Posted: 2020-07-04 09:49 PM . Last Modified: 2024-04-04 03:32 AM
Dears,
I have Netboze 450 with mixed racks environment and I have the demand to secure 5 AR100 racks with access control handles and have checked the NBACS125 handles does not fit on the Rack, any one can suggest alternative handles which are compatible with DCE?
Many Thanks,
MK
(CID:133372229)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 09:49 PM . Last Modified: 2024-04-04 03:32 AM
Hi Mohd Khader, thanks for posting! Let's hope you find your answer here.
Thanks,
Stine
(CID:134026244)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 09:49 PM . Last Modified: 2024-04-04 03:32 AM
Mohd Khader,
I do not believe that there are any rack access (handles with card readers) that are compatible with the WX (wallmount) series of racks. Most handles are compatible with SX series with select other series of racks depending on: handle kits, main NetBotz appliances, or conversion kits.
Best Regards,
Cory
(CID:134029188)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 09:49 PM . Last Modified: 2023-10-20 04:58 AM