Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

OPC UA data timestamp does not replicated correctly

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • OPC UA data timestamp does not replicated correctly
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
sbeadle Champion
335
AndrewScott
AndrewScott
125
BevanWeiss
BevanWeiss
103
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Dragonfly1
Dragonfly1
Explorer

Posted: ‎2026-06-12 09:11 AM

3 Likes
4
306
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-06-12 09:11 AM

OPC UA data timestamp does not replicated correctly

I'm using Geoscada in edge to pull modbus devices. This Geoscada will be connect to another Geoscada (intermediate Geoscada) using OPC UA to pass data to this Geoscada, and this Geoscada will ultimately connect to Central Geoscada also using OPC UA to pass data to this Geoscada, so here is the architecture 

 

Geoscada (Edge) --> Geoscada (Intermediate) --> Geoscada(Central)  ( All using OPC UA Connection)

 

As data moves from 1 Geoscada to the others, I observed that at the Intermediate and Central level, Geoscada automatically generate more data with different quality at the Intermediate and Central level. This behavior is impacting the calculation tags which uses this tag as an input. Attached is the screenshot of my data 
Is there anyone experiencing this behavior? 

Attachments
Labels
  • Labels:
  • Drivers
  • SCADA
  • ViewX
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
AdamWoodlandToo
AdamWoodlandToo
Mentor

Posted: ‎2026-06-15 08:43 PM

0 Likes
0
294
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-06-15 08:43 PM

Not seen such behaviour before, but I've not really pushed the OPC-UA driver yet.

 

Can you add milliseconds to the timestamp (in your user profile) just to check nothing funky going on at that level?

 

Might need to get some driver logs for OPC UA and get support to have a look too.

Reply

Link copied. Please paste this link to share this article on your social media post.

Dragonfly1
Dragonfly1
Explorer

Posted: ‎2026-06-16 09:01 AM

0 Likes
0
258
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-06-16 09:01 AM

I added milliseconds to the timestamp and test DA protocol 

Geoscada (Edge) --> Geoscada (Intermediate) --> Geoscada(Central)  ( All using OPC DA Connection)

I notice that from Edge to Intermediate, the timestamp replicated correctly, but from Intermediate to Central, the timestamp is incorrect ( screenshot).

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Noel_Henderson
Noel_Henderson Explorer
Explorer

Posted: ‎2026-06-17 06:45 AM

0 Likes
1
245
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-06-17 06:45 AM

I noticed that the timestamps in question on the final system are the same as the previous good value timestamp, which is actually the proper way that OPC UA is supposed to propagate bad quality timestamps. I wonder if this is due to different settings between the servers with regards to the 'Log Historic Value on Communication Failure' settings for the Outstations.

Server 01 is saving the timestamp of the Modbus demand poll to say that it thinks the value at timestamp '2026-06-16 10:50:16.980' was zero, even with a bad quality. In my work, this would be considered an invalid inference, since the demand scan failed, and we do not know what the value was at that timestamp. Writing any value, including a zero, would not be reliable, which is why the OPC UA spec says to write a null. Zero is a valid value, and if a client does not filter on quality, they might think there was a valid zero value at the timestamp. We only knew the value at the previous timestamp. We could not infer the value for a failed scan and assign it the timestamp of the failed scan. Therefore, all we could do was say that, as far as we knew, the last known value's timestamp was the timestamp of the previous poll, and that was also the time we wanted marked as being the start of the bad quality data, until proven otherwise by a subsequent good poll. There IS no valid data that can be inferred during a communications failure state. The ONLY information you know is that you don't know anything. Marking the value at the previous timestamp as the last known good value that is carried forward until the next good scan is the OPC standard.


I would try unchecking the box for the Modbus Outstation on Server 01 to disable the 'Log Historic Value on Communication Failure' option or increase the Persistence Timeout to longer than the scan time. However, increasing the Persistence Timeout can result in out of order data with timestamps that do not make sense. If you simply do not store made up values when you can't reach the device, you will get consistent timestamps across servers. You can still track communications failures/failed scans at the outstation level, instead of the individual point level. This would also help to minimize communication failure alarms/events on individual points.

In the Geo SCADA help system, search for:
Driver Reference > Advanced Drivers Guide > Configuring an Outstation > Specify Whether Points Log a Historic Value on Communication Failure
and
Driver Reference > Advanced Drivers Guide > Configuring an Outstation > The Effects of Logging a Value Historically on Communication Failure

Reply

Link copied. Please paste this link to share this article on your social media post.

Dragonfly1
Dragonfly1
Explorer

Posted: ‎2026-06-18 11:48 AM

In response to Noel_Henderson
0 Likes
0
201
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-06-18 11:48 AM

@Noel_Henderson thank you for your response.
I tried playing with 'Log Historic Value on Communication Failure' and it still yield the same result. Also, they data from the my screenshot is not actual data from a Modbus device, they data is from my OPC data simulator, so there is no option for be to tweak the Outstation object. 

The server configurations across 3 servers are the same. I think regardless of protocol, it should document the correct timestamp when the value goes to bad quality state 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore