM . Last Modified: ‎2024-04-04 02:38 AM

Now, please check both UPS's web-page Configure SNMPv1 Access Control through the web-GUI (Configuration -> Network -> SNMPv1 -> Access Control).

Compare both web-pages, whether everything is the same?

(CID:134029797)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:09 PM . Last Modified: ‎2024-04-04 02:38 AM

In response to DCIM_Support
0 Likes
0
6248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:09 PM . Last Modified: ‎2024-04-04 02:38 AM

The Access Control had "Public" instead of "EHITro" - I have changed it as follows:

 

(CID:134029804)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:09 PM . Last Modified: ‎2024-04-04 02:38 AM

In response to DCIM_Support
0 Likes
0
6248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:09 PM . Last Modified: ‎2024-04-04 02:38 AM

So I ran the discovery again and the following was the result:

 

(CID:134029827)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:09 PM . Last Modified: ‎2024-04-04 02:38 AM

In response to DCIM_Support
0 Likes
0
6246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:09 PM . Last Modified: ‎2024-04-04 02:38 AM

I.e., if on both UPS's Read community string = EHITro, then exact this string you need paste in doscovery dialog gateway software. This is first.

Secondly, for all native Schneider Electric devices Write community string must be enabled (Write+). This is necessary for priority scanning, i.e. for operational allerting. Since you have shown in the screenshot, this option will not work.

With respect.

(CID:134029838)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:10 PM . Last Modified: ‎2024-04-04 02:38 AM

In response to DCIM_Support
0 Likes
0
6246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:10 PM . Last Modified: ‎2024-04-04 02:38 AM

I also re-ran the discovery for another UPS (VE222UP1) and it came up with the same thing as follows:

 

(CID:134029842)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:10 PM . Last Modified: ‎2024-04-04 02:38 AM

In response to DCIM_Support
0 Likes
0
6246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:10 PM . Last Modified: ‎2024-04-04 02:38 AM

Is there something going on with the EcoStruxure IT Gateway?  I now have 26 devices (UPS's) not responding. 

(CID:134029848)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:10 PM . Last Modified: ‎2024-04-04 02:38 AM

In response to DCIM_Support
0 Likes
0
6246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:10 PM . Last Modified: ‎2024-04-04 02:38 AM

See my comment about Write community string. Additionaly, please check the UPS's web-pages Configuration -> Network -> FTP server and Configuration -> Security -> Firewall -> Configuration. FTP server must be enabled and Firewall must be disabled.

(CID:134029851)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:10 PM . Last Modified: ‎2024-04-04 02:38 AM

In response to DCIM_Support
0 Likes
0
6246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:10 PM . Last Modified: ‎2024-04-04 02:38 AM

From your comment:

Is there something going on with the EcoStruxure IT Gateway?  I now have 26 devices (UPS's) not responding.

Maybe you have a change in the network or on the firewall? Check the log files on your UPS. What can be seen, can a network flood or something else?..

With respect.

(CID:134029854)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:10 PM . Last Modified: ‎2024-04-04 02:38 AM

In response to DCIM_Support
0 Likes
0
6246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:10 PM . Last Modified: ‎2024-04-04 02:38 AM

All twenty-six (26) of our APC UPS's have the SNMP v1 Access Control as follows:

 

 

(CID:134029868)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:10 PM . Last Modified: ‎2024-04-04 02:38 AM

In response to DCIM_Support
0 Likes
0
6246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:10 PM . Last Modified: ‎2024-04-04 02:38 AM

The FTP Server Access is as follows:

 

(CID:134029872)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:10 PM . Last Modified: ‎2024-04-04 02:38 AM

In response to DCIM_Support
0 Likes
0
6246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:10 PM . Last Modified: ‎2024-04-04 02:38 AM

This is good, but the Access Type for private Community Name must be definitely Write+. This requirement of EcoStruxure IT Gateway software is important.

