Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Connecting multiple Camera Pod 165's to a NetBotz Wall Monitor 755

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Re: Connecting multiple Camera Pod 165's to a NetBotz Wall Monitor 755
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
160
Jef
Jef Leader
114
gsterling
gsterling Mentor
79
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
maayre
maayre
Contributor

Posted: ‎2025-09-10 11:58 AM

0 Likes
3
1722
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-10 11:58 AM

Connecting multiple Camera Pod 165's to a NetBotz Wall Monitor 755

According to the NetBotz 5.x User Guide, you can use a network switch or hub to connect up to four cameras - presumably including Camera Pod 165's to a NetBotz Wall Monitor 755 via the Private LAN port.

 

Can anybody recommend a manufacturer, model they have used to complete the above successfully.

 

Thanks in advance.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
maayre
maayre
Contributor

Posted: ‎2025-11-20 09:42 AM

In response to maayre
0 Likes
0
1295
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-20 09:42 AM

All,

Related to this topic:

 

Following testing, I can confirm that it is possible to connect two Camera Pod 165's to a single NetBotz Wall Monitor 755 by means of connecting them to the Netgear GS305P 5-Port Gigabit PoE+ Compliant Unmanaged Network Switch and then connecting this to the Private LAN port.

 

Initially, one of the two Camera Pod 165's was reported as Not Authorized under the Devices screen, but after deleting the device and then rebooting the NetBotz Wall Monitor 755 it was then accessible.

 

NOTE: The Netgear GS305P 5-Port Gigabit PoE+ Compliant Unmanaged Network Switch has a PoE budget up to 63W Total so two Camera Pod 165's as required in this instance is possible, however, there is a model that supports up to 90W total so could potentially support three.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
JLehr
JLehr Champion
Champion

Posted: ‎2025-09-22 12:11 PM

1 Like
2
1684
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-22 12:11 PM

Hi @maayre 

To be clear, the user guide states:

 

You can connect a network switch or hub to the Private LAN ports to connect up to ten downstream devices, including up to four cameras. Performance may vary depending on the amount of video recorded or the number of sensors attached to your downstream devices.

 

Cameras refers to the NetBotz Camera Pod 165.

 

Please note that successful deployment will vary depending on factors other than hub/switch hardware.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

maayre
maayre
Contributor

Posted: ‎2025-09-22 01:56 PM

In response to JLehr
0 Likes
1
1656
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-22 01:56 PM

Thanks for your reply @JLehr.

 

A couple of related updates for your and the wider groups awareness:

 

  1. Having separately consulted the EcoStruxure IT Data Center Expert Technical Support team - who also support NetBotz devices, they stated that Schneider Electric do not have a recommended manufacturer or model network switch or hub to be used in such instances.
  2. Having also consulted a member of our Network Services team, they suggested the Netgear GS305P 5-Port Gigabit PoE+ Compliant Unmanaged Network Switch as a possible option.

Does anybody in the community have experience either with the suggested switch or with a multi Camera Pod 165 set-up to a single NetBotz Wall Monitor 755? Please advise.

Reply

Link copied. Please paste this link to share this article on your social media post.

maayre
maayre
Contributor

Posted: ‎2025-11-20 09:42 AM

In response to maayre
0 Likes
0
1295
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-20 09:42 AM

All,

Related to this topic:

 

Following testing, I can confirm that it is possible to connect two Camera Pod 165's to a single NetBotz Wall Monitor 755 by means of connecting them to the Netgear GS305P 5-Port Gigabit PoE+ Compliant Unmanaged Network Switch and then connecting this to the Private LAN port.

 

Initially, one of the two Camera Pod 165's was reported as Not Authorized under the Devices screen, but after deleting the device and then rebooting the NetBotz Wall Monitor 755 it was then accessible.

 

NOTE: The Netgear GS305P 5-Port Gigabit PoE+ Compliant Unmanaged Network Switch has a PoE budget up to 63W Total so two Camera Pod 165's as required in this instance is possible, however, there is a model that supports up to 90W total so could potentially support three.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.