Simple Modbus 64bit Integer

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Simple Modbus 64bit Integer
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
321
AndrewScott
Admiral AndrewScott
115
BevanWeiss
Spock BevanWeiss
99
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Oz_Ba
Lieutenant Oz_Ba
Lieutenant

Posted: ‎2025-11-06 05:21 AM . Last Modified: ‎2025-11-27 01:19 AM

0 Likes
4
315
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-06 05:21 AM . Last Modified: ‎2025-11-27 01:19 AM

Simple Modbus 64bit Integer

I need to configure an analog point that combines four consecutive Modbus registers into one 64-bit integer value. Is there a native way to achieve this in Geo SCADA Expert?

 

Thanks.

Labels
  • Labels:
  • SCADA
  • Telemetry
  • Tags:
  • 64bit
  • english
  • modbus
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2025-11-06 08:21 AM

1 Like
1
308
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-06 08:21 AM

The simple Modbus analog point doesn't have a 64-bit integer data type, only 16-bit and 32-bit integers.

The only 64-bit data type is IEEE-754 double precision floating point.

 

See "Driver Reference > Modbus - Simple Driver > Configuring Analog Points > Configure the Modbus Point Properties" page in the help.

 

The closest I can think of would be to use two analog points with UDINT data type to read each half of the 64-bit integer and then use a logic program to combine the two halves into a "Long Long" or "Unsigned Long Long" variable object, but that's rather messy and a variable doesn't have the features of a point.


Andrew Scott, R&D Principal Technologist, AVEVA
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2025-11-06 08:32 PM

In response to AndrewScott
0 Likes
0
295
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-06 08:32 PM

With 'smarter' Flow Meters (and similar devices like Power Meters) there is starting to get a reasonably large number of field devices that have 64-bit registers to hold totaliser values.

 

It would be ideal if GeoSCADA Expert did include a 'special' 64-bit Advanced Modbus Point (with 1234, 4321, 2143, 3412, register type ordering options for retrieval).. I guess it could just be an option under the current Advanced Modbus Analog point...  I can't recall the native datatype for the Point's .Value field...  if it's already 64bit then it should be fine... otherwise I guess that's the bigger challenge..

 


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Reply

Link copied. Please paste this link to share this article on your social media post.

gabarit
Lieutenant JG gabarit
Lieutenant JG

Posted: ‎2025-11-06 10:39 PM . Last Modified: ‎2025-11-06 10:57 PM

0 Likes
0
289
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-06 10:39 PM . Last Modified: ‎2025-11-06 10:57 PM

As @AndrewScott said, to use two UDINTs but calculate them in Calcilation Analog Point.

Reply

Link copied. Please paste this link to share this article on your social media post.

AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2025-11-07 02:07 AM

1 Like
0
268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-07 02:07 AM

Both simple and advanced analog points (and calculated analog points) use IEEE-754 double precision floating values so they can't store a 64-bit integer value without introducing a conversion error., hence my suggestion of using a 64-bit variable rather than an analog point.

 

However, depending on the application, maybe a conversion error is acceptable so an analog point could be used.


Andrew Scott, R&D Principal Technologist, AVEVA
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore