Good day all
Please assist
We would like to add netbotz 550 external sensors to the default notification policy. Is there anyway that we can do that? i would like to set thresholds and customise each sensor.
Is this possible.
Currently, i have configured these settings by right clicking the device - netbotz appliance configuration>Alert thresholds> and selecting sensors. After following all the prompts i do not receive e-mails. I presume that these sensors are not in the default notification policy.
Any suggestions.
Your assistance is much appreciated
(CID:130098889)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:51 PM . Last Modified: 2024-04-05 12:06 AM
Dear juice,
In general, NetBotz-4.x appliance is absolutely independent device from DCE-server.
This means, that in order for you to be able to receive any notifications about the status of external sensors, that are connected to particular NetBotz-4.x appliance, all the relevant settings need to be done on this particular NetBotz-4.x appliance. These settings can be made in the usual way, using the APC Advanced View software or using the DCE-client software, as you wrote:
...Currently, i have configured these settings by right clicking the device - netbotz appliance configuration>Alert thresholds> and selecting sensors.
If briefly, for example, in order to receive e-mail notifications, the SMTP server must be correctly configured on your NetBotz-550 (not on the DCE-server). In addition, on your NetBotz-550 (not on the DCE-server), an e-mail notification policy must be configured, which must then be applied to the alarm threshold for a specific external sensor.
More details about this can be found in the NetBotz-4.x user manual on page Netbotz v4.x. If you have any questions, please ask.
Workaround: applicable for almost all external sensors, that are connected to the NetBotz-4.x appliance, except for discrete state sensors.
For example, let's take an external temperature sensor: in order to nothing configure on the NetBotz-4.x appliance, it is necessary in the DCE-client to create a corresponding virtual sensor for the above external temperature sensor. Then, for this virtual temperature sensor, you can create an alarm threshold in the DCE-server, apply the DCE-server notification policy for it, and check the result.
In this case, you do not need to configure the SMTP server on NetBotz-4.x appliance, you do not need to create alarm thresholds on NetBotz-4.x appliance, you do not need to create notification policies on NetBotz-4.x appliance, and you can disable the external sensor alarms on NetBotz-4.x appliance. I.e., absolutely everything is configured through a single DCE-server. It is this workaround solution, that I have been using successfully for many years 😀.
With respect.
(CID:130099077)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:51 PM . Last Modified: 2024-04-05 12:06 AM
Dear juice,
Have you been able to solve your problem, or do you have any more questions about it?
With respect.
(CID:130680471)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:52 PM . Last Modified: 2023-10-20 04:59 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.