New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Branch circuit monitoring and sensor mapping in amps
EcoStruxure IT Forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-10-2610:16 AM
Branch circuit monitoring and sensor mapping in amps
Hi team,
we have integrated power meters from DCE in ITA that show the current of different breakers that feed rack pdus.
We see the peak current properly in the power pop-up window, but we do not see the power information in the 2D view in the rack bars. Is it mandatory to include in the sensor mapping the information regarding to the power? We have only configured the sensor mapping in current, because the data that we have is only amps.
Do we have to convert this amps to watts multiplying by 230v in the power sensor mapping tab?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-10-2704:54 AM
Hello.
Yes. the tool-tip bars are based on watts, not amps so you will need to sensor map the amps data in the power sensor mapping view and convert the amps to watts using the multiplier field.
You may need to check the specs on the device to see the correct volts for the individual circuits as while the power meter may accept 230V, the per phase voltage may be different.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-10-2704:54 AM
Hello.
Yes. the tool-tip bars are based on watts, not amps so you will need to sensor map the amps data in the power sensor mapping view and convert the amps to watts using the multiplier field.
You may need to check the specs on the device to see the correct volts for the individual circuits as while the power meter may accept 230V, the per phase voltage may be different.