If you are worried about security, then allow private Community Name only for the IP address of your server with the gateway software (NMS IP/Host Name).

With respect.

(CID:134029877)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:10 PM . Last Modified: ‎2024-04-04 02:38 AM

In response to DCIM_Support
0 Likes
0
6246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:10 PM . Last Modified: ‎2024-04-04 02:38 AM

The Firewall Configuration is disabled as follows:

 

 

(CID:134030357)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:10 PM . Last Modified: ‎2024-04-04 02:38 AM

In response to DCIM_Support
0 Likes
0
6246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:10 PM . Last Modified: ‎2024-04-04 02:38 AM

The twenty-six (26) UPS's we have that have connected to EcoStruxure IT Gateway (but not at the moment) have "private" "public2" and "private2" ALL with Access Type of "Disabled".

(CID:134029907)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:11 PM . Last Modified: ‎2024-04-04 02:37 AM

In response to DCIM_Support
0 Likes
0
6246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:11 PM . Last Modified: ‎2024-04-04 02:37 AM

For the above reason, this is not good...

(CID:134029917)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:11 PM . Last Modified: ‎2024-04-04 02:37 AM

In response to DCIM_Support
0 Likes
0
6246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:11 PM . Last Modified: ‎2024-04-04 02:37 AM

My point is - they are working (connecting) on EcoStruxure IT Gateway

(CID:134029933)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:11 PM . Last Modified: ‎2024-04-04 02:37 AM

In response to DCIM_Support
0 Likes
0
6246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:11 PM . Last Modified: ‎2024-04-04 02:37 AM

Also, I have the EcoStruxure IT Gateway installed on my work laptop, this means that when I leave work and my laptop is shut off the Gateway is also. Should I have the EcoStruxure IT Gateway installed on a standalone server (Physical or Virtual)?

(CID:134029949)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:13 PM . Last Modified: ‎2024-04-04 02:37 AM

In response to DCIM_Support
0 Likes
0
6246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:13 PM . Last Modified: ‎2024-04-04 02:37 AM

Dear John Beck,

From your comments:

...Should I have the EcoStruxure IT Gateway installed on a standalone server (Physical or Virtual)?

Yes, of course. This is the only way to do it, otherwise I do not see the point in this all.

After all, when you shut off your working laptop, the entire connected system of your UPS's, your gateway software, the network, the SE cloud servers and your mobile app falls into one big mistake 😀.

More details about the system requirements for the gateway server hardware operating in 24/7 mode can be found in topic System requirements:

Server
  • A server, or a PC that is always on, with Microsoft® Windows® 7 64-bit, Windows 2008 R2 SP1 64-bit or greater operating system
  • At least 2 core and 4GB of RAM
  • 2GB hard disk space

EcoStruxure IT Gateway was tested on Microsoft Windows Server 2008 R2 SP1, Server 2012 SP1, and Server 2016.

The application takes 225MB of disk space, and the server retains a maximum of 8 days of data, about 128MB per day.

Scale for small, medium, and large installations
Size
Number of devices
Number of sensors
RAM
CPU
Size on disk
Small 250 34,000 4GB 2 128MB per day
Medium 2000 270,000 8GB 8 512MB per day
Large 5000 540,000 16GB 24 1.1GB per day

_

Firewall
  • Port 443 TCP outbound
  • To connect using static IPs, add 40.84.62.190 and 23.99.90.28

If you have any more questions, please ask.

With respect.

(CID:134030351)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:13 PM . Last Modified: ‎2024-04-04 02:37 AM

0 Likes
0
6246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:13 PM . Last Modified: ‎2024-04-04 02:37 AM

Dear John Beck,

Tell us, please, did you solve your problem or not?

With respect.

(CID:134680032)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:13 PM . Last Modified: ‎2023-10-20 05:10 AM

0 Likes
0
6246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:13 PM . Last Modified: ‎2023-10-20 05:10 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore