Ask our Experts
Didn't find what you are looking for? Ask our experts!
New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).
Search in
Please select a country to continue with beta search.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-11-06 05:21 AM . Last Modified: 2025-11-27 01:19 AM
I need to configure an analog point that combines four consecutive Modbus registers into one 64-bit integer value. Is there a native way to achieve this in Geo SCADA Expert?
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-11-06 08:21 AM
The simple Modbus analog point doesn't have a 64-bit integer data type, only 16-bit and 32-bit integers.
The only 64-bit data type is IEEE-754 double precision floating point.
See "Driver Reference > Modbus - Simple Driver > Configuring Analog Points > Configure the Modbus Point Properties" page in the help.
The closest I can think of would be to use two analog points with UDINT data type to read each half of the 64-bit integer and then use a logic program to combine the two halves into a "Long Long" or "Unsigned Long Long" variable object, but that's rather messy and a variable doesn't have the features of a point.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-11-06 08:32 PM
With 'smarter' Flow Meters (and similar devices like Power Meters) there is starting to get a reasonably large number of field devices that have 64-bit registers to hold totaliser values.
It would be ideal if GeoSCADA Expert did include a 'special' 64-bit Advanced Modbus Point (with 1234, 4321, 2143, 3412, register type ordering options for retrieval).. I guess it could just be an option under the current Advanced Modbus Analog point... I can't recall the native datatype for the Point's .Value field... if it's already 64bit then it should be fine... otherwise I guess that's the bigger challenge..
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-11-06 10:39 PM . Last Modified: 2025-11-06 10:57 PM
As @AndrewScott said, to use two UDINTs but calculate them in Calcilation Analog Point.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-11-07 02:07 AM
Both simple and advanced analog points (and calculated analog points) use IEEE-754 double precision floating values so they can't store a 64-bit integer value without introducing a conversion error., hence my suggestion of using a 64-bit variable rather than an analog point.
However, depending on the application, maybe a conversion error is acceptable so an analog point could be used.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.