Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Connect data sensor from DCIM server (DCE 7.2) to other SCADA server

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Connect data sensor from DCIM server (DCE 7.2) to other SCADA server
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
anthichi
anthichi
Explorer

Posted: ‎2021-05-18 08:24 AM

1 Like
4
2460
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-05-18 08:24 AM

Connect data sensor from DCIM server (DCE 7.2) to other SCADA server

As my question, how can i export the sensor data from Data Center Expert 7.2 server (DCIM) to other SCADA server.  I have two Supervisor system, one is DCIM and other with modbus RTU device support , now how could we use other server to supervise the device/ sensor which added into DCIM. I also search some solution like using "Modbus Tcp output module", is there other way to connect ? which is the best ? Thank you.

 

  • Tags:
  • datacenter expert
  • dce
  • DCIM
  • english
  • modbus RTU export
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
APC_Steve
APC_Steve Leader
Leader

Posted: ‎2021-05-24 05:11 AM

0 Likes
3
2441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-05-24 05:11 AM

Hi @anthichi ,

 

We don't have a Scada specific option. We do have the modbus TCP output module AP95MODBUS:

https://www.se.com/ww/en/product/AP95MODBUS/struxureware-data-center-expert-modbus-tcp-output-module...

 

With that, you can output data from up to 247 NetBotz Pods or other devices that DCE is currently monitoring. You would need some kind of 3rd party Modbus TCP to RTU gateway. I know we have none officially supported by StruxureWare Data Center Expert but I can't say what may work for your situation, sorry.


Thanks,

Steve

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
APC_Steve
APC_Steve Leader
Leader

Posted: ‎2021-05-24 05:11 AM

0 Likes
3
2442
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-05-24 05:11 AM

Hi @anthichi ,

 

We don't have a Scada specific option. We do have the modbus TCP output module AP95MODBUS:

https://www.se.com/ww/en/product/AP95MODBUS/struxureware-data-center-expert-modbus-tcp-output-module...

 

With that, you can output data from up to 247 NetBotz Pods or other devices that DCE is currently monitoring. You would need some kind of 3rd party Modbus TCP to RTU gateway. I know we have none officially supported by StruxureWare Data Center Expert but I can't say what may work for your situation, sorry.


Thanks,

Steve

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

anthichi
anthichi
Explorer

Posted: ‎2022-03-16 09:08 PM

In response to APC_Steve
0 Likes
2
2199
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-16 09:08 PM

Thank for supporting,

I had read that the modbus TCP output module AP95MODBUS only collect the Field device and transfer to DCE but cannot export vice versa, so that we can not collect and export data from devices inside DCE server to other system, is it right ?

 

p.s: can you send me the userguide of AP95MODBUS module anyway ?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Shaun
Shaun Leader
Leader

Posted: ‎2022-03-17 05:54 AM

In response to anthichi
0 Likes
1
2185
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-17 05:54 AM

Hi @anthichi,

 

This functionality is documented in the user guide, https://schneider-electric.app.box.com/s/uuy2x4fr4wfsvfy2gxkn4qttwqp9vubi

Starting on page 289 - the system calls it "Building Management System Integration".  There's no separate manual for AP95MODBUS, this is just the license to enable this functionality.

 

To be clear - the DCE can poll data from modbus field devices over modbus-tcp (or via an ethernet gateway that presents the device as modbus-tcp to the DCE) - this functionality is standard and does not require the AP95MODBUS license.  So in this usage, the DCE is acting as a modbus client/master to your monitored devices.

 

The integration that's enabled by the AP95MODBUS is modbus-tcp output, which allows you to map values from device sensors to modbus registers, so an external system can read them from the DCE via modbus-tcp.  These sensors can be from snmp devices or modbus devices that the DCE monitors, or from virtual sensors created on the DCE (eg, to sum the energy usage of several monitored devices).  So in this usage, the DCE is acting as a modbus server/slave to another modbus master.

 

The other method to read data from the DCE is using the web services API - this does not require an additional license, but usually requires some custom middleware to make it available to your SCADA system.

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

ATrabert
ATrabert Mentor
Mentor

Posted: ‎2022-03-17 06:30 AM

In response to Shaun
0 Likes
0
2179
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-17 06:30 AM

It may also be worth noting that we do have an application note for how to use/integrate with DCE using the DCE modbus tcp output module

 

https://www.se.com/us/en/download/document/SPD_JRUK-7R4L9N_EN/ 

 

Be aware you can only have up to 247 slave addresses, and as far as I know, you can only assign 1 address per devices/virtual sensor.  So in large implementations, you may have to be selective on which devices you output as modbus or have to use another integration method. 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore