Out UPS reportes "Battery near end of life. Order replacement battery" per email.
First every 2 minute. After 500 Mails I could change it to every 2 hours.
But I will uses this set of batterie for additional 6 months.
How can I stop this message for the next 4 months?
| Smart-UPS SRT 2200 | |
| SKU: | SRT2200RMXLI |
| Serial Number: | AS1613391509 |
| Firmware Revision: | UPS 05.2 (ID1010) |
| Manufacture Date: | 04/03/2016 |
| Apparent Power Rating: | 2200 VA |
| Real Power Rating: | 1980 W |
| Battery SKU: | APCRBC141 |
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-10 03:19 AM
Maybe you can change options like repeat to "no" and if it is possible something else then "until cleared"
But something else. Have you noticed this:
CAUTION:Continued operation after end of useful life notification may cause damage to the batteries.• Recycling: Remove the RBC from the XLBP. Recycle the RBC. Do not disassemble an RBC.
So maybe it is not a good idea working with outdated batteries for 6 months
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-08 05:42 AM
Isn't this message related to the installation date of the battery? Change that date. Or change the Battery Health Alarm Warning Time
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-08 06:08 AM
I changed the Battery Install Date last week.
And set the notification E-Mail to 10h. Much more is not possible.
Now I get every day two Mail.
Any other idea?
RetoFelix
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-10 01:11 AM
No i don't have other options. You can try setting the battery health alarm warning time to -1 (no notification warning)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-10 03:19 AM
Maybe you can change options like repeat to "no" and if it is possible something else then "until cleared"
But something else. Have you noticed this:
CAUTION:Continued operation after end of useful life notification may cause damage to the batteries.• Recycling: Remove the RBC from the XLBP. Recycle the RBC. Do not disassemble an RBC.
So maybe it is not a good idea working with outdated batteries for 6 months
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-10 04:29 AM
Hi
The message "near end of life" begins 6 month before end of life.
So I know that I need new batteries. But I need a reminder in 4-6 months.
I can disable this notification.
But then I forget the batterie change and to enable of this message.