Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Application whitelisting Carbon Black Product

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Application whitelisting Carbon Black Product
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:54 PM . Last Modified: ‎2024-04-03 01:24 AM

0 Likes
3
3891
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:54 PM . Last Modified: ‎2024-04-03 01:24 AM

Application whitelisting Carbon Black Product

Hi

I have an email from a customer that has DCE and DCO, and is about to deploy some protection software by Carbon Black. He has some questions about the whitelisting function regarding our software. Can anyone shed any light on the subject. I have pasted his email below:

 

At the future point in time when Application Whitelisting agents are deployed to the Woodside OT fleet, the software you supply/support will need to be added to a whitelist to ensure its continued operation.

 

At this stage we're not seeking any involvement from your organisation on the OT Cyber Resiliency Project, other than we would like you to:

 

  1. Notify us, if your organisation has had previous experience (at other customers sites), in enabling your software/hardware in conjunction with any Application Whitelisting toolsets.
  2. Notify us, if your organisation has had previous experience (at other customer sites), in enabling your software/hardware in conjunction specifically with the CB Protection toolset.
  3. Send us any Lessons Learnt logs your organisation has from previous experience in making your software/hardware operate under an Application Whitelisting toolset.
  4. Advise us of any Best Practice your organisation has in regards to making your software/hardware operate under an Application Whitelisting regime.

 

(CID:144867993)

Labels
  • Labels:
  • Data Center Expert
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:54 PM . Last Modified: ‎2024-04-03 01:24 AM

0 Likes
1
3888
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:54 PM . Last Modified: ‎2024-04-03 01:24 AM

Hi Paul,

 

I don't understand enough about the application itself to provide a precise answer. If as I imagine this is a software installed on the operating system to monitor it like an anti-virus, it can not be installed on StruxureWare DCE. DCE is a "Black Box" and nothing can be installed on the system. Although I don't have enough info on DCO, I would imagine it would potentially cause issues there as well. Additionally, if there is something  trying to connect to the systems, there is little to no info that can be obtained. There is also no "white-listing" available on the system for applications

 

If you have more specific info on how this "Carbon Black" may operate and what it needs or does, perhaps we can provide a more specific answer.

 

Steve

(CID:144868100)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:54 PM . Last Modified: ‎2024-04-03 01:24 AM

0 Likes
1
3889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:54 PM . Last Modified: ‎2024-04-03 01:24 AM

Hi Paul,

 

I don't understand enough about the application itself to provide a precise answer. If as I imagine this is a software installed on the operating system to monitor it like an anti-virus, it can not be installed on StruxureWare DCE. DCE is a "Black Box" and nothing can be installed on the system. Although I don't have enough info on DCO, I would imagine it would potentially cause issues there as well. Additionally, if there is something  trying to connect to the systems, there is little to no info that can be obtained. There is also no "white-listing" available on the system for applications

 

If you have more specific info on how this "Carbon Black" may operate and what it needs or does, perhaps we can provide a more specific answer.

 

Steve

(CID:144868100)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:54 PM . Last Modified: ‎2024-04-03 01:24 AM

In response to DCIM_Support
0 Likes
0
3888
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:54 PM . Last Modified: ‎2024-04-03 01:24 AM

Hi Steve

Thanks for your reply

Yeah, I pretty much replied the same thing to the customer so I leave it with them for now. I suggested that if their security software allows them to white-list manually that they should allow DCE and DCO, if it is set through some sort of global database, then they need to apply to the developers to allow specific software (the same way anti-virus databases work). I let them know that they are java apps and that the relevant JRE will be required to run also.

I guess ultimately its up to them to configure the white list, and our software like any other software can be allowed or disallowed.

(CID:144868290)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:54 PM . Last Modified: ‎2023-10-20 05:01 AM

0 Likes
0
3888
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:54 PM . Last Modified: ‎2023-10-20 05:01 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore