Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

VBSscript changes in Geo SCADA 2025R2 new script engine

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • VBSscript changes in Geo SCADA 2025R2 new script engine
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
sbeadle Champion
337
AndrewScott
AndrewScott
128
BevanWeiss
BevanWeiss
104
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
rlao
rlao
Contributor

Posted: ‎2026-10-27 10:56 PM

3 Likes
4
421
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-10-27 10:56 PM

VBSscript changes in Geo SCADA 2025R2 new script engine

With the recent release of 2025R2, the Geo SCADA Knowledge Base has been updated with a new article, which outlines all the changes to VBScript as part of the new script engine introduced in 2025R2.

 

Are these changes being presented as known bugs to be actioned or intended features that are here to stay? A lot of them are changes to what has been previously considered valid syntax for years, such as the use of default properties on Forms (no longer supported in 2025R2) and not needing to populate all pick action parameters to execute a script (2025R2 now needs everything to be explicitly populated). Updating our mimic scripts to conform to these new rules is a monumental effort for us with the size of our SCADA systems. 

 

And to be frank, some of these announced changes sound a bit bizarre. List Boxes now scroll horizontally rather than vertically when you populate them with more items that graphically fit into the box? Does this mean we can no longer design our forms to have vertical scroll bars on list boxes? Again, is this being presented as a bug or a feature?

 

As an end-user, I am very concerned about the amount of work we need to do to prep our systems for the 2025R2 update. We definitely weren't expecting to have to overhaul our scripting just to be able to move to this update. I have already raised a few of these with Support who have pointed me back to this very same KB article, so it feels we are going a bit in circles.

Labels
  • Labels:
  • SCADA
  • Scripting
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
AdamWoodlandToo
AdamWoodlandToo
Mentor

Posted: ‎2026-10-28 05:17 PM . Last Modified: ‎2026-10-28 05:34 PM

2 Likes
0
402
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-10-28 05:17 PM . Last Modified: ‎2026-10-28 05:34 PM

In a bit of self-promotion, these issues have driven (not supported or sanctioned by SE, open-source and provided without warranty) https://github.com/adamwoodland2/GeoSCADA-Script-Exporter which does two things:

 

1. Exports the scripts from mimics, pick actions and script libraries to disk (needs access to a running Geo SCADA, have tested it against 2025 R2 Release only)

2. Analyses the exported files (no access to Geo SCADA needed so you can copy files off a server) and identifies the issues highlighted in the article above.

 

As things get found or new thing get added to the article, the analyser script gets updated (using Claude).

 

People are welcome to give it a go against a test database and see if it is of any help.

Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
sbeadle Champion
Champion

Posted: ‎2026-10-29 03:17 AM

0 Likes
1
371
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-10-29 03:17 AM

A big thank-you to Adam for creating this tool.

 

Unfortunately the script engine has had to be changed because Microsoft is eventually withdrawing VBScript. You'll see evidence of this in the Windows Event Viewer when ViewX is started - warnings for applications using VBScript.

 

The script engine has transitioned to .Net, and some changes were needed because the new engine has some different behaviors. .Net and WPF forced list scrolling to change, and the script engine is more 'fussy' about types etc.

 

Support and development will be keeping a close eye on feedback and tickets, so some issues could be investigated to see if there are ways to improve them. (e.g. the missing parameter issue).

 

Further feedback is welcome.

Reply

Link copied. Please paste this link to share this article on your social media post.

rlao
rlao
Contributor

Posted: ‎2026-10-29 05:09 PM . Last Modified: ‎2026-10-29 05:15 PM

In response to sbeadle
1 Like
0
354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-10-29 05:09 PM . Last Modified: ‎2026-10-29 05:15 PM

Hi Steve,

 

Thanks for the info

 

Regarding the general tightening of syntax, I don't believe the full impact of this script engine change has been accurately communicated in Schneider's messaging, hence why it has caught us off-guard.

 

The GS2025R2 release was recently presented at one of the Schneider roadshows I attended. The question was asked about the new scripting changes and the feedback from the presenters was that they were not aware of any major impact to existing scripting...

 

This has not been the case for us at all. Even with templating and use of script libraries, all these 'minor changes' are replicated hundreds (possibly thousands) of times across all our scripts. Sifting through and fixing them all up is very time-consuming if we don't homebrew our tools like what Adam has (thanks to Adam for sharing these as well). Are Schneider going to be developing tools to help end-users navigate these changes?

 

On specific changes:

 

The Pick Action change is going to catch a lot of people out, because it will silently fail if you don't specify all arguments now. I think we need to have a proper error message now if this method of configuration is not allowed.

 

Is vertical scrolling on List Boxes truly gone? We have widely used user forms that generates long lists of points for users to multi-select to build ad-hoc trends. Having those be horizontally scrollable makes the form look extremely weird and not a pleasant user experience at all. And there is nothing we can do to work around this as an end-user.

Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
sbeadle Champion
Champion

Posted: ‎2026-10-30 04:02 AM

0 Likes
0
305
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-10-30 04:02 AM

Thank you very much for this feedback. They will reassess the specific items of pick actions and scrolling.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore