Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

AP7175 & AP7155

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • AP7175 & AP7155
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:35 PM . Last Modified: ‎2024-04-03 02:36 AM

0 Likes
9
1833
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:35 PM . Last Modified: ‎2024-04-03 02:36 AM

AP7175 & AP7155

Hello,

I have several number of AP7175 and AP7155. I was trying to make a virtual sensor for kWh and only one AP7175 could give me that option.

what might be wrong?

 

Thank you in advanced

(CID:143760818)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 9
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:35 PM . Last Modified: ‎2024-04-03 02:36 AM

0 Likes
1
1833
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:35 PM . Last Modified: ‎2024-04-03 02:36 AM

Hi Grigorios,

 

I don't have a AP7155 for testing but the first thing I would suggest looking at is the device sensors in DCE. If you right click and view device sensors, are the sensor values listed in watts or KW? If they're listed in watts, you can't use them for a KW virtual sensor.

 

Steve

(CID:143760837)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:35 PM . Last Modified: ‎2024-04-03 02:36 AM

In response to DCIM_Support
0 Likes
0
1833
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:35 PM . Last Modified: ‎2024-04-03 02:36 AM

Everyone are in watts. But the problem is that they don't give me energy used option (kWh) except one AP7175!!!

(CID:143760866)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:35 PM . Last Modified: ‎2024-04-03 02:36 AM

0 Likes
1
1833
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:35 PM . Last Modified: ‎2024-04-03 02:36 AM

I think problem is that if you use AP7175 and AP7155 you are running on old nmc hardware which had never energymeter on it. you need to make sure you are running on AP7175B and AP7155B those are running with nmc2 boards and will supply enerymeter datapounts.

(CID:144313638)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:35 PM . Last Modified: ‎2024-04-03 02:36 AM

In response to DCIM_Support
0 Likes
0
1833
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:35 PM . Last Modified: ‎2024-04-03 02:36 AM

Maybe this is the problem. But The strange thing is that I have 2 exact same AP7175 but only the one gives me the kWh option as you can see at the attached (.203 vs .204)

(CID:144313770)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:35 PM . Last Modified: ‎2024-04-03 02:36 AM

0 Likes
3
1833
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:35 PM . Last Modified: ‎2024-04-03 02:36 AM

Hi can you go to device with your mouse, rightclick and show sensors? Make a screenshot of this and post it here....

(CID:144313822)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:35 PM . Last Modified: ‎2024-04-03 02:36 AM

In response to DCIM_Support
0 Likes
0
1833
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:35 PM . Last Modified: ‎2024-04-03 02:36 AM

The one with the many sensors gives me the kWh option despite the "unplugged" as you saw on my previous answer

The other one give only the kw option.

(CID:144313834)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:35 PM . Last Modified: ‎2024-04-03 02:36 AM

In response to DCIM_Support
0 Likes
0
1833
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:35 PM . Last Modified: ‎2024-04-03 02:36 AM

I see a ton of "Unplugged" sensors. That happens for a number of reasons. If all sensors are showing off line (they aren't) that's showing a no-comm. 

If, like you're seeing, some sensors are off-line, the same ones all the time, that's one of 2 things.

1: The device firmware was updated and no longer has these sensors available

or

2: DCE / the appropriate DDF was updated such as what's noted in the following k-base:

http://www.apc.com/us/en/faqs/FA282386

 

The unplugged sensors in this case should be deleted unless you need the historical data. I do not see KWh in your screenshot but if the only available sensors report unplugged, you're not going to get any data going forward.

If the device shows a KWh sensor, you should be able to use it for a threshold. In your screenshots however, these sensors are not shown. 

Please also note that KW and KWh are totally different sensors. KW is simply a measure of power where KWh is a measure of power over time. 

I've got 2 large Symmetras, a 250K and a 40K. Both have KW values for load but only the 250 has a KWh sensor. Some devices simply do not have the sensor you're looking for and it can (as Ueli noted) be based on the age of the unit or the firmware it's running.

 

 

(CID:144313861)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:35 PM . Last Modified: ‎2024-04-03 02:36 AM

In response to DCIM_Support
0 Likes
0
1833
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:35 PM . Last Modified: ‎2024-04-03 02:36 AM

So, I will delete the unplugged sensors.

And the particular devices AP7155 & AP7175 don't have kwh sensors.

Thank you very much for your time

(CID:144313894)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:36 PM . Last Modified: ‎2023-10-20 04:55 AM

0 Likes
0
1833
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:36 PM . Last Modified: ‎2023-10-20 04:55 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore