We have over 300 remote APC UPS in the 1500 and 2200 variety. We monitor the device with DCE 7.2.1. Over the last 6 weeks I have notice devices all over our footprint are showing a communication alarm. The units are still accessible through the Web interface but still they shop up as Communication as being down.
I expect that our security department is locking down the remote firewall and my have closed down the UPS communication port? I can't get them to own up to actions. Can you tell me how the UPS Communicates with DCE?
Thanks much for your support.
(CID:132665856)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 08:19 PM . Last Modified: 2024-04-04 04:14 AM
Chuck,
With these particular alarms it is most likely lost SNMP communications. Ports 161 and 162 are the default ports for SNMP communications. We do use other ports for DCE, but these are the two that are most likely blocked. You should also check and make sure that nobody has turned off/changed the SNMP values on the NMCs themselves.
(CID:132665864)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 08:19 PM . Last Modified: 2023-10-20 04:56 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.