Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Cannot install the certificate because the Private Key does not exist

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Cannot install the certificate because the Private Key does not exist
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
exceller25cvx
exceller25cvx
Explorer

Posted: ‎2025-06-10 05:49 PM

0 Likes
3
1062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-10 05:49 PM

Cannot install the certificate because the Private Key does not exist

I am working on configuring a new virtual appliance using StruxuWare DCE 8.3

Through the DCE Client interface,

I had to open the certificate in Notepad and individually copy and paste 3 parts into a text box to have certs installed in the Server SSL certificates section.

In the Server Access section, I installed one of the parts and it gives me the above error. I tried to upload the .cer file as a whole and I get a "invalid certificate" error message.

Labels
  • Labels:
  • Data Center Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
APC_Steve
APC_Steve Leader
Leader

Posted: ‎2025-06-12 04:19 AM . Last Modified: ‎2025-06-12 04:19 AM

0 Likes
1
1032
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-12 04:19 AM . Last Modified: ‎2025-06-12 04:19 AM

Hi @exceller25cvx ,
The only time I've ever seen this is one of 2 reasons:

1-you did not go to the cert page and create a certificate signing request. This must be done to create the private key and provide the necessary information for the public key.

or

2-After creating the CSR, the DCE server was rebooted. If you reboot the server before importing the certificate that was made based on the CSR, the private key that's waiting for the new cert is deleted and you'll need to create a new CSR and cert based on that.

 

Thanks,

Steve

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
APC_Steve
APC_Steve Leader
Leader

Posted: ‎2025-06-12 04:19 AM . Last Modified: ‎2025-06-12 04:19 AM

0 Likes
1
1033
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-12 04:19 AM . Last Modified: ‎2025-06-12 04:19 AM

Hi @exceller25cvx ,
The only time I've ever seen this is one of 2 reasons:

1-you did not go to the cert page and create a certificate signing request. This must be done to create the private key and provide the necessary information for the public key.

or

2-After creating the CSR, the DCE server was rebooted. If you reboot the server before importing the certificate that was made based on the CSR, the private key that's waiting for the new cert is deleted and you'll need to create a new CSR and cert based on that.

 

Thanks,

Steve

Reply

Link copied. Please paste this link to share this article on your social media post.

exceller25cvx
exceller25cvx
Explorer

Posted: ‎2025-06-12 03:52 PM

In response to APC_Steve
0 Likes
0
1022
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-12 03:52 PM

Hello APC_Steve

After I made this post earlier, I figured out from searching other articles that I needed to create a CSR. I did give that CSR to get signed off on by Certificate Authority  but the file I received back still says the same error message.

Reply

Link copied. Please paste this link to share this article on your social media post.

exceller25cvx
exceller25cvx
Explorer

Posted: ‎2025-06-16 12:24 PM

0 Likes
0
987
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-16 12:24 PM

I had a 2nd CSR generated from within the DCE client and signed off by 3rd party CA authority or other IT team. Thanks for the help @APC_Steve 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore