Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Asset Provisioning - Adding a device to multiple racks.

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Asset Provisioning - Adding a device to multiple racks.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 04:58 PM . Last Modified: ‎2024-04-03 04:18 AM

0 Likes
8
1826
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:58 PM . Last Modified: ‎2024-04-03 04:18 AM

Asset Provisioning - Adding a device to multiple racks.

Hi!

In working on a DCO configuration, I found that I am unable to add rackmounted devices to "each rack in room" or "selected racks" in DCO. In this case, I'm specifically trying to install 2 rack ATSes into most racks in a room using the "selected racks" feature, and am not able to. I also appear to be unable to copy and paste more than one ATS at a time.

DCO 8.2.7.

 

Any help is appreciated!

 

(CID:139693855)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 04:58 PM . Last Modified: ‎2024-04-03 04:18 AM

0 Likes
0
1826
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:58 PM . Last Modified: ‎2024-04-03 04:18 AM

I can confirm the behavior as well. Perhaps this is a bug.

Regards

GregS

(CID:139694402)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 04:58 PM . Last Modified: ‎2024-04-03 04:18 AM

0 Likes
0
1826
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:58 PM . Last Modified: ‎2024-04-03 04:18 AM

Thanks for checking it out Greg. There may be a reason for this, but perhaps our dev team could take a look and log a bug report if appropriate.

(CID:139694412)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 04:58 PM . Last Modified: ‎2024-04-03 04:18 AM

0 Likes
0
1826
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:58 PM . Last Modified: ‎2024-04-03 04:18 AM

Hi Greg,

I thought I found something of a workaround, and it turns out that workaround causes DCO to crash when saving as well.

I created a device category in the genome and put two identical rack ATSes in it. I was then able to drag that category into a rack and it would place two rATSes in the rack with one action, which I thought would save me some time.

As it turns out, if you create a device category with multiple identical (or near identical - I changed the name slightly and had the same issue) devices and try and save, the DCO client will crash, lose any changes, and restart.

I'll email you a screenshot as I'm getting an error when trying to attach it here.

(CID:139694491)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 04:58 PM . Last Modified: ‎2024-04-03 04:18 AM

0 Likes
3
1826
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:58 PM . Last Modified: ‎2024-04-03 04:18 AM

Hi Jeff,

Asset Provisioning is basically designed to recommend the best location for a server in the rack layout. I don't think it is designed to be used for other items such as rack pdus and definitely not for rack ats usage.

In general we can only add one rack mounted item to a rack at a time, so adding multiple devices in one go (to a rack) is unsupported.

We can only copy one rack-mounted item at a time (to Clipboard), copying some random rack ats and then dragging them to a rack (from Clipboard) worked for me without any problem. 

Please also notice that only one rack ats can/may be connected to pair of the rack pdus (in the rack).

Kind regards

(CID:140216027)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 04:58 PM . Last Modified: ‎2024-04-03 04:18 AM

In response to DCIM_Support
0 Likes
0
1826
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:58 PM . Last Modified: ‎2024-04-03 04:18 AM

Hi Jef,

While the primary purpose of asset provisioning is absolutely for finding the best place to install a piece of equipment, what other purpose would the "Each rack in room" or "Selected racks" options serve other than mass deployment of rack mounted equipment?

In our services group, we frequently use the tool for mass deployment of rack pdus in new configurations (for 0u pdus, we just change the mounting to rear right OR rear left, add to selected racks, then change mounting to the other side and repeat). Without this ability, our configuration services would take far longer.

I am able to add a single 1U rackmount PDU using selected racks or each rack in room, why not a rack ATS?

I've used asset provisioning to add 2 0U, 1 outlet "rack PDUs" in each side of each rack, and made all of the upstream power connections, and am now trying to add 2 1U rack ATSes in each rack and connect each one to two of the four rack pdus in the rack.

(CID:140216120)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 04:58 PM . Last Modified: ‎2024-04-03 04:18 AM

In response to DCIM_Support
0 Likes
0
1826
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:58 PM . Last Modified: ‎2024-04-03 04:18 AM

Just adding to this. Simply manually dragging and dropping rack 2 rATSes into each rack, without even making any power connections, on more than 2-3 racks at a time also appears to crash the client when saving, losing my work.

(CID:140216182)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 04:58 PM . Last Modified: ‎2024-04-03 04:18 AM

In response to DCIM_Support
0 Likes
0
1826
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:58 PM . Last Modified: ‎2024-04-03 04:18 AM

Hi Jeff,

For the purpose of asset provisioning 😀, as described in the following page:

https://sxwhelpcenter.ecostruxureit.com/display/UADCO8x/Working+with+Asset+Provisioning

The system recommends the best location for a server in the rack layout, using available space, cooling, and power capacity to optimize capacity utilization and avoid stranded capacity.

To effectively identify the best location for the selected equipment using this feature, ensure the system is set up correctly, including the appropriate rack PDUs, UPS and PDUs, and power paths.

 

Concerning your client crash when adding rack-ats units: can you please provide the following: how to reproduce with screen captures illustrating which genome device is being used, and possibly modified in the local genomes. It would also be great if I may have a copy of your backup file.

Thanks,

Kind regards

(CID:140216497)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 04:58 PM . Last Modified: ‎2023-10-20 05:01 AM

0 Likes
0
1826
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:58 PM . Last Modified: ‎2023-10-20 05:01 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore